Rob wrote:
>The FCP is good for 4000 the same as the ZCP 

All newer I/A series CPs (at least I know this from CP40s and up) have a hard 
limit of 4000 CB-Objects per CP, this is an intended limitation of an internal 
object list, not a performance or memory constraint. It has been designed this 
way to limit the maximum time required in a worst case for a hot remarry of 
redundant CPs. Most of the times you reach earlier other limits in a CP but if 
you use large numbers of simple blocks you can easily reach that limit.

Each compound and each block occupies one place in that list. Also ECB blocks 
count for that list. So 4000 tags can never be reached (as you need some list 
entries for the Compounds and the ECBs. ;-) And if for any reason you need more 
than one block per Tag (we have installations where this is the case, e.g. for 
tagbased naming on bits which have to be extracted from words) the maximum 
number of Tags is even lower.

Just to be precise.

Best regards / Mit freundlichen Grüßen
 
Marcel Sieling
Senior Application Consultant
 
Invensys Systems GmbH
Emanuel-Leutze-Str. 11 
D-40547 Düsseldorf
Germany
T +49 211 5966302
M +49 163 5966302
F +49 163 99 5966302
E  marcel.sieling@xxxxxxxxxxxx <-new!
 
iom.invensys.com
Geschäftsführer: Harald Konermann, Amtsgericht Düsseldorf - HRB37252
Hauptsitz der Firma: Emanuel-Leutze-Str. 11, 40547 Düsseldorf, Germany
P  Please consider the environment before printing this e-mail q

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of jrmcleish63@xxxxxxxxxxxxxxx
Sent: Thursday, April 29, 2010 12:04 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] FBM230 and DH+

Jack,

as far as I know you need to have a separate license for each CP and a separate 
license for each FDSI that is configured for that CP, hope so because we have 
purchased heaps. If you are only going to install FDSI on that particular CP 
with no IO type FBM then there is a special license which covers this and is 
much less expensive. 

The FCP is good for 4000 the same as the ZCP and as you mentioned 2000 blocks 
for the FDSI.  What we have found is that it is easy have a large number of 
serial data and having to use DCI blocks to interface to standard blocks makes 
the problem worse. In our case all of our ex ABSTN graphics pointed to ether 
MCIN or MCOUT blocks, we were unable to get graphic to look at the packed 
output of the PACKIN so had to retain the MCINs. Version 8.4 has help some in 
reducing this but not eliminated the DCI - Standard IA block problem.

We have now two FCPs with FDSI's only and are buying another two to do a 
similar job.
We also put in 6 x 232's and directly wired to an Anybus modbus-devicenet 
gateways to replace some of our ABSTN and PLC5's this has worked well.

My only gripe, and it's the old UNIX / Windoz argument is that the AB Serial 
drivers don't work in UNIX we were unable to load the driver. We got round this 
be configuring a dummy FDSI on a AW70, loading the FDSI then plugging it in to 
the CP hosted on the SOTM machine. Not the best solution but it does work. I 
still have to chase this up with Foxboro.


Regards, Rob.

*** Confidentiality Notice: This e-mail, including any associated or attached 
files, is intended solely for the individual or entity to which it is 
addressed. This e-mail is confidential and may well also be legally privileged. 
If you have received it in error, you are on notice of its status. Please 
notify the sender immediately by reply e-mail and then delete this message from 
your system. Please do not copy it or use it for any purposes, or disclose its 
contents to any other person. This email comes from a division of the Invensys 
Group, owned by Invensys plc, which is a company registered in England and 
Wales with its registered office at Portland House, Bressenden Place, London, 
SW1E 5BF (Registered number 166023). For a list of European legal entities 
within the Invensys Group, please go to 
http://www.invensys.com/legal/default.asp?top_nav_id=77&nav_id=80&prev_id=77. 
You may contact Invensys plc on +44 (0)20 7821 3848 or e-mail 
inet.hqhelpdesk@xxxxxxxxxxxxx This e-mail and any attachments thereto may be 
subject to the terms of any agreements between Invensys (and/or its 
subsidiaries and affiliates) and the recipient (and/or its subsidiaries and 
affiliates).


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: