Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit

  • From: "Joseph M. Riccardi" <Joe@xxxxxxxxxxxxx>
  • To: <foxboro@xxxxxxxxxxxxx>
  • Date: Thu, 22 Sep 2016 11:20:46 -0700

Russ and Terry,

Thanks for the help and suggestions.  I will address both of your comments
below...

1st I would like to review what I see at this point...
-   I double checked the SysDef configuration and everything looks good,
just as I changed them.  The System Monitor was reassigned to the new AW70,
the CPs are all hosted by the new AW70, the old AW70 is gone, and all of the
checked and verified columns are "Yes" with a modified date of yesterday.
:-)
-  The d:/usr/fox/sp/IIF.pkg file shows the new AW70, all CPs/FBMs that were
re-hosted, and ASMON7 (System Monitor?) as NOTYET.  ;-(  I see a number of
the standard software packages as DONE, including AICC7 (ICC?).  During the
commit process I inserted all of the appropriate diskettes (i.e., System
Monitor, ICC, CP60, etc.) when prompted and all installed without errors.  

At this point my conclusion is that the SysDef process and the move CSA
process was successful, but the commit process failed miserably.  Why?

Status...
-  When I call up the System Management Display the System Monitor is not
shown, getting error "System Monitor not responding".  That makes sense
since ASMON7 = NOTYET.
-  When I open the CIO_Config it appears that all of the Compounds are
listed but when I pick one I get "CSA Error - CSgetcmpd Failed".  That makes
sense since CSA move OK but AICC7 = NOTYET.  
-  If I select the CIO_Station_Config there are no CPs listed.
-  All of the /usr/fox/sp/*lns files look correct.
-  sldb is a new file to me but it only shows the Stations hosting volumes.
What should it show?
-  All CPs are empty and not even on line.   
-  I moved the Checkpoint files from the old AW70 to the new one to reboot
them as soon as I resolve the commit process issues.  Or I was hoping to do
a Load_All from the Save_All files I created and then checkpoint them so the
Checkpoint files are up to date.

It sure looks to me like I am close if I can figure out why the commit
process failed.  Any ideas?  Or just do it again?

Thanks


Joseph M. Riccardi
386-451-7607 Cell
 
Joe@xxxxxxxxxxxxx
 
"To give real service you must add something that cannot be bought or
measured with money; and that is sincerity and integrity." - Donald A. Adams


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Boulay, Russ
Sent: Wednesday, September 21, 2016 8:11 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit

When you open ICC and you can see the Compounds listed, that is directly
from CSA If yo select a compound and get that message you are seeing, that
is because it is a compound that it believes is not in a CP hosted by that
AW Windows machines can only edit CP's that they host.
Also if no CP's show when you select edit station, that is for the same
reason.
Windows AW's can only edit CP's that they host, so that station doesn't
believe it host any.

Your procedures to move CP hosting did not go according to plan.

If you look on that AW and check d:/usr/fox/sp/IIF.pkg ....what are the
statuses of the packages....DONE, NOTYET, REINST ??

Also in same directory....the file sldb .....does it show correct hosting ??
[  Joseph M. Riccardi  ] 


Joe,
 
Removing any station from a system is always difficult in IA without doing a
complete Day0 install.
 
Not clear if you can get into a specific CP from the control configurator or
not. Are the CP's good in System Management?
 
If the CP's are good in SysMgmt but you cannot access them in the
configurator, you should be able to clean out a CP by copying the
DB<LBUG>.init  file into DB<LBUG>.UC (checkpoint file) and rebooting the CP
which initializes the CP memory.  Then hopefully you can access the CP in
the control configurator.    When you are in the CP with the control
configurator, INITIALIZE the CP which will clear all the other files
including the CSA files.  
 
 
Terry

____________________________________________________________________________
_________

Russ Boulay   |   Schneider Electric   |   Process Automation  |   United
States   |   Support Engineering Manager
Phone: +1 508 446 1769  |  Mobile: +1 508 446 1769
Email: russ.boulay@xxxxxxxxxxxxxxxxxxxxxx |   Site:
https://support.ips.invensys.com     ;|   Address: Fairfield, California
94534 United States

*** Please consider the environment before printing this e-mail


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Terry Doucet
Sent: Wednesday, September 21, 2016 7:49 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit

Joe,

Removing any station from a system is always difficult in IA without doing a
complete Day0 install.

Not clear if you can get into a specific CP from the control configurator or
not. Are the CP's good in System Management?

If the CP's are good in SysMgmt but you cannot access them in the
configurator, you should be able to clean out a CP by copying the
DB<LBUG>.init  file into DB<LBUG>.UC (checkpoint file) and rebooting the CP
which initializes the CP memory.  Then hopefully you can access the CP in
the control configurator.    When you are in the CP with the control
configurator, INITIALIZE the CP which will clear all the other files
including the CSA files.


Terry

From: Joe@xxxxxxxxxxxxx
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit
Date: Wed, 21 Sep 2016 17:59:53 -0700

Scott,

Thanks for the advice but there is no emergency here...

We wanted to basically remove an AW70 from the Node and move its 
hosting responsibilities to a different, existing AW70.  I followed 
the SysDef and Windows NT Upgrade Considerations manuals as best as I 
could and all appeared to go smoothly, no errors.  It looks like most 
of it is there and not sure if the manuals missed something or I did.
Just looking to the expertise of this group, especially folks like 
yourself, as we all do to help out with the 2 issues:
-  When I open the CIO_Config it appears that all of the Compounds are 
listed but when I pick one I get "CSA Error - CSgetcmpd Failed".  The 
CPs are empty and not even on line because I think I need to move the 
Checkpoint files from the old AW70 to the new one to reboot them; 
maybe?  I was hoping to do a Load_All from the Save_All files and then 
checkpoint them so the Checkpoint files are up to date.
-  If I select the CIO_Station_Config there are no CPs listed.  Is 
that not just a missing cplns type file somewhere?

I want to perform a clean Load_All on the CPs, just not sure when/how 
as nothing was mentioned in the manuals.

Thanks


Joseph M. Riccardi
386-451-7607 Cell

Joe@xxxxxxxxxxxxx

"To give real service you must add something that cannot be bought or 
measured with money; and that is sincerity and integrity." - Donald A.
Adams


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx
[mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Landry, Scott
Sent: Wednesday, September 21, 2016 3:31 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit

   Joe,

    The Field Service organization as an internal Best Practices 
bullet item typically requires our Service Engineers
    to submit a upgrade/system plan doing significant alterations to a 
customer system.

    Do you have a organization that is capable of reviewing, 
commenting and proctoring such installations ?

    My old mentor John Duggar used to say "Poor planning on your part 
does not constitute an Emergency on my part"


   Regards,


    Scott


________________________________________
From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of Boulay, Russ [Russ.Boulay@xxxxxxxxxxxxxxxxxxxxxx]
Sent: Wednesday, September 21, 2016 5:06 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit

That was quite the load of changes.  So was old CP host checkpoint 
files removed, rm_station run to remove former sict table entries. Is 
CSA truly only running in one place now.  There is a whole list of checks.

Sent from my iPhone

On Sep 21, 2016, at 2:48 PM, Joseph M. Riccardi <Joe@xxxxxxxxxxxxx>
wrote:

Russ, et al

Thanks for the lead on the cdrom setup...  As part of the SysDef 
changes, I also wanted to move a System Monitor, the CSA, the ICC, 
and the CP Hosting to a different AW70.  I think the SysDef changes 
were easy enough and the
"5.2.1 Procedure to Move CSA between 70 Series Stations" per V6.1 
Windows NT Upgrade Considerations Manual B0193XL also seemed to go 
smoothly with no errors.

However, when I open the CIO_Config it appears that all of the 
Compounds are listed but when I pick one I get "CSA Error - 
CSgetcmpd Failed".  And if I instead select a Station there are no CPs
listed.
Before starting I ran /opt/fox/ciocfg/api/save_all for all CPs on 
the original AW70, copied them all to the new AW70, but when I run 
/opt/fox/ciocfg/api/load_all for each CP the script just hangs forever.

Where did I go wrong; what did I miss?


Joseph M. Riccardi
386-451-7607 Cell

Joe@xxxxxxxxxxxxx

"To give real service you must add something that cannot be bought 
or measured with money; and that is sincerity and integrity." - Donald
A.
Adams


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx
[mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Boulay, Russ
Sent: Tuesday, September 20, 2016 7:17 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows NT AW70 V6.4 SysDef changes and 
commit

Disable I/A boot from red fox in control panel Reboot PC Install 
appropriate
day0 cdrom for your version Run setup from cdrom From menu that's 
appears select the commit option, or sub menu that gets you there 
Make sure you are using a reconciled day 1 commit



-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx
[mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Joseph M.
Riccardi
Sent: Tuesday, September 20, 2016 6:40 PM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Windows NT AW70 V6.4 SysDef changes and commit

Windows NT AW70 folks,
I revised the SysDef files and created a commit diskette.  There are 
a number of manuals describing the SysDef process up to and 
including creating the commit diskette but I cannot find anything on 
what to do with
it next?
I have done plenty of UNIX boxes (Config/Install_AW) but never a 
WinNT
box.
Anyone remember how to re-commit Windows NT AW70?

Thanks


Joseph M. Riccardi
386-451-7607 Cell

Joe@xxxxxxxxxxxxx <mailto:Joe@xxxxxxxxxxxxx>

"To give real service you must add something that cannot be bought 
or measured with money; and that is sincerity and integrity." - Donald
A.
Adams




______________________________________________________________________
___ This mailing list is neither sponsored nor endorsed by Schneider 
Electric (formerly The Foxboro Company).  Use the info you obtain here 
at your own risks.  See the disclaimer at 
www.thecassandraproject.org/disclaimer.html

foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave





_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html

foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

*** Confidentiality Notice: This e-mail, including any associated or
attached files, is intended solely for the individual or entity to which it
is addressed. This e-mail is confidential and may well also be legally
privileged. If you have received it in error, you are on notice of its
status. Please notify the sender immediately by reply e-mail and then delete
this message from your system. Please do not copy it or use it for any
purposes, or disclose its contents to any other person.
 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 


 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: