It does appear to work that way, which unfortunately has rarely been 
useful to me, for the reasons you cite.  I usually end up doing it in a 
CALC* block.  You might also be able to use a DTIME block with appropriate 
PERIOD and compare the first and last buckets, but I've never tried it.

Corey Clingo
BASF Corporation






"Wilson, Brad" <brad.wilson@xxxxxxxxxxxxxxxx> 
Sent by: foxboro-bounce@xxxxxxxxxxxxx
05/04/2007 10:34 AM
Please respond to
foxboro@xxxxxxxxxxxxx


To
<foxboro@xxxxxxxxxxxxx>
cc

Subject
Re: [foxboro] Rate of Change Alarming






There is nothing in REALM that allows you to qualify how it calculates
the rate of change - I'm guessing it compares inputs from scan to scan
which could result in very erratic reading for flows & pressures.
Temperatures are more steady, so perhaps you slow down the scan rate for
the REALM and see if that helps.

Brad Wilson
brad.wilson@xxxxxxxxxxxxxxxx
Invensys Systems, Inc
1090 King Georges Post Rd, Suite 204
Edison, NJ  08837
732-874-0087


-



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: