You might also consider Calca/Calc blocks and using the memory address
and the avg function to do that. Here is code for a one hour sliding
window using 20 samples at 3 minute intervals.
Note that the RI001 & RI002 values are used to establish the reset value
and decrement amount. The period is one minute. Maybe someone knows a
way to get a better resolution for something like this? You should be
able to connect this to your ROC value and make it work as your 5 min
avg and possible manipulate it to trigger ROC alarming.

NAME   =3D LINE3:37WY2307
  TYPE   =3D CALC
  DESCRP =3D 1 HOUR SLIDING WINDOW
  PERIOD =3D 6
  PHASE  =3D 0
  LOOPID =3D=20
  RI01   =3D :37JI2307.PNT
  HSCI1  =3D 10000
  LSCI1  =3D 0.0
  DELTI1 =3D 1.0
  EI1    =3D KW
  RI02   =3D 2.0
  HSCI2  =3D 100.0
  LSCI2  =3D 0.0
  DELTI2 =3D 1.0
  EI2    =3D %
  RI03   =3D 1.0
  HSCI3  =3D 100.0
  LSCI3  =3D 0.0
  DELTI3 =3D 1.0
  EI3    =3D %
  STEP01 =3D IN RO02
  STEP02 =3D BIP 48
  STEP03 =3D CST
  STEP04 =3D IN M19
  STEP05 =3D STM M20
  STEP06 =3D IN M18
  STEP07 =3D STM M19
  STEP08 =3D IN M17
  STEP09 =3D STM M18
  STEP10 =3D IN M16
  STEP11 =3D STM M17
  STEP12 =3D IN M15
  STEP13 =3D STM M16
  STEP14 =3D IN M14
  STEP15 =3D STM M15
  STEP16 =3D IN M13
  STEP17 =3D STM M14
  STEP18 =3D IN M12
  STEP19 =3D STM M13
  STEP20 =3D IN M11
  STEP21 =3D STM M12
  STEP22 =3D IN M10
  STEP23 =3D STM M11
  STEP24 =3D IN M09
  STEP25 =3D STM M10
  STEP26 =3D IN M08
  STEP27 =3D STM M09
  STEP28 =3D IN M07
  STEP29 =3D STM M08
  STEP30 =3D IN M06
  STEP31 =3D STM M07
  STEP32 =3D IN M05
  STEP33 =3D STM M06
  STEP34 =3D IN M04
  STEP35 =3D STM M05
  STEP36 =3D IN M03
  STEP37 =3D STM M04
  STEP38 =3D IN M02
  STEP39 =3D STM M03
  STEP40 =3D IN M01
  STEP41 =3D STM M02
  STEP42 =3D IN RI01
  STEP43 =3D STM M01
  STEP44 =3D AVE
  STEP45 =3D OUT RO01
  STEP46 =3D IN RI02
  STEP47 =3D OUT RO02
  STEP48 =3D SUB RI03 RO02
  STEP49 =3D OUT RO02
  STEP50 =3D EXIT
END

Ronald G. Schafer
10026 Old Ridge Rd.
Ashland Va. 23009
804-227-4034
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Jaudon, Mike
Sent: Monday, May 07, 2007 11:22 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Rate of Change Alarming

Thanks to Leonardo (DiCapro) Moramarco and Brad Wilson (Pickett) for
your help but there is just one little hiccup I have to work out.

With the 500 DegF in 5 min ROC alarm (1.67 DegF/Min) and the parameters
you guys suggested it worked perfectly (I got the alarm after 5 minutes)
with one exception.

If at any point the ROC dropped below 1.67 (say for 10 seconds at the 2
minute mark) but increased back up and above the 1.67 (from the 2 minute
mark through the 5 minute mark) it would not give an alarm.  It did give
the alarm later, however (at the 7 minute and 10 second mark).

It looks that the rate must be above the 1.67 for 5 consecutive minutes
for the alarm to generate whereas I what I want is "the average ROC of
1.67 for 5 minutes" then generate an alarm.

Corey Clingo mentioned a DTIME block and I believe it will do the
(weighted) average of a measurement over time.  I will see if I can get
this to work.

Thanks to all for your help.

Michael L. Jaudon
TRONOX, LLC
(Technology Group-Hamilton, MS)
(662)343-8710 Office
(662)304-0313 Cell
mike.jaudon@xxxxxxxxxx
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: