[TCUG] Re: Installation Earthing

  • From: "Gursharan Nijran" <Gursharan.Nijran@xxxxxxxxxxxxxxxxxxxxx>
  • To: tcug@xxxxxxxxxxxxx
  • Date: Thu, 26 Sep 2002 15:48:23 +0100

Please note that the Line Earth Loop Impedence is measured from the 
origin of the supply. The LELI of a cable run is governed by the circuit 
protection device operating in 5 seconds. The cable calculations for the 
initial design of a particular cable run of the system should be based 
upon the calculations for the LV cable only. From my calculations based 
upon the manufacteurs Data sheet for 16 x 1.5 sq mm cable which is used by
Nottingham City Council the maximum length for a this cable is 180 mts 
which requires a maximum LELI of 4.58 ohms. This is protected by the 10 
amp BS 88 controller lamp switch card fuse which requires 31 amps to 
disconnect the circuit witin 5 seconds.Please check with your controller 
manufacteur for the rating and type of protective device which protects 
your cable runs from the controller. It should be noted that many of the 
cable runs have an ELV cable running along side of the LV cable thus 
putting the two CPC (circuit protective conductor) i.e. steel wire 
armouring, in parallel thus giving a lower LELI. The ELV cable might not 
take the same route to the poles as the LV cable. Therefore care should 
be taken in what is the true LELI of the cable run.
With regards to corrosion on the swa of the cable it is in the codes of 
practise for the installation of cables that any outer sheathing which is 
removed for gland termination should be made good with equivelent 
materials to prevent corrosion.
If you are installing cable runs in excess of the 180 mts your options 
might be has follows:-
1.) Increase the size of cable to suit your circuit calculations for your 
cable run. i.e  R1 phase conductor  and R2 CPC cross sectional area (csa) 
2.) Increase R2 by the means of an additional CPC run in parallel with 
the LV cable CPC along its length.
The increase in the size of cable and additional R2 is determined by 
circuit calculation.
Tom.Friend(at)nottinghamcity.gov.uk

-----Original Message-----
From: "Probert, Norman (Environmental Services)" 
<NProbert@xxxxxxxxxxxxxxxxxxxxx>
To: tcug@xxxxxxxxxxxxx
Date: Fri, 20 Sep 2002 15:25:15 +0100
Subject: [TCUG] Installation Earthing

> 
 
> We have been looking into providing better earth continuity at
> installations, we believe that the existing method using the armouring
> is no
> longer sufficient and can lead to high readings therefore a separate
> 10mm
> earth conductor should be used from each pole. There are two options
> either
> build this into the existing cable or install a separate armoured cable
> containing earth only. Our problem is that this is a non standard cable
> and
> would have to be purchased in significant quantities 5,000 metres at a
> go,
> we are finding it hard to convince our suppliers that they could offer
> this
> cable to others and we are also reluctant to make the purchase
> ourselves.
> 
> My question is
> 
> A  Does anybody else agree that it is a good idea (if enough took it up
> it
> could become standard instead of special).
> 
> B  Does anybody currently use this type of cable  already and if they
> do who
> makes it.
> 
> C Has anybody got a better idea
> 
> 
> Norman Probert
> Senior Engineer Traffic Control Systems
> 
> Tel 01905-766822
> Email nprobert@xxxxxxxxxxxxxxxxxxxxx
> <mailto:nprobert@xxxxxxxxxxxxxxxxxxxxx>
> 
> 
> 
> **********************************************************************
> Privileged/Confidential information and/or Copyright Material
> may be contained in this email.  The information and Material
> is intended for the use of the addressee(s) only.
> 
> If you are not the addressee or the person responsible for 
> delivering it to the intended addressee(s), you may not copy or
> deliver it to anyone else or use it in any unauthorised manner.
> To do so is prohibited and may be unlawful.  If you receive this
> email by mistake, advise the sender immediately by using the
> reply facility in your email software.
> 
> Any views or opinions presented are solely those of the author
> and do not necessarily represent those of Worcestershire County
> Council.
> 
> Although this email and attachments are believed to be free of any
> virus or other defects which might affect any computer or IT systems
> into which the are received, no responsibility is accepted by 
> Worcestershire County Council for any loss or damage arising in any
> way from the receipt or use thereof.
> 
> **********************************************************************
> -----------------------------------------------------------
> A message from the TCUG mailing list. For information about
> the list visit //www.freelists.org/webpage/tcug
> 
> 
> This footnote also confirms that this email message has been swept by
> MIMEsweeper for the presence of computer viruses
> ***********************************************************************
> *********************************************************************
> 



***************************************************************************
This e-mail (and any attachments) is confidential and may contain personal
views which are not the views of Nottingham City Council unless specifically
stated. If you have received it in error, please delete it from your system,
do not use, copy or disclose the information in any way nor act in reliance
on it and notify the sender immediately. Please note that Nottingham City
Council monitors e-mails sent or received. Further communication will
signify your consent to this.
***************************************************************************
-----------------------------------------------------------
A message from the TCUG mailing list. For information about
the list visit //www.freelists.org/webpage/tcug

Other related posts: