Dirk,

Reading the documentation (Volume 3 of B0193AX - Rev N) suggests that each
FBM can support up to eight PLB blocks.  This is not a feature I have tried
or seen used.


Regards,

Martin Theobald
Senior Support Engineer
Field Engineering Services

Main:   +44 (0) 1925 837 267
Fax:    +44 (0) 1925 831 690
Mob:    +44 (0) 7767 87 1989

Invensys Systems (UK) Ltd.
32 Melford Court,
Hardwick Grange,
Woolston,
Warrington.
WA1 4RZ
United Kingdom




-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx
[mailto:foxboro-bounce@xxxxxxxxxxxxx]On Behalf Of Corey R Clingo
Sent: 12 May 2005 15:58
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Reduce IFL's for FBM


This has been an interesting discussion.  I've personally never used PLBs, 
because I didn't need the processing speed that they give (in truth, I'm 
not sure it's really any faster, but I presume the FBM processes logic at 
a somewhat greater rate than the CP), and I try to avoid YAT (Yet Another 
Tool) unless the benefit warrants it.  But I've never needed PLBs, either; 
CALCA/LOGIC blocks, CINs, COUTs, and GDEVs provide all the tools I have 
ever needed for discrete interlocks.  And locking of appropriate 
parameters (via connection to themselves or other blocks) provides 
adequate protection from changes (though I still would like to see a 
system-wide security mechanism, enforced at the CP level).

Corey Clingo
BASF Corp.







"Dirk Pauwels" <dirkpauwels_1@xxxxxxxxxxx>
Sent by: foxboro-bounce@xxxxxxxxxxxxx
05/12/2005 02:40 AM
Please respond to foxboro

              To:  foxboro 
              cc: 
         Subject:       Re: [foxboro] Reduce IFL's for FBM






We're using PLB's, cause it's the easiest way to configure Interlocks,
unfortunately the number of IFL's also limit the interlocking, so we''re
also using seq/calc etc for interlocking. The disadvantage of using seq 
code
interlocking is that the blocks can still be activated via select. With 
PLB
interlocks, the blocks cannot be operated from the select unless all
interlocks are OK.
For Motor and valve control we use GDEV's and PLB's, for valves we use 2
cin's/ofl's for open/close feedback and 1 CO for open and close. For 
motors
we're only using the running cin/ofl and 1 CO. The ofl's are connected to
the DEVLM's of the GDEV. STAIND is used to show status on screen
We can attach 8 motors to an FBM(2)41 or 42 card, or 4 valves. The number 
of
IFL is not really the limit here, but there are only 8 Co's on a FBM41/42.
Using FBM242 you would have 16 Co's

I'll send Daniel an example offlist.

Rgds,

Dirk Pauwels - DCS coordinator
Engineering dept.
Lawter International BVBA
An RSM Company
Ketenislaan 1c ? Haven 1520
B-9130 Kallo, Belgium
T.  +32.(0)3.570.95.97/ Mob. +32.(0)497.428.300
F.  +32.(0)3.570.16.09
E mail: dirk.pauwels@xxxxxxxxxx







 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: