Re: [foxboro] PIO Bus Errors

  • From: "Tadeo Armenta" <dmarc-noreply@xxxxxxxxxxxxx> (Redacted sender "tadeoarmenta" for DMARC)
  • To: "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>
  • Date: Tue, 19 Jun 2018 20:59:29 +0000 (UTC)

sible replace the fieldbus terminator. Check for suspect faulty field 
signals.FBM age - If FBMs are older than 2005 they might be subject to the 
advisory others suggested, Newer FBMs are more susceptible, so, probably the 
"worst offender" FBM is actually the newest one, he just expects a cleaner 
signal than the older ones. Having all of them in the latest image doesnt hurt. 
As Russ explained, old vertical baseplates are a problem. The trick with the 
FBM in the end of the fieldbus is FCM100 as previously stated, this "clean" the 
signal.FDSI FBMs - Not your case, but its been known that when there are comm 
issues between FDSI FBMs and external devices, these introduce PIOBUS errors to 
the system. Particularly painful, as the PIOBUS error most times doesn't show 
on the FDSI FBM, but on any other.FCP270 Rev 0U or lower - One of the symptoms 
of the faulty optocoupler is the appearance of PIOBUS errors. Try swapping the 
FCP270 modules with good know spares.
Good luck





    El domingo, 17 de junio de 2018 4:15:06 a. m. GMT+12, Steinbrecher, Nick 
<E.Steinbrecher@xxxxxxxxxxxx> escribió:  
 
 Thanks for the suggestion, Our FBM233 are in the last slot of the baseplate.
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On ;
Behalf Of Michael Jaudon
Sent: Friday, June 15, 2018 3:41 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] PIO Bus Errors

The facility I work at, Tronox, has had similar issues on two different CPs. 
Our field service rep installed an FBM (can’t remember the type) in the 
last position in the backplate and the errors went away. He did this for both 
CPs. They are still installed today. If I was at the plant site today I would 
tell you the type of FBMs.
On Fri, Jun 15, 2018 at 1:07 PM Steinbrecher, Nick < 
E.Steinbrecher@xxxxxxxxxxxx> wrote:

We have a similar problem on a PIO bus from CP270.  Ours happens every 
few minutes constantly but does not cause errors in the CP, just the 
system PIO bus errors listed below.  We are trying to decide how to 
pursue fixing this.  Look forward to any ideas that come forth.

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx 
[mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Smith, Roger
Sent: Friday, June 15, 2018 12:27 PM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] PIO Bus Errors

Honorable List,
We are getting the following sysmon errors intermittently.

2018-06-08 14:04:36 07CP03 Equip = 070404 SYSMON -00068 Single PIO Bus 
Access Error on A
2018-06-08 14:04:36 07CP03 Equip = 070404 SYSMON -00070 Single PIO Bus 
Access Recovery on A

The errors are occurring on all 9 FBM's in a cabinet.  The FBM's are 
on 2 separate racks.  Always A channel.  We replaced one FBM that was 
the most frequent offender but that did not solve the problem.  The 
most recent spate of errors started last Friday afternoon at the same 
time we had a thunderstorm/downpour.  They occurred 56 times over the 
weekend ending Sunday afternoon and have not occurred since.  (It 
hasn't rained since then either).

Has anyone else seen something similar?

Thanks,

Roger Smith



______________________________________________________________________
___ This mailing list is neither sponsored nor endorsed by Schneider 
Electric (formerly The Foxboro Company).  Use the info you obtain here 
at your own risks.  See the disclaimer at 
www.thecassandraproject.org/disclaimer.html

foxboro mailing list:  Â  Â  Â  Â  Â  Â  
//www.freelists.org/list/foxboro
to subscribe:  Â  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave




______________________________________________________________________
___ This mailing list is neither sponsored nor endorsed by Schneider 
Electric (formerly The Foxboro Company).  Use the info you obtain here 
at your own risks.  See the disclaimer at 
www.thecassandraproject.org/disclaimer.html

foxboro mailing list:  Â  Â  Â  Â  Â  Â  
//www.freelists.org/list/foxboro
to subscribe:  Â  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


--
Michael Jaudon Sent from iPhone

 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric 
(formerly The Foxboro Company).  Use the info you obtain here at your own 
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:  Â  Â  Â  Â  Â  Â  //www.freelists.org/list/foxboro
to subscribe:  Â  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:  Â  Â  Â  Â  Â  Â  //www.freelists.org/list/foxboro
to subscribe:  Â  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:  Â  Â  Â  mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

  
 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: