To expand on what Alex said, look at the interaction between INHIB and INHOPT. When INHIB is toggled, the action is determined by the value of INHOPT. INHOPT=0 will result in msgs being suppressed but detection continues. INHOPT=1 will result in both msgs and detection being suppressed. I suppose in I/A-speak, when INHIB is true, INHOPT=0 is an inhibited alarm, and INHOPT=1 is a disabled alarm. INHOPT=2/3 are the same as 0/1 with the addition that return-to-normal states are automatically acknowledged for uninhibited alarms. When INHIB is toggled, it will invoke INHOPT actions for ALL alarms in the block. Although I've never used the feature, it appears you can inhibit alarms individually by setting bits of INHALM. It appears the INHOPT setting applies to any alarm so inhibited. There is no way to, say, inhibit high meas alarming (suppress msgs only) and disable output alarming (suppress both msgs and detection) at the same time. Since INHOPT is noncon/nonset, if you want to have both capabilities in a block (inhibit sometimes, disable sometimes), I think you'd probably want to set INHOPT=1 and use INHIB to disable alarming (no detection) and redirect the alarm group to block msgs only (while still allowing detection). Brad Wilson brad.wilson@xxxxxxxxxxxxxxxx Invensys Process Systems, Inc 1090 King Georges Post Rd, Suite 204 Edison, NJ 08837 732-661-4012 o 732-874-0087 c -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Johnson, Alex P (IPS) Sent: Tuesday, October 21, 2008 7:41 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] More Process Summary Reporter Quirks Virgil, I can't answer all of your questions, you need a PSR expert and I'm not one. However,... Re: As far as I know, Foxboro only uses the term Inhibited alarm, not disabled alarm. The I/A Series supports both alarm inhibition and alarm disable options. An inhibited alarm will detect the alarm and set the alarm indication status bits, but it will not send the message to any configured alarm destinations. A disabled alarm will not detect the alarm, will not set the alarm indication status bits, and will not send a message to the configured alarm destinations. The difference between a disabled alarm and an un-configured alarm is that the disable function is one that can be changed without using the control configurator. If the alarm has never been configured, you must use the control configurator to enable it. Whereas, if you configure it and disable it, you can restore its operation at any time through your HMI. Make some sense? Regards, Alex Johnson Invensys Process Systems 10900 Equity Drive Houston, TX 77041 713 329 8472 (desk) 713 329 1600 (operator) 713 329 1944 (SSC Fax) 713 329 1700 (Central Fax) alex.johnson@xxxxxxxxxxxxxxxx * Confidentiality Notice: This e-mail and any associated files are intended solely for the individual or entity to whom they are addressed. Please do not copy it or use it for any purposes, or disclose its contents to any other person. Further, this e-mail and any associated files may be confidential and further may be legally privileged. This email is from the Invensys Process Systems business unit of Invensys plc which is a company registered in England and Wales with its registered office at Portland House, Bressenden Place, London, SW1E 5BF (Registered number 166023). For a list of European legal entities within the Invensys Process Systems business group, please click here http://www.invensys.com/legal/default.asp?top_nav_id=77&nav_id=80&prev_id=77. If you have received this e-mail in error, you are on notice of its status. Please notify us immediately by reply e-mail and then delete this message from your system. Thank you for your co-operation. You may contact our Helpdesk on +44 (0)20 7821 3859 / 2105 or email inet.hqhelpdesk@xxxxxxxxxxxxx This e-mail and any attachments thereto may be subject to the terms of any agreements between Invensys (and/or its subsidiaries and affiliates) and the recipient (and/or its subsidiaries and affiliates). _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave