I have the problem detailed below in this CAR. I wonder if it has fixed because 
in the systems I have, the problem still exists. I have systems with versions 
6.2.1, 6.5.2 and 7.1 with DM and FV, and the detail displays have not been 
fixed.
ISSUE:
Alarm deadband was not selectable for a particular AIN in SELECT, and yet
it was for other AIN blocks. The Deadband was not secured in the
configurator.  When I changed the HLOP from 2 to 1, the DB parameter was
then selectable in the configurator.  I was on the phone with TAC (RH) when
I discovered the work-around. Parameter was not selectable from either WP30
or Remote
Disp Mgr. on AW51.
HAL=      :AI1505_AIN.HAL.50
LAL=     -20.
HLPR=      1
HLGP=      1
HHAOPT=    0

RESPONSE:
11/07/97 - Response from TAC (LM):
Problem Workaround:
To enable the measurement deadband pick, "MEASDB", on the "ALARMS" overlay
for an AIN block when the "HLOP" option is set to 2, the following
procedure may be used:
       -  Using the Display Builder, load display file
          "/usr/fox/dd/ain/AIN_09"
       -  The measurement fields are covered over with filled
           rectangles and therefore should be moved for ease of
           selecting the rectangle pick for configuring. Therefore,
           place pointer in the right box under the "MEASUREMENT"
           section, select the field and move it to the right.
       -  Save file and enter the Display Configurator.
       -  Select the rectangle for the "MEASDB" field.
       -  Select "DISPLAY" from the top menu bar.
       -  Select "visibility" from the pull down menu.
       -  Set "State 2" to 1.
       -  Select "ok" and save file.
       -  Re-enter Display Builder and move the cover boxes to
          the original position.
Problem Action:
The correction for the AIN Alarm overlay for the 20 and 50 Series is
currently planned to be part of I/A Software Release V4.2.5 and V6.1.
This CAR is now closed

CAR #: 10560            Ver.: 4.2.2          STATUS : CLOSED
PRODUCT CAT : DISPLAY                 PRODUCT TYPE: DEFAULT DISP
REPORT DATE : 9/30/97


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts:

  • » [foxboro] Detail Display AIN Deadband pick problem - QUEIROLO OLIVERA, IGNACIO ESTEBAN