Well, we use Aspen IP.21, but we have similar issues.  We use a plant 
prefix, then an underscore, then the I/A tag (minus the compound), like 
so:
HA2_FI100.PNT

If the tag is not unique in a plant (it happens sometimes with I/A because 
the system only enforces tag uniqueness within a compound), we may add 
part or all of the compound name in there:

HA2_R110_FI100.PNT

where R100 is the compound name or some abreviation thereof (IP.21 limits 
standard tag point names to 24 characters).

This makes it easier to write scripts to bulk-load the IP.21 system from 
the I/A configuration.

Corey Clingo
BASF Corp.







"Clement, Mark (KIDDMET)" <MClement@xxxxxxxxxxxxxxxxxxxxxxxx>
Sent by: foxboro-bounce@xxxxxxxxxxxxx
03/04/2005 12:37 PM
Please respond to foxboro

              To:  "'foxboro@xxxxxxxxxxxxx'" 
              cc: 
         Subject:       Re: [foxboro] OSI tags for Foxboro I/A






Hi All,

What does everyone use as a tag naming convention ?
Just loops numbers or combination loop# and area # or something better ?
What works best from end user perspective ?

Regards
Mark


-----Original Message-----
From: WMagda@xxxxxxx [mailto:WMagda@xxxxxxx]
Sent: Friday, March 04, 2005 1:38 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] OSI tags for Foxboro I/A


I agree with Brad, PI-SMT is the way to go using Excel.  We started using
PI last September.  It took us a few tries, but once you have it figured
out, it is easy to add/delete as needed.
Wally Magda

IE&C Spec Sr
Colorado Springs Utilities
PO Box 214
660 W. Monument Creek Rd
USAF Academy, CO   80840
719.668.9502 office
wmagda@xxxxxxx



brad.s.wilson
Sent by: foxboro-bounce@xxxxxxxxxxxxx
03/03/2005 10:33 AM
Please respond to
foxboro@xxxxxxxxxxxxx


To
foxboro@xxxxxxxxxxxxx
cc

Subject
Re: [foxboro] OSI tags for Foxboro I/A






I remember the problems I had first setting up PI to read Foxboro ... but
once you know it, it's soooo easy.  PI-SMT is definitely the way to go ...
it's an Excel add-in which provides a drop-down menu on the top Excel
command line.  From that drop-down menu, you can either upload PI
configuration data to the spreadsheet, or download from the spreadsheet to
the PI configuration.  The macros that are employed are exactly the same
as
the script files you would run if you were doing the configuration in DOS,
so I think it should work for older versions of PI also.

The most difficult thing, as I remember, was getting the location tags
correct ... location1 is an address that points to the source (in our case
101 is our AW51, when I get my other AW hooked up, that will be 102).
location2 is the collection group on the DCS (this was the most difficult
thing for me to understand, but I'm set up with 2 groups per CP - one for
analog points, one for digital points), location3 works with the type of
data (we have 3 is 32-bit floating, 5 is digital).  This is explained
pretty well in the PI manuals, but those CP collection groups really had
me
going for a while.

The pointsource parameter differentiates the type of source device (in our
case, F=Foxboro, D=Yokagawa, C=calculated, A=Allen-Bradley, etc).

The exdesc parameter holds the DCS C:B.P reference

Using discrete inputs requires defining Digital Sets in PI which hold all
the potential values that the input may be.  For example, you might have a
Digital Set called VALVESTATESET which contains the values Open, Closed,
Opening, Closing, Mismatch ... these would correspond to the various
values
that a GDEV.STAIND might return.  That way, rather than seeing the STAIND
integer values in your PI archive, you'd see the text values.

Everything else I think is fairly straightforward.

Brad Wilson
ExxonMobil Chemical Co
Edison Synthetics Plant
732-321-6115
732-321-6177 fax
Brad.S.Wilson@xxxxxxxxxxxxxx



_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave






_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave



The Noranda/Falconbridge Anti-Virus System has scanned this
message/attachment(s) for viruses.


_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave





 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: