The HOA status is not available to the DCS. The GDEV actually uses COUT_1 to start the device (connected to one BOUT block) and COUT_2 to stop it (connected at a different BOUT). I am in contact with the Invensys engineer who built this. Thanks to all for your replies. Tim Lowell Tesoro | 210-439-5914 (cell) On May 18, 2012, at 10:06 AM, "Rick Mol" <Rick.mol@xxxxxxxxxxxxxxx> wrote: > Tim, > > It sounds like you have a good handle on the basic config, the rest of this > discussion is about handling field starts and alarming. > > The NOT Auto switch refers to the state of the field HOA switch if that is > brought into the DCS. (sometimes the Auto contact is brought into the DCS). > It may be available via the link or may be a discrete input. > > The suggestion was to use that signal, if available, to inhibit alarming > (along with INHOPT) on field start. > > It depends on how the HOA switch control is setup, can the DCS stop the > motor after a field start or not. If so, use of the DSR_RB is a better way > to go, otherwise the operators may want to know that the motor is in hand > and running from the field. > > > Regards, > Rick Mol > Coyote Technologies > 231.750.6348 > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Lowell, Timothy > Sent: Friday, May 18, 2012 12:18 PM > To: 'foxboro@xxxxxxxxxxxxx' > Subject: Re: [foxboro] GDEV configuration > > Doug et al, > > Let me see if I understand what you all are saying. > > The actual driving block is a BOUT on the FDSI. You are saying that DSR_RB > should be connected to its output (.BOUT, I think). > > DEVLM2 should be the feedback from .B1 of the device PAKIN block. > > AVLIM2 = 1 tells the GDEV to use DEVLM2. > > Does that sound right? > > I'm still not clear what to do about the hand switch. These GDEVs are locked > in Manual. Nothing should be starting or stopping the device but a board > operator using the GDEV on a graphic or an outside operator using the > outside hand switch. Using AUTDSR therefore is not an option, if I am > reading the block book correctly. Rick said something about the NOT Auto > switch. I'm not sure what that means. > > Thanks, > > Tim Lowell > Tesoro Corporation | 54741 Tesoro Rd, Kenai, AK 99611 | 907-776-3526 (work) > | 210-439-5914 (cell) > > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Douglas G. Lloyd > Sent: Friday, May 18, 2012 9:05 AM > To: foxboro@xxxxxxxxxxxxx > Subject: Re: [foxboro] GDEV configuration > > Tim, > > The DSR_RB parameter should be connected to whatever final signal you have > available that is actually driving the device. Limit switch checking is > based on the DSR_RB status if it is connected. Otherwise, it's based on the > DSRIND (i.e. the block drive request from AUTDSR, MANDSR, INTDSR, HLDDSR, > etc). The detail display colors need some interpretation if DSR_RB is > different than DSRIND, but it's not too tough once your operators understand > the patterns... > > If you have no status connection available from whatever is actually driving > the device, you'll lose limit switch versus output verifications. But, you > can still configure the block to display the actual status (i.e. connect > DSR_RB to the actual device state)... > > Regards, > Doug > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Lowell, Timothy > Sent: Friday, May 18, 2012 12:38 PM > To: 'foxboro@xxxxxxxxxxxxx' > Subject: Re: [foxboro] GDEV configuration > > Joseph, > > There is a hand switch between the GDEV and the MCC. I'm sorry if I didn't > make that clear. What do you typically do in this situation? It looks like I > have some other ideas from Rick and Corey. > > Thanks all, > > Tim Lowell > Tesoro Corporation | 54741 Tesoro Rd, Kenai, AK 99611 | 907-776-3526 (work) > | 210-439-5914 (cell) > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Joseph M. Riccardi > Sent: Friday, May 18, 2012 8:38 AM > To: foxboro@xxxxxxxxxxxxx > Subject: Re: [foxboro] GDEV configuration > > Tim, > > "All of the #2s should not be connected or set to the opposite condition." > Could you elaborate on this statement? What do you mean by #2's? > Oops, I meant 1s; DEVLM1, IGNLM1, AVLLM1. The GDEV is also used for Valves > where you may have 2 limit switches (DEVLM1 & 2) as open/closed feedback. > > As long as there is no other device between the GDEV and the MCC that could > bypass the GDEV command, nothing else should be required to get what you > want. > > Joseph M. Riccardi > > 386-441-0250 Office > 386-451-7607 Cell > > Joe@xxxxxxxxxxxxx > > "To give real service you must add something that cannot be bought or > measured with money; and that is sincerity and integrity." - Donald A. Adams > > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Lowell, Timothy > Sent: Friday, May 18, 2012 12:21 PM > To: 'foxboro@xxxxxxxxxxxxx' > Subject: Re: [foxboro] GDEV configuration > > Joseph, > > Thanks for the reply. > > "All of the #2s should not be connected or set to the opposite condition." > > Could you elaborate on this statement? What do you mean by #2's? > > The device between the GDEV and the MCC is an Eaton C441 Monitoring Relay. > Basically, you connect it to a switch that is also connected to the FDSI > FBM, and it can monitor the device statuses and turn things on and off. It's > pretty simple with no logic solver in it. > > Thanks, > > Tim Lowell > Tesoro Corporation | 54741 Tesoro Rd, Kenai, AK 99611 | 907-776-3526 (work) > | 210-439-5914 (cell) > > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Joseph M. Riccardi > Sent: Friday, May 18, 2012 8:12 AM > To: foxboro@xxxxxxxxxxxxx > Subject: Re: [foxboro] GDEV configuration > > Tim, > > You have lots of options but the basic connection for the motor Run feedback > is DEVLM2. DEVLM2 Device Limit Switch 2 is a boolean input for reading the > Opened/Running limit switch. When DEVLM2 is true, the device is > Opened/Running. > > Make sure it is not ignored; IGNLM2 = 0. And it is configured as available; > AVLLM2 = 1. > > All of the #2s should not be connected or set to the opposite condition. > > The big question is, do you have anything between the GDEV and the MCC; > i.e., a PLC, HOA, etc. > > Joseph M. Riccardi > > 386-441-0250 Office > 386-451-7607 Cell > > Joe@xxxxxxxxxxxxx > > "To give real service you must add something that cannot be bought or > measured with money; and that is sincerity and integrity." - Donald A. Adams > > -----Original Message----- > From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On > Behalf Of Lowell, Timothy > Sent: Friday, May 18, 2012 11:33 AM > To: 'foxboro@xxxxxxxxxxxxx' > Subject: [foxboro] GDEV configuration > > List, > This one should be easy for the list. We are upgrading our Motor Control > Centers, and we have some fancy new MCC buckets that can talk over Ethernet > to an FDSI block. Someone decided it would be a good idea to allow the board > operator to turn the pumps and exchanger fin fan motors on and off from the > DCS, as well as being able to operate them locally as they always had done > in the past. Previously, if we needed a pump or fin fan motor started, the > only option was to send an operator out to do it. In most cases, we didn't > even have feedback status for the pump or fin fan motor, but now we do. > > Since this project was run by an Electrical Engineer who can barely spell > I/A, he didn't put much consideration into the graphics or DCS configuration > until very late in the game, and he ended up farming the job out to Invensys > at the last minute. The Invensys engineer he hired was already on site > helping us with a cutover, and he had to throw something together in his > "spare" time. He did a very thorough and complete job with the information > he was given and with the time constraints he had, but unfortunately, he had > to leave and go to another job, and now what we have isn't quite right. > > The Invensys Engineer used GDEV blocks on the graphic to start and stop the > field devices. What we are seeing is that the feedback from the status bits > is not configured correctly. The GDEV currently does not know what the > status of the device is. If you call up the Detail Display of one of the > GDEV blocks, it is in whatever position it was left at by the graphic, even > if someone has started or stopped the device locally with a field switch. > > My question is, how do you properly configure a GDEV for ON/OFF status > feedback? There are all these options, and the block book is not > particularly helpful in deciphering which to use or not use. We basically > want the GDEV block to know what the status of its device is, so that when > we click on the device, it knows whether to prompt us to start it if it is > off, or to stop it if it is on. Right now, the GDEV is assuming that > whatever the last command we sent to it is the status of the device, which > isn't necessarily true. The device status comes back to the DCS via the > first bit of an FDSI PAKIN block, but I haven't had any luck figuring out > which parameter on the GDEV to connect it to. There is only a RUNNING bit, > and no OFF bit; that is, you can only tell the device is OFF if the RUNNING > bit is zero. > > If I could get Invensys to work on this, I would, but it's not easy > traveling to Alaska, and I think this should be an easy fix. > > Thanks, > > Tim Lowell > Tesoro Corporation | 54741 Tesoro Rd, Kenai, AK 99611 | 907-776-3526 (work) > | 210-439-5914 (cell) > > > > _______________________________________________________________________ > This mailing list is neither sponsored nor endorsed by Invensys Process > Systems (formerly The Foxboro Company). Use the info you obtain here at > your own risks. Read http://www.thecassandraproject.org/disclaimer.html > > foxboro mailing list: //www.freelists.org/list/foxboro > to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join > to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave > > > > > > _______________________________________________________________________ > This mailing list is neither sponsored nor endorsed by Invensys Process > Systems (formerly The Foxboro Company). Use the info you obtain here at > your own risks. Read http://www.thecassandraproject.org/disclaimer.html > > foxboro mailing list: //www.freelists.org/list/foxboro > to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join > to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave > _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave