Scott,
Thanks for your answer!
If IOM Image Revision is the same as SOFTWARE REV in the EQUIP INFO page of 
SMDH, then I guess my FBM230 cannot be upgraded to the latest modbus driver, as 
it is Rev 1.03. I guess I have to do some EEPROM upgrade before.

I'm already in the process of contacting my local Field Service for the 
upgrade. 

Regards

Pablo Lioi
> From: Scott.Landry@xxxxxxxxxxxxxxxxxxxxxx
> To: foxboro@xxxxxxxxxxxxx
> Date: Sat, 14 Mar 2015 07:15:00 -0400
> Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> 
> 
> 
>     Pablo,
> 
> 
>     You sure did leave a lot out of information about your hardware 
> configuration at first.
> 
>     the latest Modbus driver is V2.4 not V2.3.4, release notes below;
> 
>     Contact local Schneider/Foxboro Field Service and/or one the 
> Schneider/Foxboro/Triconex Global Technical Assistance Centers
>     for a driver download.
> 
> 
>     Release notes for FDSI Modbus driver Rev 2.4 (June 12, 2014)
> --------------------------------------------------------------------------------
>  1. Driver Revision and CRC:
>     The driver name and identification are Modbus.ziph Rev 2.4 with CRC 
> e48892e0
>  2. IOM Image dependency:
>     IOM Image revision 1.30, or later, is required for the FBM230, FBM231,
>     FBM232, and FBM233 to run the FDSI Modbus 2.4 driver.
>  3. Bugs Fixed:
>     a. CAR#1156899: The OVERSCAN diagnostic counter keeps on incrementing even
>        if there is no overscan. Modified driver to consider 100 ms additional
>        time to address scheduling overhead in calculating over scan.
>     b. CAR#1165368: The driver is sending more than 125 registers in a single
>        query when points are configured with data types like  S2, U2, U4 or S4
>        options. Modified driver group logic to consider the data type of the 
> point.
>     c. CAR#1189734: In FBM233 setup, the driver is marking the device ECB201
>        to invalid device when the device address is specified in the range 
> from
>        248 to 254 using +MN= option. Modified driver to support device address
>        range from 0 to 255.
>     d. In FBM230/FBM231 setup, the write only points are resetting to initial
>        values (point value which was set at the time of point configuration)
>        after downloading modified port configuration file. Modified driver to
>        set write only points with last updated value after port configuration
>        file download.
>     e. In FBM233 setup, the driver shows frequent role switch messages in the
>        smon log during long run when the time out is configured as 100 ms 
> (+TO=1).
>        Modified driver to re-establish the communication with the device 
> before
>        last retry of the message.
> 
> 
>    Regards,
> 
> 
>     Scott
> 
> 
> 
> ________________________________________
> From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On Behalf 
> Of Pablo Lioi [plioi@xxxxxxxxxxx]
> Sent: Friday, March 13, 2015 6:51 PM
> To: foxboro@xxxxxxxxxxxxx
> Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> 
> I would like to share my conclusions about this problem so far, as I think 
> they may be useful for others.
> In my original post I omitted some details for the sake of simplicity, but 
> now I will describe my problem and findings more thoroughly.
> Right now I have an FBM230 talking to a Fisher ROC using Modbus RTU over 
> RS232, at 9600 bps, on port 3. This communication is working ok.
> I want to modify my system so that I can use Port 3 to communicate with 3 
> (networked) Fisher ROCs using Modbus/TCP. So I installed a Modbus Serial to 
> Modbus TCP Gateway (Schneider TSX ETG100), connected Port 3 of the FBM230 to 
> the serial port of the gateway and the Ethernet Port of the gateway to the 
> ROC network. My first test was to read one register from the same ROC I was 
> previously reading over RS-232. The ROC replies and the gateway converts the 
> response back to Modbus RTU and sends it to the FBM230, but the FBM230 
> discards the message and retries.
> I know for sure that settings, cables, dip switches, etc., are Ok, because 
> I'm monitoring the line with a protocol analyser. As I stated before, I've 
> already had problems with slaves that replied too quickly to polls from the 
> FBM230, so this time I made some measurements with the protocol analyser. The 
> results are as follows:
> In my original configuration, with the FBM230 reading from the ROC over RS232 
> at 9600 bps, the time between the last byte of the query and the first byte 
> of the response message is 16 ms.
> In my new configuration, with the FBM230 connected to the gateway al 9600 
> bps, the time between the last byte of the query and the first byte of the 
> response message is 8 ms. If I change the baudrate to 38400 bps, the time 
> goes down to 5 ms.
> Conclusions so far:
> - In my new configuration, the difference in response time between 9600 and 
> 38400 bps is due to the 3.5 char times the gateway waits to mark the end of 
> the incoming message on the serial port. At 9600 bps, this time is 3.4 ms and 
> at 38400, 0.8 ms. As nothing changes on the Ethernet side, I am assuming that 
> the time it takes for the gateway to convert the message, send it to the ROC 
> over Ethernet and get the response is the same in both cases (4.5 ms, more or 
> less).
> - The FBM230 modbus master driver software is doing something (flushing the 
> receive buffer, probably) that doesn't allow it to cope with responses that 
> arrive in less than, lets say, 10 ms.
> - The only solution I see is to install a gateway with a configurable 
> response delay on the RS-232 side, or something to that effect.
> Thanks to everybody
> Regards
> Pablo Lioi
> Total Austral S.A.
> Tierra del Fuego - Argentina
> 
> > From: dmarc-noreply@xxxxxxxxxxxxx
> > Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> > Date: Thu, 12 Mar 2015 12:15:59 -0400
> > To: foxboro@xxxxxxxxxxxxx
> >
> > I believe if you can produce the foxboro PO or sales order they will send 
> > you an updated driver at no cost. It will be a computer transfer.
> >
> > Sent from my iPhone
> >
> > > On Mar 12, 2015, at 11:00 AM, Pablo Lioi <plioi@xxxxxxxxxxx> wrote:
> > >
> > > Scott,
> > > As I stated before, my driver is version 1.1 and I am using B0700BG-C.
> > > Supported device counters are Good Messages Sent, Good Messages Received 
> > > and Timeouts.
> > > I suppose I should upgrade the driver...
> > > Regards
> > > Pablo Lioi
> > >> From: Scott.Landry@xxxxxxxxxxxxxxxxxxxxxx
> > >> To: foxboro@xxxxxxxxxxxxx
> > >> Date: Thu, 12 Mar 2015 08:51:55 -0400
> > >> Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> > >>
> > >>
> > >>
> > >>    Pablo,
> > >>
> > >>
> > >>    Latest Modbus driver is V2.3.4   (B0700BG-J document)
> > >>
> > >>    If you are using RS-422 or RS-485;
> > >>
> > >> Set the RS-232 switches for the channel such that the C5 and C6 switches 
> > >> are in
> > >> the CLOSED position and the rest of the switches are in the OPEN 
> > >> position (see
> > >> Figure 4-15 on page 39).
> > >>
> > >>
> > >>
> > >>    Something else I do when I set a FDSI interface up is configure all 
> > >> the port and device counters, possible.
> > >>    I also have a graphic I re-use so they are easy to see (depends on 
> > >> the driver)  some drivers
> > >>    have a script to build the blocks and graphic(s).  Although not 
> > >> Modbus driver.
> > >>
> > >>
> > >> Port Counters:
> > >> 1. Number of good messages sent
> > >> 2. Number of good messages received
> > >> 3. Number of parity errors
> > >> 4. Number of framing errors
> > >> 5. Number of checksum errors
> > >> 6. Number of transmit errors
> > >> 7. Port Scan Time
> > >> 8. Reset Counters
> > >>
> > >> Device Counters:
> > >> 1. Number of good messages sent
> > >> 2. Number of good messages received
> > >> 3. Response timeout
> > >> 4. Number of Modbus Device Exception responses
> > >> 5. Number of Modbus gateway exception responses
> > >> 6. Last Error message received from the gateway
> > >> 7. Configured Options
> > >> 8. Number of Over Scans
> > >> 9. Over Scan time high
> > >> 10. Group Scan time
> > >>
> > >>
> > >>   Regards,
> > >>
> > >>
> > >>    Scott
> > >>
> > >> ________________________________________
> > >> From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On 
> > >> Behalf Of Landry, Scott [Scott.Landry@xxxxxxxxxxxxxxxxxxxxxx]
> > >> Sent: Thursday, March 12, 2015 7:14 AM
> > >> To: foxboro@xxxxxxxxxxxxx
> > >> Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> > >>
> > >>    Pablo,
> > >>
> > >>
> > >>    Try playing with the driver scan rate, slower and faster.  See what 
> > >> difference it makes, if any.
> > >>
> > >>    Are you using an xml  device config file ?
> > >>
> > >>
> > >>    Regards,
> > >>
> > >>
> > >>    Scott
> > >>
> > >> ________________________________________
> > >> From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On 
> > >> Behalf Of Pablo Lioi [plioi@xxxxxxxxxxx]
> > >> Sent: Thursday, March 12, 2015 5:10 AM
> > >> To: foxboro@xxxxxxxxxxxxx
> > >> Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> > >>
> > >> I'm using RTU, but my communication is not a radio link. The FBM230 and 
> > >> the slave are inside the same cabinet.
> > >>
> > >>> From: dmarc-noreply@xxxxxxxxxxxxx
> > >>> Subject: Re: [foxboro] FBM230/Modbus slave too fast problem
> > >>> Date: Wed, 11 Mar 2015 15:18:10 -0400
> > >>> To: foxboro@xxxxxxxxxxxxx
> > >>>
> > >>> Are you using Modbus rtu or ASCII? On radio units I have had better 
> > >>> luck with Modbus ASCII.
> > >>>
> > >>> Sent from my iPhone
> > >>>
> > >>>> On Mar 11, 2015, at 1:28 PM, Pablo Lioi <plioi@xxxxxxxxxxx> wrote:
> > >>>>
> > >>>> Hi everybody,
> > >>>> I'm sending this again because for some reason carriage returns seem 
> > >>>> to have been lost and the post was difficult to read.
> > >>>> In the past I had a serious problem with an FBM230 with Modbus 
> > >>>> protocol communicating with a slave using RS-232, in RTU mode.
> > >>>> When the slave response to any query from the master arrived too fast, 
> > >>>> the FBM would ignore the response and retry. I finally worked around 
> > >>>> the problem delaying the response from the slave a few milliseconds 
> > >>>> using a setting (at the slave device) that was meant for radio 
> > >>>> communication (RTS to TxD delay).
> > >>>> I am now facing the same problem again, with another slave device. The 
> > >>>> problem is that this time I have no way to delay the slave response. I 
> > >>>> tried using RTS/CTS handshake on the RS-232 line, but the problem 
> > >>>> remains. I know for sure that cable and switch settings at the TA are 
> > >>>> ok because I'm looking at the line with a protocol analyser and see 
> > >>>> correct query and response messages.I would like to know if somebody 
> > >>>> else has experienced this problem too.
> > >>>> Regards
> > >>>> Pablo Lioi
> > >>>> TOTAL AUSTRAL S.A.
> > >>>> Tierra del Fuego - Argentina
> > >>>>
> > >>>>
> > >>>>
> > >>>> _______________________________________________________________________
> > >>>> This mailing list is neither sponsored nor endorsed by Invensys Process
> > >>>> Systems (formerly The Foxboro Company). Use the info you obtain here at
> > >>>> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> > >>>>
> > >>>> foxboro mailing list:             //www.freelists.org/list/foxboro
> > >>>> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > >>>> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> > >>>
> > >>>
> > >>> _______________________________________________________________________
> > >>> This mailing list is neither sponsored nor endorsed by Invensys Process
> > >>> Systems (formerly The Foxboro Company). Use the info you obtain here at
> > >>> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> > >>>
> > >>> foxboro mailing list:             //www.freelists.org/list/foxboro
> > >>> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > >>> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> > >>
> > >>
> > >>
> > >> _______________________________________________________________________
> > >> This mailing list is neither sponsored nor endorsed by Invensys Process
> > >> Systems (formerly The Foxboro Company). Use the info you obtain here at
> > >> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> > >>
> > >> foxboro mailing list:             //www.freelists.org/list/foxboro
> > >> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > >> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> > >>
> > >>
> > >> ______________________________________________________________________
> > >> This email has been scanned by the Symantec Email Security.cloud service.
> > >> ______________________________________________________________________
> > >>
> > >> *** Confidentiality Notice: This e-mail, including any associated or 
> > >> attached files, is intended solely for the individual or entity to which 
> > >> it is addressed. This e-mail is confidential and may well also be 
> > >> legally privileged. If you have received it in error, you are on notice 
> > >> of its status. Please notify the sender immediately by reply e-mail and 
> > >> then delete this message from your system. Please do not copy it or use 
> > >> it for any purposes, or disclose its contents to any other person.
> > >>
> > >>
> > >> _______________________________________________________________________
> > >> This mailing list is neither sponsored nor endorsed by Invensys Process
> > >> Systems (formerly The Foxboro Company). Use the info you obtain here at
> > >> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> > >>
> > >> foxboro mailing list:             //www.freelists.org/list/foxboro
> > >> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > >> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> > >>
> > >>
> > >> ______________________________________________________________________
> > >> This email has been scanned by the Symantec Email Security.cloud service.
> > >> ______________________________________________________________________
> > >>
> > >> *** Confidentiality Notice: This e-mail, including any associated or 
> > >> attached files, is intended solely for the individual or entity to which 
> > >> it is addressed. This e-mail is confidential and may well also be 
> > >> legally privileged. If you have received it in error, you are on notice 
> > >> of its status. Please notify the sender immediately by reply e-mail and 
> > >> then delete this message from your system. Please do not copy it or use 
> > >> it for any purposes, or disclose its contents to any other person.
> > >>
> > >>
> > >> _______________________________________________________________________
> > >> This mailing list is neither sponsored nor endorsed by Invensys Process
> > >> Systems (formerly The Foxboro Company). Use the info you obtain here at
> > >> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> > >>
> > >> foxboro mailing list:             //www.freelists.org/list/foxboro
> > >> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > >> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> > >
> > >
> > >
> > > _______________________________________________________________________
> > > This mailing list is neither sponsored nor endorsed by Invensys Process
> > > Systems (formerly The Foxboro Company). Use the info you obtain here at
> > > your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> > >
> > > foxboro mailing list:             //www.freelists.org/list/foxboro
> > > to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > > to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> > >
> >
> >
> > _______________________________________________________________________
> > This mailing list is neither sponsored nor endorsed by Invensys Process
> > Systems (formerly The Foxboro Company). Use the info you obtain here at
> > your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> >
> > foxboro mailing list:             //www.freelists.org/list/foxboro
> > to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> > to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> >
> 
> 
> 
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
> 
> foxboro mailing list:             //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
> 
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
> 
> *** Confidentiality Notice: This e-mail, including any associated or attached 
> files, is intended solely for the individual or entity to which it is 
> addressed. This e-mail is confidential and may well also be legally 
> privileged. If you have received it in error, you are on notice of its 
> status. Please notify the sender immediately by reply e-mail and then delete 
> this message from your system. Please do not copy it or use it for any 
> purposes, or disclose its contents to any other person.
>  
>  
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>  
> foxboro mailing list:             //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>  
                                          
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: