>>Has the installation of this kit and Rev M. CP60's completely
>>resolved the issue for those of you that have already implemented it, or 
do
>>you just see reduced number of fieldbus communication errors?

The number of PIO error events and the number of FBMs involved in each 
have both been reduced dramatically.  We now see PIO errors on one or two 
FBMs every couple weeks or so over 4 CP60s.  I'm waiting to see if the 
last two changes we made will eliminate these entirely,


>>I can imagine that the tenuous
>>elevator connections on the top of the CP-60's are also serious 
contributors
>>to noise induction onto the fieldbus and dictate the use of the three 
chokes
>>on the small white coax cables coming from the top of the CP-60's.  Now 
I
>>understand why the ZCP270's use direct fiber connections for their 
fieldbus.
<snip>
>>This seems to be a clear case of poor initial design considerations
>>for the CP-60 fieldbus that now needs to be rectified by an external, 
and
>>might I say, clumsy retrofit kit that many people, including many 
Foxboro
>>field service reps aren't aware of or are not talking about.



I suspect it's more than just your imagination.  The reason I thought all 
this was hogwash is that I have dealt with Ethernet systems based on 
thinnet cable in the past, as well as other coaxial-cable-based networks 
(early Ethernet, brand H LCN, GE Mark V ARCnet).  They were undoubtedly 
sensitive to physical cable problems, but noise was never an issue in my 
experience.  I too suspect that the migration to direct fiber connections 
in the xCP270s is a tacit admission of problems with the coaxial fieldbus. 
 While the retrofit kit is an inelegant fix, it does largely solve the 
problem.  And I don't expect the CP60 to be redesigned at this point, so 
I'll take the kit over nothing.  Too bad there aren't kits for making the 
legacy nodebus redundant _and_ isolated, using Unix time as it was 
intended, etc.  (sorry, but like Duc, I couldn't resist  :).


Corey Clingo
BASF Corp.



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: