Tom, At the heart of the issue is the small peak-to-peak range of the signal itself on the CP60 field bus. You're exactly right about the same cables giving absolutely no problem when connected to earlier rev CPs. The thing is, 1 volt of noise on a signal with a +/-24 volt signal range is a small percentage of noise, but that same level of noise on a signal with a +/- 1 V range is certainly a different matter. That's why grounding has become such an important issue. It is very important that the CP60 field bus ground be a single point ground with no interconnection to a ground of different potential. Whatever signal that is on the shield of that field bus must be conducted to ground. I have not received a sufficient explanation of the reason that ladder logic in the fbms creates problems at iom82 revs above 1.11 myself, so I can not provide one to you. I can testify that I have seen it - going back to a 1.11 rev quieted down a section of field bus where there were some fbms running ladder logic. The switching process does not create the problem, it is just the mechanism that gets exercised when the noise problem is occurring. The system is set up so that when the bus that is enabled starts seeing a certain threshold of noise, it switches to the other bus. This is what you are experiencing when you have it set in the "enable switching" mode. When you disable switching, the noise is apparently not enough of a problem to cause you to lose data, etc., so you're able to run in that mode. The different revs of iom82 have tried to modify that noise sensing capability to make it less sensitive to noise that is not really sufficient to interfere with operations. I have also encountered sites with problems due to positioning of the enclosure itself, such as very near to a bank of switching power supplies, for example. Your local Foxboro service engineer should be able to get their regionally-owned digital scope to use to look at your ground. Even with great precautions, you might be surprised at what is really going on the ground. It's worth a shot if you're still experiencing problem. Shelby -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of tom.vandewater@xxxxxxxxxxxxxx Sent: Tuesday, March 22, 2005 3:21 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] CP-60 Fieldbus Communication Errors Shelby, Thanks for the suggestions. We have paid a lot of attention to proper grounding and our DCM's and 100 series FBM's are mounted in IE-32's connected to ground in the manner specified by the document you referenced. Our twinax runs are of minimal length, < 50ft, and just jump from between one or two additional IE-32's in the same room. The twinax cable we use is a "Foxboro approved" Belden cable. In fact most of it is the same cable we used between the old CP-10/30/40's and the old style FBI's and we didn't have communication issues until we hooked them up to CP-60's. I am curious to clear up one thing you mention. You said: "Unless you are running ladder logic in your FBMs, the fallback to rev. 1.11 will provide only marginal relief." What relationship is there between running ladder logic in FBM's and receiving intermittent fieldbus errors? I've heard similar statements before but never heard an explanation. I'm also interested to see if anyone can explain why all of the intermittent fieldbus communication errors cease to report whenever you run the CP fieldbus in "Bus A Disable Switching" or "Bus B Disable Switching". Does the CP quit reporting fieldbus communication errors when bus switching is disabled or could the bus switching strategy actually be the cause of the communication errors? Nobody from Foxboro has ever explained what is going on with that. Even though the errors are a lot less frequent, we also get intermittent errors on CP 60's that have only a short thinnet cable run to the 3Com SuperStack 6 port fiber optic hubs and all fieldbus segments communicate via FCM10EF's and fiber. Given that fact, I doubt that grounding is an issue and it is more likely to be a fieldbus communication timing issue. I appreciate all of the feedback from Troy, Teresa, Ted, Robert, and Dirk. To me, it still sounds like there may be more issues here than just proper grounding or software/EEprom levels, and I look forward to any light that could be shed on my questions about ladder logic or fieldbus switching. Cheers, Tom VandeWater _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave