Greetings, all wise and all knowing list. We have an application where data from a Carrier chiller needs to be = brought into the I/A via a Micro I/A. The problem is that, per TAC, the = Micro I/A will not read the extended Modbus registers (6 digit) 300000 to = 399999. It only reads 5 digit registers (ex. 30000 to 39999). The = chiller only supplies register addresses in the extended range. The FBM224 has the same limitation. The FBM 230 will support extended = registers, but requires the 270 series controller. There is no option to move the registers in the chiller. It's just a = conversion module from BacNet to Modbus. =20 The chiller supports BacNet, so the BacNet to Modbus converter from = Fieldserver may be an option. Has anybody else out there ran into something like this? Thanks and Regards, Rick Mol ESCO Company IT/Automation Admin. 231.727.6409 rdmol@xxxxxxxxxxxxxxx _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave