Re: [foxboro] Extended Modbus Registers into I/A

  • From: "Blunier, Mark" <Mark.Blunier@xxxxxxxxxxxxxxx>
  • To: <foxboro@xxxxxxxxxxxxx>
  • Date: Wed, 26 Apr 2006 12:19:04 -0500

> [mailto:foxboro-bounce@xxxxxxxxxxxxx]On Behalf Of Rick Mol
>=20
> We have an application where data from a Carrier chiller needs to be =
=3D
> brought into the I/A via a Micro I/A.  The problem is that,=20
> per TAC, the =3D
> Micro I/A will not read the extended Modbus registers (6=20
> digit) 300000 to =3D
> 399999.  It only reads 5 digit registers (ex. 30000 to 39999).   The =
=3D
> chiller only supplies register addresses in the extended range.
>=20
> The FBM224 has the same limitation.  The FBM 230 will support=20
> extended =3D
> registers, but requires the 270 series controller.

In B0400FK - Rev C, Page 79 it states
 "The address field in the Modbus protocol is two bytes, restricting
address to the range 0 to 65535 (1 to 65536 when 1-bases).  The
configurator enforces this limitation..."

It does not indicate that a the limitation is different for the CP60.
If this is the case, the manuals are VERY misleading.  Can someone
from Foxboro verify if extended addresses will work for the CP60?

Mark
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: