Dirk,
     You didn't say what the error number is that you are receiving.  If it is 
3 then the sequence is failing while trying to write a secured variable and 
this indicates it is having trouble executing the line after the one you 
suspect is causing your error.  AUTDSR cannot be written if either of the 
following parameters are set.  MANSW or AUTSW.  This may not be your problem 
but if the error you get is error # "3" I would be willing to bet that it is.  
If it is a different error then I would agree with Gabriel.  Any direct read or 
write to a C:P:B pararameter from sequence code essentially causes a wait while 
the sequence pauses for the response to its request.  By linking to a BI or RI 
parameter the sequence gets the value before it executes the code and doesn't 
have to wait for a response to an OM call.
        If there are other sequences that use MANSW or AUTSW or if operators 
have the ability to set those parameters it could be what is causing your error 
as it tries to write AUTDSR.
       Either way, please let us know if/when you identify a solution.
Cheers,
Tom Vandewater
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: dirk.pauwels@xxxxxxxxxx
Sender: foxboro-bounce@xxxxxxxxxxxxx
Date: Wed, 25 Aug 2010 10:03:39 
To: <foxboro@xxxxxxxxxxxxx>
Reply-To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] system error in sequences

Gents,
Question to the HLBL experts outthere...

We noticed some of our sequences (only a few of the 900+ we have) 
sometimes (very, very  rarely, but it does happen) go into sys_error. In 
most of my sequences I've build in some exception handlers which send the 
error to SN000x, so I can see which line caused the sys error. Usually it 
's a line containing a  C:B:P reference. It's as if the system doesn't 
recognize this adress for a short period, causing a sys error, which sends 
the sequence into manual mode. 

I did some testing, writing a sequence which contained a non-existing 
adress, and noticed the same behaviour.

I then changed the exception to manual handler to retry 3 times with a 
time interval of 5 secs. This way if a sequence goes into sys error - and 
therefore manual mode-  on an adress temporarely unavailable (for reasons 
I wouldn't know), it has time to restore itself by retrying. This has 
solved this problem in most cases, but it hasn't completely cured it.
I know I'm not supposed to write any executing code in the exception to 
sys error, but I think I can get away with this type of code in the 
exception to manual handler wright?

This morning we noticed that a smal sequence was in manual mode after a 
sys error for no apparent reason, sys error seemed to be caused by the 
"IF (:PRESS_CP4:PT_HOPPERR1.PNT - :LOGIC_PRESS:R1_PRESS.RO01)......." 
line. There was nothing wrong with both of the adresses by the time I 
checked them. We put the sequence in auto again and it started executing 
with no problem at all

the code is very basic: (could be a bit scrambled)

IF BI0001 = TRUE THEN
        REPEAT
                IF (:PRESS_CP4:PT_HOPPERR1.PNT - 
:LOGIC_PRESS:R1_PRESS.RO01) < RI0002 AND :PRESS_CP4:PT_HOPPERR1.PNT < 5 
THEN
                        :NITRO_R:R1_V_H60AC.AUTDSR := TRUE;
                ELSE :NITRO_R:R1_V_H60AC.AUTDSR := FALSE;
                ENDIF;
        UNTIL :POWDER_R:FILL_HOPPER.BI0001 = TRUE OR BI0001 = FALSE;
        GOTO stop;

ELSE GOTO stop;
ENDIF;

<<stop>>

        :NITRO_R:R1_V_H60AC.AUTDSR := FALSE;
        :POWDER_R:R1_V_071AC.AUTDSR := FALSE;

ENDSEQUENCE

I do know I'm offending some HLBL rules, like the sequence is not in the 
same CP as some of the adresses it refers to and I use the C:B.P in the 
code rather then using user labels. (this can very easily be corrected in 
this case, but in most cases I do not have enough Reals or booleans to use 
user labels), but could this be the reason for the occasional "misfire"?
If this communication "hickup"cannot be avoided what would be the 
preffered workaround? Should i give it more time to retry in the exception 
to manual handler?

Another strange thing is that allthough the sequence doesn't seem to 
recognize the adress, there are no comm alarms, smurfed data, failed OSI 
PI tags or anything of the sort. We do not have problems with other 
sequences running at the same time which use C:B.P from the same CP or 
compound. The problem seems to confined to the sequence (not always the 
same sequence)

We're on 8.4.2 and CP270's, no overruns detected. Most sequences are at 
BPCSTM 100

thanks for the help!

Dirk 


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: