Client System OM Version Solaris, AW51D Nodebus IA 6.2 5300 points @ 1.0 sec on each of 2 AWs, each feeding a PC drives primary ops interface in Wonderware Intouch for a power plant reliable operation since installation, 11/2009. options not applicable OPC server and client coexist on each Wonderware Tagserver PC single default delta systemwide, single scan rate systemwide delta is 0.001, yes, engineering units scan is 1.0 sec redundancy (or fault tolerance) achieved because we have 2 AW/PC pairs and Wonderware InTouch sorts out which is alive/failed and client WW HMIs switch between tagservers. Switchover is automatic. NOTA A single problem was found during implementation (which Matricon would not correct) in that if the Client writes a value back to the Foxboro system before initialization of OM lists is complete, the interface fails and both ends of the link must be restarted (system reboots required). We avoid occurance by use of fancy apps programming in the Wonderware client so no write can be issued before it's time. This setup replaces a Wonderlink arrangement which had existed before. Though Foxboro documents said the the product was supported, the customer says that as a practical matter, there was no support available (nobody at TAC knew the product). Further, the NT systems which had been carrying the Wonderlink and Tagserver functions were becoming unreliable and replacements we hard to find. Hence, new, XP PCs and the OPC link were implemented. This is a temporary measure (2 or 3 years) as they plan complete system replacement as money allows. The 5300 tags ; for each AIN, we read the PNT, Block and Alarm status words, and Alarm Limits. That means for 1 AIN we read 5 'tags' Similar 'tag' sets exist for controllers, AOUTs and so forth. The Foxboro system handles only the Analog controls of the plant. There are myriad Allen-Bradley PLCs for discrete functions which also connect to the WW Tagservers, though not thru the OPC interface. We have done other Matricon OPC I/Fs, both on Solaris and Windows (none yet on MESH), but I have no details. We have also done a couple of Foxboro OPCs, but only to support reporting. Regards, William C Ricker FeedForward, Inc. -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of dave.caldwell@xxxxxxxxxxxxxx Sent: Tuesday, March 15, 2011 1:09 PM To: foxboro@xxxxxxxxxxxxx Subject: [foxboro] Matrikon OPC Server for Foxboro I/A Hello List, Does any one have any experience with the Matrikon OPC Server for Foxboro I/A? I am interested in the following: * Whether or not you are using the FoxAPI or OM API version? * Are you on Solaris or Windows? Which model AW? * Are you on nodebus or MESH? * What is your I/A version? * How many points collected, update frequency, and for what purpose? * Has the server been reliable? o How long has it gone without issue? o How often do problems arise? o What has been the symptoms and sources of trouble? * Are you using primary, distributed load, or stand-by server option? * Are you using COM (client local to server), DCOM, tunneling, or other? * Are you specifying a delta value and a scan rate for each point? o If so, does this mean the OM scanner in the remote station will scan .......the OM list for changes greater than delta every x seconds, and .......report a change to the station requesting the object? o Is delta specified in engineering units? o Is scan rate in seconds? o If no attribute is specified what are the defaults? * Is there a way to make the FoxAPI or OM API AW redundant? In other words, should something happen to the collector AW can a backup AW be automatically brought on-line to collect the points for the OPC Server? Thanks, Dave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave