Donato, One would expect that 100% - idle time = CP load but this is not always the case with the CP station block. I would suggest that you monitor CPLOAD, fieldbus load and the accumulated overruns and ignore idle time as it is often meaningless. These numbers can be historized to give you long term information. I would also monitor the OM parameters from the Station display. If you get overruns, then your CP is overloaded. Howmany overruns you get per day gives you an idea of how often you are overloaded. You want zero overruns. Any overruns can give errors in ACCUM blocks and CALC timing functions. Foxboro EDOC has an Excel spreadsheet for the CP60 loading. If you do not have any sequence blocks, you should be able to get the Excel spreadsheet to match your existing CP60 load and fieldbus load. You can then transfer this data to the newer CP270 Excel spreadsheet and get a very good idea of what the existing loading would be on a new CP270. I suspect that you could ask that this be done by Invensys / Foxboro as part of any quotation for an Upgrade. I believe that Foxboro recommends that total CPLOAD is less than 80 and total FB scan is less than 60. If you have sequence blocks then loading gets very complicated since lines of sequence code processed per block period can vary with the logic and it is tough to assign a value in the Excel spreadsheet for this logic. If you have a lot of sequence blocks you likely need assistance from a Foxboro expert. Terry > I am proposing a migration to a Preferred platform of I/A. We > currently have I/A 7.1.1 with CP60 controllers. I would like to base > my proposal on two arguments: > > 1) Processor idle time is 30% and there are possible additions on the > way. Are there recommendations as to how little idle time is too > little? > > Donato Azevedo _________________________________________________________________ Hotmail & Messenger are available on your phone. Try now. http://go.microsoft.com/?linkid?24461 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave