The acceptable impedance has to take account of the actual circuit.  The
fuse used for the test needs to have a reasonable value to ensure that it
withstands the test current.  Which is why testing through the lamp drives
should be avoided, it could damage them.  There are claims that they should
not be damaged, but why take a risk of abusing a device not designed for the
test load?

As for 20% testing, don't risk it! Remember there have been knock downs etc
in the preceding six years, this isn't a nice cosy house, it is a much
harsher environment.  The site file should have copied of impedance tests
from each repair, but are they being done/recorded?  (If not why not?)  The
six year test updates the whole site record and needs to be completed and
filed.

PW

-----Original Message-----
From: Bill Emett [mailto:bill.emett@xxxxxxxxxxxxxxxxxxxxxxx]
Sent: 15 June 2004 14:44
To: tcug@xxxxxxxxxxxxx
Subject: [TCUG] Re: 6 year electrical testing


Why would you need to disconnect all cores at pole top, surely only one
core would be necessary to form a circuit to test and an ELI test will
also prove armoring.
Most courses on this subject relate to house wiring which suggests you
only have to test 20%  of the system this should reduce the down time if
applied to signals. Unless this 20% shows a problem then the whole
system has to be checked.

One of the queries I have is with E.L.I testing at poles is as
follows,
Our contractors tell me they use a spare live feed but this would only
test straight from the origin via whatever fuse they use to the pole
back via the armored cable and the usual Manweb path to the substation
this is bound to give a favourable result.
 This can't give the practical reading via the  phase drive circuits
which are essentially in series and have there own resistance which must
be included in the E.L.I figure.
A figure quoted for a max E.L.I test for a particular controller is 5
ohms which is down to the 10A fuse on the phase drive card, not the main
20 or 30 amp fuse in the supply which this figure would fail.
>>> chris.gladwyn@xxxxxxxxxxxxxxxxxx 15-Jun-04 1:33:39 pm >>>



************************************************************************
This email contains confidential information, solely for the 
person/organisation intended. If you received it in error,
 please contact the sender right away and do not copy this email for any
purpose, or disclose its contents to any person. The contents of an
attachment to this email may contain software viruses which could
damage your own computer system. While Owen Williams has taken every
reasonable precaution to minimise the risk, we cannot accept liability
for any damage which you sustain as a result of software viruses. You
should carry out your own virus checks before opening the attachment.
************************************************************************
-----------------------------------------------------------
A message from the TCUG mailing list. For information about
the list visit //www.freelists.org/webpage/tcug

Other related posts: