[SI-LIST] Re: Necessity of Ground signal for RS485 transmission at 500 ft cable length

  • From: "Curt McNamara" <CurtM@xxxxxxxxxxx>
  • To: "steve weir" <weirsi@xxxxxxxxxx>, <adeelmk@xxxxxxxxxxx>
  • Date: Thu, 24 Feb 2005 19:54:09 -0600

Steve, I hope you are not saying you would connect remote grounds 
without a fusible link! This would be a serious safety error as currents 
through the cable could cause insulation failure and a fire hazard. 
 
It would be good practice to use a fuse or other UL/CSA approved 
safety device if it is possibile for remote grounds to be connected. 
The resistor example is from the annals of history and was not a 
recommendation on my part. 
 
I see you also recommend the use of isolated transceivers 
as best practice for communications links with remote grounds. 
 
It should be noted that remote grounds might be the two sides of a
room! In many cases the AC on two separate circuits follow very 
different paths back to the mains.
 
                                                  Curt

Curt McNamara. P.E.
Senior Electrical Engineer
Logic Product Development
411 Washington Ave. N Suite 101
Minneapolis, MN 55401
Tel 612-436-5178
Fax 612-672-0443
curtm@xxxxxxxxxxx
www.logicpd.com
This message (including any attachments) contains confidential information
intended for a specific individual and purpose, and is protected by law.
If you are not the intended recipient, you should delete this message and
are hereby notified that any disclosure, copying, or distribution of this
message, or the taking of any action based on it, is strictly prohibited


________________________________

From: steve weir [mailto:weirsi@xxxxxxxxxx]
Sent: Thu 2/24/2005 4:54 PM
To: Curt McNamara; adeelmk@xxxxxxxxxxx
Cc: si-list@xxxxxxxxxxxxx
Subject: RE: [SI-LIST] Re: Necessity of Ground signal for RS485 transmission at 
500 ft cable length



Curt, I have never been a real big fan of the resistor as it can become its
own fire hazard under a number of conditions.  But then, I just basically
loathe box to box interconnects that are not isolated.  If DC offsets don't
bite, EFTs often do.

Regards,

Steve.
At 04:37 PM 2/24/2005 -0600, Curt McNamara wrote:
>In two widely separated systems earth ground (or neutral) often
>varies by many volts, effectively becoming a common mode offset.
>
>You can connect a ground between the systems, however this
>wire can definitely conduct large amounts of current! In RS-232
>days this connection was often made with a small series resistor
>which became a "fusible link" if the grounds were too far apart.
>
>For distant RS-485 transmission try an isolated transceiver ...
>
>                                        Curt
>
>
>Curt McNamara. P.E.
>Senior Electrical Engineer
>Logic Product Development
>411 Washington Ave. N Suite 101
>Minneapolis, MN 55401
>Tel 612-436-5178
>Fax 612-672-0443
>curtm@xxxxxxxxxxx
>www.logicpd.com
>This message (including any attachments) contains confidential information
>intended for a specific individual and purpose, and is protected by law.
>If you are not the intended recipient, you should delete this message and
>are hereby notified that any disclosure, copying, or distribution of this
>message, or the taking of any action based on it, is strictly prohibited
>
>
>________________________________
>
>From: si-list-bounce@xxxxxxxxxxxxx on behalf of Steve Weir
>Sent: Thu 2/24/2005 8:09 AM
>To: adeelmk@xxxxxxxxxxx
>Cc: si-list@xxxxxxxxxxxxx
>Subject: [SI-LIST] Re: Necessity of Ground signal for RS485 transmission
>at 500 ft cable length
>
>
>
>Adeel there is no such thing as the "receiver not supporting the
>common".  The receiver most definitely has its common mode referenced to
>the negative supply rail.  This is clear in any '485 receiver
>specification.   You can answer your question by evaluating the loss and
>the allowable ground noise between the two points.  Your limit will be set
>by when the signal either falls below the nominal 50mV receiver threshold,
>or the CM noise take you out of the CM range.
>
>Steve.
>At 07:02 PM 2/24/2005 +0500, Adeel Malik wrote:
> >Steve,
> >         Using the ground signal wire keeps the common voltage range
> >within -7V to +12 V, that of course improves noise immunity as well as
> >reliability. But the point is that if the slave device doesn't support
> >the ground signal connection, then up to how much distance the Master
> >can transmit the data reliably at 57600 baud rate over RS485 Network
> >without that ground wire.
> >
> >Adeel
> >
> >-----Original Message-----
> >From: si-list-bounce@xxxxxxxxxxxxx [mailto:si-list-bounce@xxxxxxxxxxxxx]
> >On Behalf Of steve weir
> >Sent: Thursday, February 24, 2005 6:40 PM
> >To: adeelmk@xxxxxxxxxxx; si-list@xxxxxxxxxxxxx
> >Subject: [SI-LIST] Re: Necessity of Ground signal for RS485 transmission
> >at 500 ft cable length
> >
> >Adeel, RS485 is not galvanically isolated.  Think receiver common mode
> >range.
> >
> >Steve.
> >At 06:24 PM 2/24/2005 +0500, Adeel Malik wrote:
> > >Hi All,
> > >             Can someone comment on the need of separate Ground Signal
> > >Wire in addition to the standard 2-wire RS485 Connections between the
> > >Master and Slave device. I have come to know that separate Ground wire
> > >b/w the two devices communication via RS485 at higher baud rates and
> > >increased cable length improves signal transmission.
> > >Regards,
> > >Adeel Malik
> > >
> > >------------------------------------------------------------------
> > >To unsubscribe from si-list:
> > >si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
> > >
> > >or to administer your membership from a web page, go to:
> > >//www.freelists.org/webpage/si-list
> > >
> > >For help:
> > >si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
> > >
> > >List FAQ wiki page is located at:
> > >                 http://si-list.org/wiki/wiki.pl?Si-List_FAQ
> > >
> > >List technical documents are available at:
> > >                 http://www.si-list.org
> > >
> > >List archives are viewable at:
> > >                 //www.freelists.org/archives/si-list
> > >or at our remote archives:
> > >                 http://groups.yahoo.com/group/si-list/messages
> > >Old (prior to June 6, 2001) list archives are viewable at:
> > >                 http://www.qsl.net/wb6tpu
> > >
> >
> >The weirsp@xxxxxxxxxx e-mail address will terminate March 31, 2005.
> >Please update your address book with weirsi@xxxxxxxxxx
> >
> >
> >------------------------------------------------------------------
> >To unsubscribe from si-list:
> >si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
> >
> >or to administer your membership from a web page, go to:
> >//www.freelists.org/webpage/si-list
> >
> >For help:
> >si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
> >
> >List FAQ wiki page is located at:
> >                 http://si-list.org/wiki/wiki.pl?Si-List_FAQ
> >
> >List technical documents are available at:
> >                 http://www.si-list.org
> >
> >List archives are viewable at:
> >                 //www.freelists.org/archives/si-list
> >or at our remote archives:
> >                 http://groups.yahoo.com/group/si-list/messages
> >Old (prior to June 6, 2001) list archives are viewable at:
> >                 http://www.qsl.net/wb6tpu
> >
>
>The weirsp@xxxxxxxxxx e-mail address will terminate March 31, 2005.
>Please update your address book with weirsi@xxxxxxxxxx
>
>
>------------------------------------------------------------------
>To unsubscribe from si-list:
>si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
>
>or to administer your membership from a web page, go to:
>//www.freelists.org/webpage/si-list
>
>For help:
>si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
>
>List FAQ wiki page is located at:
>                 http://si-list.org/wiki/wiki.pl?Si-List_FAQ
>
>List technical documents are available at:
>                 http://www.si-list.org
>
>List archives are viewable at:
>                 //www.freelists.org/archives/si-list
>or at our remote archives:
>                 http://groups.yahoo.com/group/si-list/messages
>Old (prior to June 6, 2001) list archives are viewable at:
>                 http://www.qsl.net/wb6tpu
>
>
>
>

The weirsp@xxxxxxxxxx e-mail address will terminate March 31, 2005.
Please update your address book with weirsi@xxxxxxxxxx





------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field

List FAQ wiki page is located at:
                http://si-list.org/wiki/wiki.pl?Si-List_FAQ

List technical documents are available at:
                http://www.si-list.org

List archives are viewable at:     
                //www.freelists.org/archives/si-list
or at our remote archives:
                http://groups.yahoo.com/group/si-list/messages
Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu
  

Other related posts: