Absolutely! There have been several designs that worked (and I mean 
functionally!) when in a metal chassis that did not when the chassis
was redesigned to plastic.  

-----Original Message-----
From: si-list-bounce@xxxxxxxxxxxxx [mailto:si-list-bounce@xxxxxxxxxxxxx] On ;
Behalf Of Istvan Novak
Sent: Friday, May 11, 2018 7:24 AM
To: doug@xxxxxxxxxx; leeritchey@xxxxxxxxxxxxx
Cc: joel@xxxxxxxxxx; gurushankara@xxxxxxxxxxx; si-list@xxxxxxxxxxxxx
Subject: [SI-LIST] Re: Logic ground and chassis/safety ground

This message originated outside of DISH and was sent by: 
si-list-bounce@xxxxxxxxxxxxx

All this having said, we should also remember that multiple connections to a 
chassis ground is no substitute for good design practices within each board 
and/or module (like switching power supplies) that gets connected to the 
chassis.  If we allow significant 'functional' current flowing through the 
chassis instead of dedicated return paths in the boards/subsystems, it will 
likely create signal and power integrity issues.

Regards,

Istvan Novak


On 5/11/2018 2:29 AM, Douglas Smith wrote:

But Lee I am talking about solving operational and ESD problems for over 40 
years now, having been in engineering for iced 55 years.
Solutions are not unique but carry different costs. Multiple grounds result 
in the least cost solutions most of the time and the highest PCB to chassis 
resonant frequencies (hopefully beyond what would be a problem. All the 
boards and chassis members are connected whether you want or not by 
impedances on thd order of 30 Ohms at high frequencies. Single point ground 
guarantees strong and low frequency resonance. Only with multiple grounds do 
you have the option of killing the Q of the PCB/chassis resonance by adding 
loss. I demonstrate this effect in all of my classes. It is easy to measure 
and prove. I demonstrated the advantages of multiple grounds at AT&T Bell 
Labs about 40 years ago.
You may have designs that work but I can show they cost more than they should 
to achieve good ESD performance. This is easy to show which I do every six 
weeks at my courses. A single pF of capacitance will couple Amps of ESD 
current at very low Voltages.
There are about a half dozen articles on my website ( http://emcesd.com ;) 
that prove my point with measurements and analysis.
I am not saying your designs don’t work, only that single point ground is 
not achievable above tens on MHz and attempting single point ground raises 
system cost to make it work.
Doug Smith Sent from my iPhone IPhone: 408-858-4528 Office: 
702-570-6108 Email: doug@xxxxxxxxxx Website: http://dsmith.org On Thu, May ;
10, 2018 at 8:50, leeritchey@xxxxxxxxxxxxx <leeritchey@xxxxxxxxxxxxx> wrote:
Sorry Doug. Been doing this a long time and have had very good results. Have 
fixed many EMI problems by removing all but one connection between logic 
ground and the case or Faraday cage- which many seem to want to call chassis 
ground.

-----Original Message-----
From: si-list-bounce@xxxxxxxxxxxxx <si-list-bounce@xxxxxxxxxxxxx> On 
Behalf Of Douglas Smith
Sent: Wednesday, May 9, 2018 9:33 PM
To: leeritchey@xxxxxxxxxxxxx
Cc: joel@xxxxxxxxxx; gurushankara@xxxxxxxxxxx; si-list@xxxxxxxxxxxxx
Subject: [SI-LIST] Re: Logic ground and chassis/safety ground

Hi All,
I respectfully disagree with Lee’s comments. It almost guarantees an 
ESD problem. I have fixed hundreds of ESD problems by connecting the two 
grounds in as many places as possible.
Also doing so significantly reduces the cost of switching supplies operating 
from the mains, lowering induced noise by 30 dB on average for a given 
supply. I have lost count on this kind of fix.
One connection also guarantees the lowest resonant frequency of the 
chassis-PCB resonant circuit (which WILL exist) and prevents the simple 
solution to kill the Q of that resonance. Multiple connections raise this 
frequency but the best is multiple connections and then to de-Q the resonance 
you will always have between the PCB and the chassis.
After 40 years of fixing chassis-PCB interactions I have developed quite a 
base of solutions.
Doug Smith Sent from my iPhone IPhone: 408-858-4528 Office: 702-570-6108 
Email: doug@xxxxxxxxxx Website: http://dsmith.org On Wed, May 9, 2018 at ;
10:12, leeritchey@xxxxxxxxxxxxx <leeritchey@xxxxxxxxxxxxx> wrote:
There is no electrical reason why you need to connect these two. If you do 
connect them, do it in only one place and do it with a DC connection. I make 
that connection on the side of the PCB where the unshielded wires exit as a 
way to minimize potential EMI escaping on those unshielded wires.

Don't know where all of the rules of thumb come from about capacitors and 
multiple connections.

Lee RItchey

-----Original Message-----
From: si-list-bounce@xxxxxxxxxxxxx <si-list-bounce@xxxxxxxxxxxxx> On 
Behalf Of Joel Brown
Sent: Wednesday, May 9, 2018 9:47 AM
To: gurushankara@xxxxxxxxxxx
Cc: si-list@xxxxxxxxxxxxx
Subject: [SI-LIST] Re: Logic ground and chassis/safety ground

Unless you have a requirement or other reason to keep them isolated It would 
be best to connect them together.
If you decide to keep them them isolated then add multiple capacitors between 
signal and chassis ground at each chassis connection point that can be 
populated with different value capacitors or zero ohm resistors. Another 
option is to have a chassis ground plane layer in your PCB that is connected 
to signal ground at multiple points with capacitors. If you don't have a 
solid RF connection between signal and chassis ground then there can be an RF 
potential between the two grounds that can radiate if you have antenna 
structures such as slots in your enclosure or external cables.
Joel


On Wed, May 9, 2018 at 9:16 AM, Guru Shankara 
<gurushankara@xxxxxxxxxxx>
wrote:

Hi Experts,
I am working on a modem design that is powered by an AC/DC supply 
(isolated).

The design includes a base board that hosts a mezzanine/daughter card 
and both the baseboard and the mezzanine cards are powered by 12V DC.

The chassis walls and misc. mechanical hardware have a conductive 
coating on the inside and will be connected to the 
chassis/safety/earth ground of the AC/DC power supply.


As the name implies, the chassis/safety/earth ground provides for 
safety of the operator if there is a situation where the higher 
voltage side line of the AC/DC supply rips off and makes contact with 
the
chassis.
So, I prefer NOT to connect the board logic ground to the 
chassis/safety/earth ground of the supply.

Any thoughts on if I should connect them together or not?


Also, if they need to be connected, is there a recommended method?

Really appreciate your help.


Thank you,

Gurushankar

------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum is accessible at:
http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
//www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
http://www.qsl.net/wb6tpu




------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum is accessible at:
http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
//www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
http://www.qsl.net/wb6tpu



------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum is accessible at:
http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
//www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
http://www.qsl.net/wb6tpu
------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum is accessible at:
http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
//www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
http://www.qsl.net/wb6tpu



------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum is accessible at:
http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
//www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
http://www.qsl.net/wb6tpu
------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
                http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
              //www.freelists.org/archives/si-list
  
Old (prior to June 6, 2001) list archives are viewable at:
              http://www.qsl.net/wb6tpu
   



------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
               http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:     
                //www.freelists.org/archives/si-list
 
Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu
  

------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
               http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:     
                //www.freelists.org/archives/si-list
 
Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu
  

Other related posts: