FBM230 is for single-ported devices. It has 4 ports which can be individual=
ly set as RS232, RS422 or RS485. RS232/422 are single-drop, so 4 devices co=
uld be attached to each FBM. RS485 allows multidrop for a total of 64 devic=
es distributed over the 4 ports. (Keep in mind that data loading may restri=
ct the number of devices to less than 64.) FBM231 is the redundant version =
for dual-ported devices.

FBM232 is for Ethernet 10/100 TCP/IP or UDP/IP communication. It supports 6=
4 devices through hubs or switches. FBM233 is the redindant version for dua=
l-poerted devices.

Some docs you'll want to read:
B0700AH - FDSI User's Guide
B0700BG - FDSI Driver for Modbus (Serial & TCP/IP) (FBM230/231/232/233)
B0700BH - FDSI Driver for OPC Client (only FBM232/233)
B0700BJ - FDSI Driver for Allen-Bradley ControlLogix PLC (only FBM232/233)

The basic principle is there is a FBM driver file (.ZIPH) and a port config=
uration file (.XML) for each FBM. There is a device configuration file (.XM=
L) for each device attached to the FBM. The format of these .XML files diff=
ers depending on the type of FBM, the driver and the device.

For example, the Modbus driver pre-defines all the transaction types, so th=
ere is no need to build the equivalent of MDSCAN or FDSCAN blocks to define=
 the transactions. The DCI blocks simply refer to the addresses within each=
 transacton type. So to read 16 inputs (Modbus FC2) starting bit 73, PAKIN.=
PNT would simply be 10073:C16. The driver already know that 10073 falls wit=
hin the range for FC2. The driver manuals explain all the details of addres=
sing for each protocol.

Brad Wilson
brad.wilson@xxxxxxxxxxxxxxxx
Invensys Systems, Inc
1090 King Georges Post Rd, Suite 204
Edison, NJ  08837
732-874-0087

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On=
 Behalf Of Corey R Clingo
Sent: Monday, September 17, 2007 3:09 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] RE =A0: Communication problem b/w FBM231 & AB PLC

>>The AB Gateway (or Integrator30) limiting resource is usually the RS232 =

baud rate, likely 19, 200.

Not in our experience.  Our Int30As will not saturate even a 9600 baud =

serial link, a fact which I find puzzling to this day, given the hardware. =

 We do generally have more than one PLC per A-B highway (but not an =

excessive number), but the Honeywell PLCGs I used to use fared far better =

in a multiple-PLC scenario than Int30s do, and Rockwell RSLinx is in =

another universe entirely  performance-wise. =



Since our efforts to optimize the gateways led to even more problems =

(frozen data with no system errors, primarily), we are switching slowly to =

an AW70 integrator.  It's not a situation I like, but the AW70 has much =

better performance (it uses RSLinx to deal with the PLCs), and it's about =

our only other option unless we decide to go to V8 and CP270s.  In =

addition (because of RSLinx),  it can read _any_ PLC data from _any_ A-B =

PLC, regardless of the PLC type or the manner in which it's connected. =

Int30s can't deal with anything not directly connected to the highway they =

are attached to.


That said, you are correct about the desire to pack the data and read as =

many (contiguous) registers with as few ABSCANs as possible.  The effects =

of ABSCAN processing overhead can be profound -- we noticed it the few =

times we were able to make the changes without any other adverse =

side-effects.


Now, back to Imran's question :)  The addressing format will be different =

in the FBM231s than on the DI I imagine.  I've never set up a FBM231, but =

to continue my previous example, a CIN that referenced a bit in B3 on the =

Int30 might have a PNT_NO of 3:0.1, where in the AW70 it would be an FCIN =

block with a PNT_NO of [PLC_NAME]B3:0.1.  For the AW70 I found this out by =

trial and error with an OPC test tool (the AW70 reads in data via OPC), =

but I found this documentation for my FBM224s in the Modbus FBM User's =

Guide.  So your block types will be different ("standard I/A" in the DI =

vs. DCI in the FBM231), and the IOM_ID and PNT_NO will likely be =

different.  Unfortunately I did not find a document on the Invensys site =

that described the addressing format for serial-connected A-B PLCs; they =

only seem to have one for OPC connections.


Corey Clingo
BASF Corporation






"Doucet, Terrence" <tdoucet@xxxxxxxxxxxxxxxxxx> =

Sent by: foxboro-bounce@xxxxxxxxxxxxx
09/17/2007 10:14 AM
Please respond to
foxboro@xxxxxxxxxxxxx


To
<foxboro@xxxxxxxxxxxxx>
cc

Subject
[foxboro] RE : Communication problem b/w FBM231 & AB PLC





Imran,

The AB Gateway (or Integrator30) limiting resource is usually the RS232 =

baud rate, likely 19, 200.  Each serial communication   consists of =

overhead (addresses, security check, etc) that do not provide information =

about your process and data (your process good stuff) that all must be =

part of the 19,200 baud.   You need to try and minimize the overhead by =

reading (or writing) contiguous bytes of PLC data.

Most users get the PLC logic to move the various pieces of information in =

the PLC into contiguous data areas in the PLC and then the Foxboro =

Integrators read that contiguous data with the largest read that is =

possible.

If you just read your input data directly, most of your 19,200 baud would =

be overhead. It takes a little work to map the data in and then read it =

out on the Foxboro side but it is well worth the effort. At 19,200 baud =

you can usually read about 350 bytes per second of your data but there are =

a lot of other factors (like the number of PLC's on your DH+ network) that =

could lower this 350 bytes per second.  Also you need to keep writes from =

the Foxboro to the PLC to low numbers per second.





 =

 =

_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 =

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
 =



Confidentiality Notice:
This e-mail and any associated files are intended solely for the individual=
 or entity to whom they are addressed. Please do not copy it or use it for =
any purposes, or disclose its contents to any other person. Further, this e=
-mail and any associated files may be confidential and further may be legal=
ly privileged. This email is from the Invensys Process Systems business uni=
t of Invensys plc which is a company registered in England and Wales with i=
ts registered office at Portland House, Bressenden Place, London, SW1E 5BF =
(Registered number 166023).  For a list of European legal entities within t=
he Invensys Process Systems business group, please click here http://www.in=
vensys.com/legal/default.asp?top_nav_id=3D77&nav_id=3D80&prev_id=3D77.

If you have received this e-mail in error, you are on notice of its status.=
 Please notify us immediately by reply e-mail and then delete this message =
from your system. Thank you for your co-operation. You may contact our Help=
desk on +44 (0)20 7821 3859 / 2105 or email inet.hqhelpdesk@xxxxxxxxxxxxx T=
his e-mail and any attachments thereto may be subject to the terms of any a=
greements between Invensys (and/or its subsidiaries and affiliates) and the=
 recipient (and/or its subsidiaries and affiliates).


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: