Hi Tom,
Strange thing is we don't get sys errors for most of these cards in the 
sysmon when the state alarms occur, recently we do get sysmon errors for 2 
of the cards, but never on the same timestamp then the alarms.
I might try to disable bus switching like you did tomorrow, at the rate 
the alarms are occuring now I should soon see if it's related to the bus 
comm errors.

thanks for the help & Rgds,

Dirk 



tjvandew@xxxxxxxxx 
Sent by: foxboro-bounce@xxxxxxxxxxxxx
29/09/2010 14:50
Please respond to
foxboro@xxxxxxxxxxxxx


To
foxboro@xxxxxxxxxxxxx
cc

Subject
Re: [foxboro] FCP270-FBM100






Dirk, we had some funky problems with temporary communication errors on 
FBM-41's running ladder logic, even on CP-60's.  This may or may not be 
related.  The errors were captured by System Monitor and caused the 
fieldbus to switch from A to B and back again.  This communication problem 
could be associated with what you are seeing because the ladder logic 
executes in the memory of the FBM and then all values get communicated to 
the CP across the fieldbus.  If there are fieldbus communication errors 
that cause a delay in fieldbus COMM's the PLB interface block running in 
the CP may not be getting status updates from CIN or OFL's as they are 
happening in the ladder.  To insure this isn't your problem be sure that 
you are capturing ALL of your system monitor errors and then check to see 
if you get any intermittent fieldbus errors from the offending FBM41 at 
the same time as the plb error.
FYI, we forced our fieldbus to communicate only on A bus and the 
intermittent errors quit coming into system monitor.  We theorized that an 
error caused the bus to switch if bus switching was enabled and would stay 
on the same bus and retry if bus switching was disabled.  A CAR was 
entered but never resolved to our satisfaction.  When I was in Hawaii I 
saw the same error occur on the Bailey migration IO that contained 100 
series components.  The error can happen on other 100 series FBM's with 
FBM04's Beng the 2nd biggest offender but discrete FBM's runnng ladder 
logic were far and away the most frequent.  To me it appeared to be a 
fieldbus communication timeout issue where the FBM's ran out of time to 
fnish communication in the time allotted and that caused the error.
Regards,
Tom Vandewater
Control Conversions, Inc.
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: dirk.pauwels@xxxxxxxxxx
Sender: foxboro-bounce@xxxxxxxxxxxxx
Date: Wed, 29 Sep 2010 12:11:00 
To: <foxboro@xxxxxxxxxxxxx>
Reply-To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] FCP270-FBM100

Hi List,
We've had following problem ever since we changed from CP60 to FCP270, 
I've posted it earlier, but never found a sollution for it. Seemed we were 

the only site to suffer from it. Maybe in the meantime someone else has 
experienced this behaviour. So I'm posting it again:

Mesh 8.4.2, ZCP270's, mix from FBM100 and FBM200.

The problem we're having is limited to FBM100 only (FBM41/42), and for the 

moment we have it on 2 CP's, the other CP's seem to be fine

ZCP270 -> FCM100 -> FBI twinax -> FBM100's

Each FBM41/42 is used with GDEV and PLB -  looking more or less like this:

-| |--------------------|\|----------------------------------------------( 

)
ifl open/close    ifl HLD                               CO open/close 
output to vlve
-| |---------------------------------------------------------------------( 

)
cin feedback from vlve open                     OFL
-| |---------------------------------------------------------------------( 

)
cin feedback from vlve closed                   OFL

The ofl is tied to the devlm1/2 of the GDEV.

What happens on +/- 25 FBM41/42 cards, (most cards are OK) is that the cin 

feedback from the vlve fails for a short time (1-2 secs), which causes the 

valve to goto into state alarm, which might trigger some interlocks. (if a 

certain valve position is expected for some action)

At first we thought this failing of the feedback had to do with 
power/wiring etc, but we couldn't find anything wrong. 
these are the steps we took on one of the problem cards trying to solve 
this problem:

1. We installed a bridge on the feedback, to determine if it was power or 
software related, and even then the cin-ofl failed.......So nothing 
power/wiring  related

2. We then changed the card, still same problem

3. we changed the nose cone, still same problem 

4. I put some delay (on/off) 5-10sec in the PLB , to prevent the ofl 
failing when the cin failed. cin fails for 1 sec so a delay of 5-10sec 
would certainly solve it. Turns out the OFL still fails????? which 
probably means it's not actually the cin that fails but the cin-ofl fail 
together despite the delay......Don't understand this.....

5. I set the FBM ECB to 5 sec's, as wel as the PLB block and the GDEV 
block, to slow down processing, hoping this would prevent DCS from seeing 
the cin fail. Errors seemed to decrease at first, but no final solution

6. Invensys adviced to swap the 41 cards for a more recent type, still 
same problem

7. We updated the FBM100's Eeprom, still same problem

8. We're now planning on moving one of the valves onto an FBM200 card, 
with temp wiring from one cabinet to another (messy), this will probably 
solve it.........

Since we do not have the means to change all of the FBM100's for 200's I'm 

hoping there's another solution, but sofar we haven't been able to find 
any....I ran out of inspiration....

Problem seems to be related to the use of ZCP270, FBM41 with PLB's. We 
didn't have this kind of problem with the CP60's.

Suggestions anyone?

Thanks & Rgds,

Dirk 

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: