Corey,

We have a couple of FBM224s communicating with GE Multilin 469s in a 2300v
MCC. One installation has six starters on one 485 network and the other has
4 with room for 2 more. 

I can not tell you exactly how much delay one or more of the slaves being
powered off adds to the network cycle time, but I can say we have not noted
any perceivable increase in the delay to start or stop one of these devices.

We have an outage coming up at the end of the month; maybe I will do some
testing.

Our MCCs are wired with a test switch. The test switch allows for the
control circuits to be powered up with the bucket racked out. The 110v power
comes from a source other that the control power transformer. These lineups
are fairly new and they met code when installed.

Regards,
Bob Wingard

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Corey R Clingo
Sent: Friday, July 06, 2007 6:06 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] FBM224-multiple slaves on one port

I haven't looked at the docs yet to see what information is available from 
the starters.  But regardless, I doubt I'll be able to talk anyone into 
reversing the breaker-starter order;  the breaker is used to deenergize 
the bucket itself (and never mind the possible NEC implications).  I'm 
probably making more out of this than is there; the bucket will remain 
energized if the motor is hooked up in the field regardless, to keep the 
dryers/heaters activated.  If the motor is disconnected, say for repair, 
we would probably just offline (you heard it verbed here first, folks) the 
device in system management, which I presume would prevent it from being 
polled.

We are hooking up a non-critical daisy-chain setup in my other plant soon, 
so I'll probably test some of these theories on that string.


Best Regards,

Corey Clingo
BASF Corporation






"Kevin Fitzgerrell" <fitzgerrell@xxxxxxxxx> 
Sent by: foxboro-bounce@xxxxxxxxxxxxx
07/06/2007 05:33 PM
Please respond to
foxboro@xxxxxxxxxxxxx


To
foxboro@xxxxxxxxxxxxx
cc

Subject
Re: [foxboro] FBM224-multiple slaves on one port





Corey,

Last time I looked at a similar project I didn't get specs until too
late, but it looked like the best solution would leave the starters
online with the breaker downstream.  Ours had several parameters that
would have been convenient to monitor even while racked out.

Regards,

Kevin FitzGerrell



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: