Question: But there could still be design and/or installation issues which is why I also asked a 2nd question; why is it suspect? Answer: I think that he is grasping at straws, the 20% level swing from cool of night to heat of day is causing him some heartburn. Once I have the measurements I asked for I think I can help him understand what is going on. Question: Is your installation based on a dry or wet reference leg, could there be condensate in the dry reference leg, where is the condensate pot located, etc.? Answer: It is a dry leg installation. They have experience some issues with this, but think that the local instrument tech has now resolved this or at least is making an attempt to. I suggested that he introduce a loop above the top of the tank. This has worked well for me in the past. Trending the last 24 hours we had a 3 DegF temp swing and a 7 psig deviation. Thanks Troy ************************** Troy Brazell DCP Midstream ISA CCST Sr. Process Control Analyst Office 405-605-3877 Cell 405-301-2994 tlbrazell@xxxxxxxxxxxxxxxx ************************** -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Joseph M. Riccardi Sent: Wednesday, September 01, 2010 2:10 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Compensated Level Indication Troy, The point we need to make with your plant manager is that you are already doing pressure compensation with the way you have piped the transmitter. It is inherent with the design. But there could still be design and/or installation issues which is why I also asked a 2nd question; why is it suspect? Is your installation based on a dry or wet reference leg, could there be condensate in the dry reference leg, where is the condensate pot located, etc.? A lot of work without a good reason to suspect the existing installation and measurement accuracy. If the installation is clean, then temperature compensation could be easily added if necessary. I would perform a simple hand calculation based on your typical temperature swings to estimate the potential error as a result of no temperature compensation. The final question to your plant manager would be "What is an acceptable error (.0008 per degree change)?" Next... Joseph M. Riccardi DCS Services - Industrial Process Control North-Central Office (OH, PA, MI, IN, WV area) South-East Office (FL, GA, AL, SC, NC area) "To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity." - Donald A. Adams -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Brazell, Troy L Sent: Wednesday, September 01, 2010 2:46 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Compensated Level Indication Thanks Joseph. The transmitter is tubed just as you described. I have done the Boiler applications that the list has been talking about, but with propane, from the research that I have done, I really don't know why this plant manager thinks that he need any compensation. I took the GPA physical properties for propane and interpolated the density and unless my calculations are totally wrong the density only changes about .0008 per degree. Not enough to worry about. I guess what I was really looking for is there a real need for doing compensation on most level applications and if so how would one do this outside of using a MV transmitter? A little history on this case; Twice in the last year they had a loss of their refrigerant propane do to operator error. As usual they want something to "monkey proof" the system. I can do rate of change alarming or something similar which should do what they are asking. The normal swing in this surge tank is about 20% from the heat of day until the cool of night (demand) and the level is not maintained at a constant level. When the level gets low enough they will order a transport load and shove it into the surge tank, so it can be all over the place. I am still waiting for the local folks to send the tap location dimensions so that I can run some calculations. It could be that 20% is only a few hundred gallons. Thanks ************************** Troy Brazell DCP Midstream ISA CCST Sr. Process Control Analyst Office 405-605-3877 Cell 405-301-2994 tlbrazell@xxxxxxxxxxxxxxxx ************************** -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Joseph M. Riccardi Sent: Wednesday, September 01, 2010 12:54 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Compensated Level Indication Folks, In reading some of the responses and suggestions to Troy's inquiry, I have now been waiting for some of the old boiler control experts to chime in before possibly embarrassing myself by making another bid. Old boiler control experts; another dying breed? Where is Fred Devore when I need him? Hope he is still enjoying his retirement in Raccoon Lake, IN. IMHO, and with all due respect, I would not get side tracked with the drum level comparisons. Yes, it also has its unique characteristics (as many of them were listed in the responses) but they are different from the propane level application Troy is looking at. As for the reference to the steam tables, I suspect they were required for the mass steam flow calculation, not for the drum level measurement. The steam table properties are needed because of the different properties associated with saturated steam (there is a relationship between the saturation temperature and the pressure) vs. superheated steam (no direct relationship between temperature and pressure) et al. If I can back up 1 step, I would get answers to the following questions: * How is the existing propane level transmitter piped? o Is it piped the way I suggested below (low pressure side of the dP level transmitter connected to the top of the tank)? * If yes, why is there a request for the pressure compensation (why is it suspect?)? * If no, how is it piped? Once we address the pressure compensation issues, the temperature side of the equation is easy. Joseph M. Riccardi DCS Services - Industrial Process Control North-Central Office (OH, PA, MI, IN, WV area) South-East Office (FL, GA, AL, SC, NC area) Joe@xxxxxxxxxxxxx "To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity." - Donald A. Adams -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Joseph M. Riccardi Sent: Tuesday, August 31, 2010 8:33 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Compensated Level Indication Troy, I have been waiting for all of the measurement experts to chime in before possibly embarrassing myself but it seems they are few and far between. Another dying breed? I am certainly no expert but I'll throw my 2 cents on the table to start the bidding process. In a closed tank pressurized system, the only pressure compensation required on the level measurement is from the pressure in the vapor space above the liquid; no? Isn't the low pressure side of the dP level transmitter connected to the top of the tank; this is called the reference leg? This reference leg can be dry or wet depending on the application and/or installation. Changes to the vapor pressure are automatically compensated for in the same way as the effect of barometric pressure changes are canceled out in open tanks (low pressure side of the dP level transmitter is open to atmosphere). Temperature changes affect the Specific Gravity but I think this is a straight forward calculation that must be included. Any help so far or should I fold them... Joseph M. Riccardi DCS Services - Industrial Process Control North-Central Office (OH, PA, MI, IN, WV Area) South-East Office (FL, GA, AL, SC, NC Area) "To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity." - Donald A. Adams -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Brazell, Troy L Sent: Tuesday, August 31, 2010 12:12 PM To: foxboro@xxxxxxxxxxxxx Subject: [foxboro] Compensated Level Indication All knowing list, I have had a request thrown at me that I have never had before. This plant is asking for pressure and temperature compensated level indication on a propane refrigerant surge tank. I have the dP level, head pressure and vapor temperature. Has anyone done this? Thanks Troy ************************** Troy Brazell DCP Midstream ISA CCST Sr. Process Control Analyst Office 405-605-3877 Cell 405-301-2994 tlbrazell@xxxxxxxxxxxxxxxx ************************** _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave