Re: [foxboro] Common Alarm Group - try run ksh

  • From: Hizamri Johari <hizamri@xxxxxxxxxxxxx>
  • To: foxboro@xxxxxxxxxxxxx
  • Date: Sun, 23 Feb 2014 13:48:42 +0800

Dear Pablo

I tried these syntax on our IA 8.8 :

"Silence Horn" "run ksh /usr/fox/alarms/silence.bat" on a menu ( xxx.mnu 
) file..

I have also tried on a display bar ( xxx.dbr ) file :

dmcmd dbar_button 16 "dmcmd run ksh /usr/fox/alarms/silence.bat" -l 
"Silence Horns"

with the content of silence.bat:

pref -WS7002 amcmd "silence_horns"
pref -WS7003 amcmd "silence_horns"
pref -WS7012 amcmd "silence_horns"
pref -WS7013 amcmd "silence_horns"


I think most if not all IA commands default to a D: drive...

Both work silently, without any windows command box annoyance..

Better yet, change the silence.bat extension to silence.ksh to avoid any 
confusion with other dos batch command file...

God knows best..
Best regards..
Hizamri

On 2/21/2014 2:48 AM, Pablo Lioi wrote:

Ignacio,
Thanks! I've already solved the problem - in a way - after finding an 
oldpost of yours in the archive.


What I did:


***Sidebar button in Foxview***


For each environment, I edited the '.dbr' file and added the following line:


dmcmd dbar_button 16 "dmcmd run startp /min 
d:\usr\fox\alarms\silence.bat" -l "Silence Horns"


***Silence Horns button in CAD***


run startp /min d:\usr\fox\alarms\silence.bat


***batch file***


silence.bat:


d:

cd \usr\fox\system32

pref -WS7002 amcmd "silence_horns"

pref -WS7003 amcmd "silence_horns"

pref -WS7012 amcmd "silence_horns"

pref -WS7013 amcmd "silence_horns"


This works... but there are a couple of  problems:


1 - When I push the sidebar "Silence Horns" button for the first time 
after changing environment, it takes ages for the batch file to silence 
the horns and finish. Operators get nervous and push the button several 
times, resulting in several instances of the batch file running in 
separated command windows. After this, everything works fine.

2 - The "/min" switch doesn't work when the batch file is called from 
theCAD button, so there's an annoying "flash" when the command window 
opensand closes.


Regards,

Pablo


>
>
>
>
>> From: ignacio.queirolo@xxxxxxx
>> To: foxboro@xxxxxxxxxxxxx
>> Subject: Re: [foxboro] Common Alarm Group
>> Date: Thu, 20 Feb 2014 18:00:42 +0000
>>
>> Pablo, check the following links:
>> //www.freelists.org/post/foxboro/foxboro-HyperSnap-6,7
>> //www.freelists.org/post/foxboro/foxboro-Run-a-bat-Windows-in-a-Foxview-Button,3
>>
>> Regards
>>
>> -----Mensaje original-----
>> De: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]En 
>> nombre de Pablo Lioi
>> Enviado el: miércoles, 12 de febrero de 2014 18:40
>> Para: foxboro@xxxxxxxxxxxxx
>> Asunto: Re: [foxboro] Common Alarm Group
>>
>> Ok, this is what I did:
>>
>>
>> 1- I created a script in my WS7003 workstation (silence.scp) with the 
>> following text:
>>
>>
>>
>> #!/bin/sh
>> pref -WS7013 amcmd "silence_horns"
>>
>>
>>
>> Note: WS7003 and WS7013 are in DIFFERENT CAG's
>>
>>
>>
>> 2 - With the horn sounding in WS7013, I run the script from the command line 
>> in WS7003 and verified that the horn is silenced, as expected.
>>
>>
>>
>> 3 - With ADMC I modified the action of the "Silence horn" button to:
>>
>>
>>
>> silence_horns
>>
>> run /usr/fox/alarms/silence.bat
>>
>>
>>
>> The first line takes care of the horns in the CAG and the second line 
>> silences the horns of the workstations outside of the CAG.
>>
>>
>>
>> Note that I had to write a batch file for the "run" command. I tried the 
>> "script /usr/fox/alarms/silence.scp" first, but it didn't work.
>>
>>
>>
>> This is the text of the silence.bat file:
>>
>>
>>
>> d:
>>
>> cd \usr\fox\alarms
>>
>> call \nutc\bin\ncenv.cmd
>>
>> \nutc\mksnt\sh.exe silence.scp
>>
>>
>>
>> With this configuration, pressing the "Silence horns" button in the CAD 
>> silences both the horns in all workstations.
>>
>>
>> PROBLEM: there's an annoying "flash" after pressing the "Silence horns" 
>> button, when the command line window opens and closes.
>>
>>
>>
>> 4 - There's a "Silence horns" button in the Foxview button bar. I tried to 
>> modify the dbr environment file to launch the script, but failed. The sintax 
>> I tried was:
>>
>>
>>
>> dmcmd dbar_button 16 "dmcmd run /usr/fox/alarms/silence.bat" -l "Silence 
>> horns"
>>
>>
>>
>> Is there a better way of calling the script from a CAD button (and a menu 
>> bar button)?
>>
>>
>>
>> Regards,
>>
>> Pablo
>>
>>
>>
>>> From: Russ.Boulay@xxxxxxxxxxxx
>>> To: foxboro@xxxxxxxxxxxxx
>>> Date: Wed, 12 Feb 2014 10:16:20 -0500
>>> Subject: Re: [foxboro] Common Alarm Group
>>>
>>> I believe the second CAG group approach would still clear all alarms in 
>>> both groups.
>>>
>>> You need to set a standard for horn silence.....like a button on graphic or 
>>> annun keyboard that will run the pref command to all workstations to 
>>> silence horns.
>>> Silence 4 workstations
>>>
>>> #!/bin/sh
>>> pref -AMNAME amcmd "silence_horns"
>>> pref -AMNAME amcmd "silence_horns"
>>> pref -AMNAME amcmd "silence_horns"
>>> pref -AMNAME amcmd "silence_horns"
>>>
>>> ______________________________________________________________________
>>> _______________
>>>
>>> Russ Boulay | Schneider Electric | Invensys | United States | Support
>>> Engineering Manager
>>> Phone: +1 508 446 1769 | Mobile: +1 508 446 1769
>>> Email: russ.boulay@xxxxxxxxxxxx | Site: www.invensys.com | Address:
>>> 2000 Crow Canyon Place Suite 170, 94583 San Ramon, California, United
>>> States
>>>
>>> *** Please consider the environment before printing this e-mail
>>>
>>> -----Original Message-----
>>> From: foxboro-bounce@xxxxxxxxxxxxx
>>> [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of
>>> martin.theobald@xxxxxxxxx
>>> Sent: Wednesday, February 12, 2014 7:00 AM
>>> To: foxboro@xxxxxxxxxxxxx
>>> Subject: Re: [foxboro] Common Alarm Group
>>>
>>> Pablo,
>>> Each workstation can be in up to two Common Alarm Groups (CAGs). Use the 
>>> 'CAG NAME2' field in the <commgrp.cfg> file to set up a second overall 
>>> group for all four workstations. Make sure that the change is made on all 
>>> of the workstations to be affected. Each workstation will need to be 
>>> rebooted to make the change effective.
>>>
>>> See document B0700AT Workstation Alarm Management for further details.
>>> The are also a number of FAQ/SOL notes on the GCS site.
>>>
>>>
>>> Regards,
>>>
>>> Martin Theobald
>>>
>>> -------------------------------------------------
>>> eControl - Runcorn
>>> INEOS Chlor Vinyls
>>>
>>> M: +44 7767 87 1989
>>> T: +44 1928 51 2044
>>> F: +44 1928 51 6653
>>> -------------------------------------------------
>>>
>>>
>>>
>>> From: Pablo Lioi <plioi@xxxxxxxxxxx>
>>> To: "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>,
>>> Date: 12/02/2014 14:32
>>> Subject: [foxboro] Common Alarm Group
>>> Sent by: foxboro-bounce@xxxxxxxxxxxxx
>>>
>>>
>>>
>>> Hello all,
>>> In our control room, we have four I/A 8.4.3 XP operator workstations.
>>>
>>> Operators wanted the workstations grouped in pairs for alarm management.
>>> So I configured two alarm groups, with 2 WS each (say WS1/2 and WS3/4), and 
>>> set the clear alarm option to "Delete alarm throughout the CAG".
>>> Everything worked as expected.
>>>
>>> But there is a problem: operators want the "Silence Horns" function to work 
>>> on both groups at the same time (i.e., pressing the "Silence Horns"
>>> button in any workstation silences horns in all workstations). For what I 
>>> know, it can't be done...
>>>
>>> As an alternative, I could put all the workstations back in the same
>>> CAG to solve the "Silence Horns" problem, but I would need some trick
>>> to make the clear and ack alarm function work in pairs (i.e., clearing
>>> alarms in WS 1 also clears alarms in WS 2 and vice-versa, but doesn't
>>> affect WS 3 and 4; clearing alarms in WS 3 also clears alarms in WS 4
>>> and vice-versa, but doesn't affect WS 1 and 2)
>>>
>>> As for why would anybody want to group 4 WS that are a few feet apartfrom 
>>> each other in two groups... well, it's one of those Operations things.
>>>
>>> Thanks,
>>>
>>> Pablo Lioi
>>>
>>> TOTAL AUSTRAL S.A.
>>>
>>> Tierra del Fuego - Argentina
>>>
>>>
>>>
>>>
>>>
>>> ______________________________________________________________________
>>> _ This mailing list is neither sponsored nor endorsed by Invensys
>>> Process Systems (formerly The Foxboro Company). Use the info you
>>> obtain here at your own risks. Read
>>> http://www.thecassandraproject.org/disclaimer.html
>>>
>>> foxboro mailing list: //www.freelists.org/list/foxboro
>>> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
>>> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>>>
>>>
>>> INEOS is a trade mark, the property of INEOS Capital Limited. The "Bubble 
>>> Logo", CERECLOR, DX PLUS, MEFLEX, METHOKLONE, PERKLONE, SOLVE-CARE, 
>>> TRIKLONE and TRISEC are trade marks, the property of INEOS ChlorVinyls 
>>> Limited. CEREPLAS, DIRECT SALT, HYDROSOFT, LINDROX AND WHITEROX are trade 
>>> marks, the property of INEOS Enterprises Limited. BICHLOR, CHLORCOAT, FM 
>>> and PEMcoat are trade marks, the property of INEOS Technologies Limited. 
>>> EVIPOL is a trade mark, the property of INEOS Vinyls UK Limited.
>>>
>>>
>>>
>>>
>>> ______________________________________________________________________
>>> _ This mailing list is neither sponsored nor endorsed by Invensys
>>> Process Systems (formerly The Foxboro Company). Use the info you
>>> obtain here at your own risks. Read
>>> http://www.thecassandraproject.org/disclaimer.html
>>>
>>> foxboro mailing list: //www.freelists.org/list/foxboro
>>> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
>>> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>>>
>>>
>>>
>>> *** Confidentiality Notice: This e-mail, including any associated or 
>>> attached files, is intended solely for the individual or entity to which it 
>>> is addressed. This e-mail is confidential and may well also be 
>>> legallyprivileged. If you have received it in error, you are on notice of 
>>> its status. Please notify the sender immediately by reply e-mail and then 
>>> delete this message from your system. Please do not copy it or use it for 
>>> anypurposes, or disclose its contents to any other person. This email 
>>> comesfrom a division of the Invensys Group, owned by Invensys plc, which is 
>>> acompany registered in England and Wales with its registered office at 3rd 
>>> Floor, 40 Grosvenor Place, London, SW1X 7AW (Registered number 166023).For 
>>> a list of European legal entities within the Invensys Group, please select 
>>> the Legal Entities link at invensys.com. Invensys PLC is owned by the 
>>> Schneider-Electric Group.
>>>
>>> You may contact Invensys plc on +44 (0)20 3155 1200 or e-mail 
>>> reception@xxxxxxxxxxxx. This e-mail and any attachments thereto may be 
>>> subject to the terms of any agreements between Invensys (and/or its 
>>> subsidiaries and affiliates) and the recipient (and/or its subsidiaries and 
>>> affiliates).
>>>
>>>
>>>
>>>
>>> ______________________________________________________________________
>>> _ This mailing list is neither sponsored nor endorsed by Invensys
>>> Process Systems (formerly The Foxboro Company). Use the info you
>>> obtain here at your own risks. Read
>>> http://www.thecassandraproject.org/disclaimer.html
>>>
>>> foxboro mailing list: //www.freelists.org/list/foxboro
>>> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
>>> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>>>
>>
>>
>> _______________________________________________________________________
>> This mailing list is neither sponsored nor endorsed by Invensys Process 
>> Systems (formerly The Foxboro Company). Use the info you obtain here atyour 
>> own risks. Read http://www.thecassandraproject.org/disclaimer.html
>>
>> foxboro mailing list: //www.freelists.org/list/foxboro
>> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
>> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>>
>> AVISO LEGAL: Esta información es privada y confidencial y está dirigida 
>> únicamente a su destinatario. Si usted no es el destinatario original de 
>> este mensaje y por este medio pudo acceder a dicha información por favor 
>> elimine el mensaje. La distribución o copia de este mensaje está 
>> estrictamente prohibida. Esta comunicación es sólo para propósitos de 
>> información y no debe ser considerada como propuesta, aceptación ni como una 
>> declaración de voluntad oficial de YPF S.A. y/o subsidiarias y/o afiliadas. 
>> La transmisión de e-mails no garantiza que el correo electrónico sea seguro 
>> o libre de error. Por consiguiente, no manifestamos que esta información sea 
>> completa o precisa. Toda informaciónestá sujeta a alterarse sin previo 
>> aviso. This information is private and confidential and intended for the 
>> recipient only. If you are not the intended recipient of this message you 
>> are hereby notified that any review, dissemination, distribution or copying 
>> of this message is strictly prohib
>   it
>> ed. This communication is for information purposes only and shall not be 
>> regarded neither as a proposal, acceptance nor as a statement of will or 
>> official statement from YPF S.A. and/or subsidiaries and/or affiliates. 
>> Email transmission cannot be guaranteed to be secure or error-free. 
>> Therefore, we do not represent that this information is complete or accurate 
>> and it should not be relied upon as such. All information is subject to 
>> change without notice.
>>
>>
>> _______________________________________________________________________
>> This mailing list is neither sponsored nor endorsed by Invensys Process
>> Systems (formerly The Foxboro Company). Use the info you obtain here at
>> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>>
>> foxboro mailing list: //www.freelists.org/list/foxboro
>> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
>> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>>
>                                       
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list:             //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>
>


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: