I have learned from a highly placed source inside the company that due to
the resolution of the real-time clock (20 ms), the accuracy of each loading
calculation is as follows:

         BPC      Max. Error    Usefulness
  
         0.1 s     20.0 %       not very
         0.2 s     10.0 %       marginal
         0.5 s      4.0 %       OK
         1.0 s      2.0 %       OK
         2.0 s      1.0 %       OK

Thus, it is not that the STATION block does not work at faster BPCs, but
that the measurement accuracy degrades substantially when the BPC is less
than 0.5s (500ms).

Does this make sense?

Regards

Alex Johnson