Re: [foxboro] CP280 Power Fails

  • From: "Ismael_Reyes@xxxxxxxxxxxxx" <Ismael_Reyes@xxxxxxxxxxxxx>
  • To: "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>
  • Date: Mon, 2 Dec 2019 14:52:40 +0000

Wondering if this is similar to "MP47481162 Release Notes"?
We had problem identical to MP47481162 on a particular asset.

Seems these notes corrected w/o MEP but required waiting for downtime.
MEP/MRP may be a way to correct w/o downtime.

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> On Behalf Of 
Maks Wilde
Sent: Wednesday, November 27, 2019 3:43 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] CP280 Power Fails

MEP - Module Exchange Program.
If you have a Customer First contract you likely have access to this program.
Cheers!


Maks Wilde
Senior Process Control Engineer
https://urldefense.com/v3/__http://www.kicsystems.ca__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_dwXa7hNg$
 

On Wed, Nov 27, 2019 at 2:59 PM Sergio Fagundes <sergiofagundes77@xxxxxxxxx>
wrote:

Hello Maks,

We have experienced the same warnings. And we replaced the hw of 
primary CP. After that don’t have anymore alarms.

But about your information “ Their final recommendation was to MEP all 
FCP280 pairs exhibiting the issue. This fixed the problem.” What do 
you mean “MEP”?

Att,
Sérgio Fagundes

Enviado via iPhone

Em 27 de nov de 2019, à(s) 15:23, Maks Wilde <makswilde@xxxxxxxxx>
escreveu:

Hi Roger,
I've seen this problem at multiple sites. It became worse over time, 
spamming the smon_log to such extent that we had to inhibit the 
alarming
on
the FCPs in question (not great). Working with TAC over a few months 
we upgraded the firmware multiple times. Their final recommendation 
was to
MEP
all FCP280 pairs exhibiting the issue. This fixed the problem.

Best Regards,

Maks Wilde
Senior Process Control Engineer
https://urldefense.com/v3/__http://www.kicsystems.ca__;!332wCyZQUuk!
eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_dwXa7h
Ng$

On Wed, Nov 27, 2019 at 11:55 AM Smith, Roger <rsmith@xxxxxxx> wrote:

Thanks Tony,

We'll check that out.

Roger Smith
Process Control
Green Bay Packaging
Arkansas Kraft Division
Desk (501)354-9569
Mobile (501) 208-7635
Email: rsmith@xxxxxxx


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> 
On Behalf Of Stankiewicz, Anthony P.
Sent: Wednesday, November 27, 2019 10:12 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] CP280 Power Fails

Roger,
Not sure if this is related to your problem, but there is also a 
kit
for a
ferrite core that goes onto the power cables right next to the plug 
at
the
CP baseplate.
See Customer Advisory FCP280, FDC280, and CNI Power Cable Ferrite 
Core Requirements, June 5, 2019 Advisory states the following:
Ferrite cores are used to suppress electromagnetic interference (EMI).
It
is better to attenuate system interference presence detected at the
source
before they find their way to multiple high frequency "sneak" paths.
Once
the EMI noise is in the system, it can easily migrate through the 
ground system as common mode EMI noise.
These ferrite cores must be installed on all FCP280, FDC280, and 
CNI baseplate input power cables to make the EMI emissions and 
immunity
levels
fall within the parameters of the EMC directives.
Ferrite cores must be installed on the DC Power cables, as near to 
the baseplate as possible, to ensure proper and stable module 
communications and installation compliance with EU Directive 
2014/30/EU on
Electromagnetic
Compatibility.
Review your installation to determine if you have ferrite cores
installed
and they are completely clamped in place. If you require new 
ferrite
cores,
kit AG101EL can be ordered by contacting your local support office. 
Each kit will contain (2) BF162YG ferrite cores, (4) cable tie 
wraps and
special
instructions.
For orders received prior to June 30, 2022, there will be no charge 
for these kits. After this date, ferrites will be available at 
standard
pricing.

Regards,
Tony Stankiewicz

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> 
On Behalf Of Russell Boulay
Sent: Wednesday, November 27, 2019 10:56 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] CP280 Power Fails

EXTERNAL MAIL: Caution Opening Links or Files

________________________________

What FCP280 image you running.?

Images above 092024 have compensation for modules with intermittent 
reporting of Power Fail messages.




-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> 
On Behalf Of Smith, Roger
Sent: Wednesday, November 27, 2019 7:46 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] CP280 Power Fails

[External email: Use caution with links and attachments]

________________________________



We have 4 sets of FT pairs of the CP280.

Roger Smith
Process Control
Green Bay Packaging
Arkansas Kraft Division
Desk (501)354-9569
Mobile (501) 208-7635
Email: rsmith@xxxxxxx


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> 
On Behalf Of Smith, Roger
Sent: Wednesday, November 27, 2019 9:41 AM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] CP280 Power Fails

Hello All,
For the 2nd time we have had a CP280 start to show failures in 
baretail/sysmon log.  We only have a total of 4 CP280's at our site.

Example:

2019-05-20 04:35:17 25CP01 Equip = CHAN_1 SYSMON -00222 CP Power 2
failed
2019-05-20 04:35:17 25CP01 Equip = CHAN_1 SYSMON -00223 CP_Power 2 
OK

The failures do not cause the system light to flash green, no * on 
the
CP,
but only show up in the log.  The fault occurs and clears within 
the
same
second.  And they occurred progressively more often over time (a 
couple
of
weeks) Power supplies and connections all look good.  Disconnecting 
a
power
connection causes the exact same error.  The first time it occurred 
we changed the shadow module but the errors re-occurred.  We then 
replaced
the
other partner and the problem went away.  Now the problem has shown 
up again on another CP in another area.  We have replaced the 
shadow on
that
one and are waiting to see if the errors return.  When I called 
them
about
this on the first occurrence TAC told me they had seen this before, 
it
was
something about an optocoupler inside the CP and was not a real 
power failure.

This time the errors say "CP Power 1" instead of 2.

Anyway, just curious if anyone else has experienced this.  Could it
really
bite us?
Happy Thanksgiving!

Roger Smith
Process Control
Green Bay Packaging




______________________________________________________________________
___
This mailing list is neither sponsored nor endorsed by Schneider
Electric
(formerly The Foxboro Company).  Use the info you obtain here at 
your
own
risks.  See the disclaimer at

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=https*3A*2F*2Furldefense.proofpoint.com*2Fv2*2Furl*3Fu*3Dhtt
ps-3A__eur02.safelinks.protection.outlook.com_-3Furl-3Dwww.thecassandr
aproject.org-252Fdisclaimer.html-26amp-3Bdata-3D02-257C01-257Cruss.bou
lay-2540se.com-257Ccfa5a28551fe4baa1bc608d773510adf-257C6e51e1adc54b4b
39b5980ffe9ae68fef-257C0-257C0-257C637104664228812333-26amp-3Bsdata-3D
QHJf21rfONZ-252BLAF6vWWA9ZLGssQa-252FW5OhEq2DRnnh60-253D-26amp-3Breser
ved-3D0*26d*3DDwIDAg*26c*3DAgWC6Nl7Slwpc9jE7UoQH1_Cvyci3SsTNfdLP4V1RCg
*26r*3DJLvVFUtR2GVf4nldLBjwX6He_7ZkRP-esYv50YY3HqA*26m*3DhmH7wfGVyH1r6
Z46btNsJpQrHrIQFTa8lIVrBUQOY0s*26s*3DoSkjt44HkiTT27jndXRbnEnjPyPakrVEM
76yGAihXME*26e&amp;data__;JSUlJSUlJSUlJSUlJSUlJSUl!332wCyZQUuk!eVj4Wg-
vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_eVmDWkXw$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C63710467940536352

8&amp;sdata=P9MrQ083NdkKaepg0l9gwvnequsb3CE01BWlelfniQ4%3D&amp;reserve
d=0=

foxboro mailing list:

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=https*3A*2F*2Furldefense.proofpoint.com*2Fv2*2Furl*3Fu*3Dhtt
ps-3A__eur02.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-
252Fwww.freelists.org-252Flist-252Ffoxboro-26amp-3Bdata-3D02-257C01-25
7Cruss.boulay-2540se.com-257Ccfa5a28551fe4baa1bc608d773510adf-257C6e51
e1adc54b4b39b5980ffe9ae68fef-257C0-257C0-257C637104664228812333-26amp-
3Bsdata-3DrkSFmzCFb7UxgB-252BtTLwqGGeFw2FHWW-252FIREy0D5An7Ik-253D-26a
mp-3Breserved-3D0*26d*3DDwIDAg*26c*3DAgWC6Nl7Slwpc9jE7UoQH1_Cvyci3SsTN
fdLP4V1RCg*26r*3DJLvVFUtR2GVf4nldLBjwX6He_7ZkRP-esYv50YY3HqA*26m*3DhmH
7wfGVyH1r6Z46btNsJpQrHrIQFTa8lIVrBUQOY0s*26s*3DlIFSd5izeVeIr_A04b8XXcd
W4cgS7lxIWriLWo2pwwo*26e&amp;data__;JSUlJSUlJSUlJSUlJSUlJSUl!332wCyZQU
uk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_eREsZ
U_g$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C637104679405373521&amp;sdata=%2BPn4k1Less2q3UYTemGyr8L5p%2B
Uu3GU1gaO2jRTJGNw%3D&amp;reserved=0=
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx
?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx
?subject=leave





______________________________________________________________________
___
This mailing list is neither sponsored nor endorsed by Schneider
Electric
(formerly The Foxboro Company).  Use the info you obtain here at 
your
own
risks.  See the disclaimer at

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=https*3A*2F*2Furldefense.proofpoint.com*2Fv2*2Furl*3Fu*3Dhtt
ps-3A__eur02.safelinks.protection.outlook.com_-3Furl-3Dwww.thecassandr
aproject.org-252Fdisclaimer.html-26amp-3Bdata-3D02-257C01-257Cruss.bou
lay-2540se.com-257Ccfa5a28551fe4baa1bc608d773510adf-257C6e51e1adc54b4b
39b5980ffe9ae68fef-257C0-257C0-257C637104664228812333-26amp-3Bsdata-3D
QHJf21rfONZ-252BLAF6vWWA9ZLGssQa-252FW5OhEq2DRnnh60-253D-26amp-3Breser
ved-3D0*26d*3DDwIDAg*26c*3DAgWC6Nl7Slwpc9jE7UoQH1_Cvyci3SsTNfdLP4V1RCg
*26r*3DJLvVFUtR2GVf4nldLBjwX6He_7ZkRP-esYv50YY3HqA*26m*3DhmH7wfGVyH1r6
Z46btNsJpQrHrIQFTa8lIVrBUQOY0s*26s*3DoSkjt44HkiTT27jndXRbnEnjPyPakrVEM
76yGAihXME*26e&amp;data__;JSUlJSUlJSUlJSUlJSUlJSUl!332wCyZQUuk!eVj4Wg-
vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_eVmDWkXw$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C63710467940537352


1&amp;sdata=5PTj7S4KQ%2F8%2FxJwgemyK%2FxVOJ1LFKovMpOBml09cTcA%3D&amp;r
eserved=0=

foxboro mailing list:

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=https*3A*2F*2Furldefense.proofpoint.com*2Fv2*2Furl*3Fu*3Dhtt
ps-3A__eur02.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-
252Fwww.freelists.org-252Flist-252Ffoxboro-26amp-3Bdata-3D02-257C01-25
7Cruss.boulay-2540se.com-257Ccfa5a28551fe4baa1bc608d773510adf-257C6e51
e1adc54b4b39b5980ffe9ae68fef-257C0-257C0-257C637104664228822326-26amp-
3Bsdata-3Dffl0vajLUQT0WWfm58IlazI-252FC35mfmQCVmUsFVB6K5g-253D-26amp-3
Breserved-3D0*26d*3DDwIDAg*26c*3DAgWC6Nl7Slwpc9jE7UoQH1_Cvyci3SsTNfdLP
4V1RCg*26r*3DJLvVFUtR2GVf4nldLBjwX6He_7ZkRP-esYv50YY3HqA*26m*3DhmH7wfG
VyH1r6Z46btNsJpQrHrIQFTa8lIVrBUQOY0s*26s*3D_5TqDi1uW6VHlzXslJkUaLLdjwU
uwoiDpkmN7Im9WGI*26e&amp;data__;JSUlJSUlJSUlJSUlJSUlJSUl!332wCyZQUuk!e
Vj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_eLzIzZ2A$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C637104679405373521&amp;sdata=ytXv4PxvGv1S2pSsvWghfhG6y63%2F
AmD10wQHxgvwnX4%3D&amp;reserved=0=
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx
?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx
?subject=leave



___________________________________________________________________
___ This email has been scanned by the Symantec Email 
Security.cloud
service.
___________________________________________________________________
___



______________________________________________________________________
___
This mailing list is neither sponsored nor endorsed by Schneider
Electric
(formerly The Foxboro Company).  Use the info you obtain here at 
your
own
risks.  See the disclaimer at

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=https*3A*2F*2Furldefense.proofpoint.com*2Fv2*2Furl*3Fu*3Dhtt
p-3A__www.thecassandraproject.org_disclaimer.html*26d*3DDwIDAg*26c*3DA
gWC6Nl7Slwpc9jE7UoQH1_Cvyci3SsTNfdLP4V1RCg*26r*3DJLvVFUtR2GVf4nldLBjwX
6He_7ZkRP-esYv50YY3HqA*26m*3DhmH7wfGVyH1r6Z46btNsJpQrHrIQFTa8lIVrBUQOY
0s*26s*3DVOKcCeqIPb9bL61QOUOCVMzf_QFdAFSwraGknNzFjNQ*26e&amp;data__;JS
UlJSUlJSUlJSUlJSUlJSUl!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcd
MI1ltLPqgJS3LWkIHvPQnkbHKC_daTwOlig$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C637104679405373521&amp;sdatafVxIOyv2kCpZQ%2FGnWPlGLG4bM39ys
w%2FYnBv%2Bec1CI0%3D&amp;reserved=0=

foxboro mailing list:

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=https*3A*2F*2Furldefense.proofpoint.com*2Fv2*2Furl*3Fu*3Dhtt
p-3A__www.freelists.org_list_foxboro*26d*3DDwIDAg*26c*3DAgWC6Nl7Slwpc9
jE7UoQH1_Cvyci3SsTNfdLP4V1RCg*26r*3DJLvVFUtR2GVf4nldLBjwX6He_7ZkRP-esY
v50YY3HqA*26m*3DhmH7wfGVyH1r6Z46btNsJpQrHrIQFTa8lIVrBUQOY0s*26s*3DVoO6
ZHF2EQlqyXWGQ2JLYb6wvNRXvqPbUmwfX-FmBTw*26e&amp;data__;JSUlJSUlJSUlJSU
lJSUlJSUl!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3L
WkIHvPQnkbHKC_cB4xC1ig$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C637104679405373521&amp;sdata=ZLP3ctiBjh%2B5t1tOk41qPJrLnAEF
zrU0Qi6jeu9ZocI%3D&amp;reserved=0=
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx
?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx
?subject=leave





______________________________________________________________________
___
This mailing list is neither sponsored nor endorsed by Schneider
Electric
(formerly The Foxboro Company).  Use the info you obtain here at 
your
own
risks.  See the disclaimer at

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=www.thecassandraproject.org*2Fdisclaimer.html&amp;data__;JQ!
332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkb
HKC_cXJ4HBkA$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C637104679405373521&amp;sdata=sKZnCHAbI1tQ5SefhWmnDKFmIEbfDF
ftt3PuHo1Ozxo%3D&amp;reserved=0

foxboro mailing list:

https://urldefense.com/v3/__https://nam02.safelinks.protection.outlook
.com/?url=http*3A*2F*2Fwww.freelists.org*2Flist*2Ffoxboro&amp;data__;J
SUlJSU!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkI
HvPQnkbHKC_feMNoi3g$
%7C01%7Crsmith%40gbp.com
%7Cb5e056ffafdf4c8e304b08d77354936b%7C817907a457054df1a2dfff993531c192
%7C0%7C0%7C637104679405373521&amp;sdataŽiBbkiiCY%2Bl%2BNTaZbppj01J5w%2
B5OreTdt37a9X2%2FpE%3D&amp;reserved=0
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx
?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx
?subject=leave





______________________________________________________________________
___
This mailing list is neither sponsored nor endorsed by Schneider
Electric
(formerly The Foxboro Company).  Use the info you obtain here at 
your
own
risks.  See the disclaimer at
https://urldefense.com/v3/__http://www.thecassandraproject.org/disclai
mer.html__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS
3LWkIHvPQnkbHKC_dByzavXg$

foxboro mailing list:
https://urldefense.com/v3/__//www.freelists.org/list/foxboro__;!3
32wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbH
KC_cOZXSvNQ$
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx
?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx
?subject=leave




--
Confidentiality Warning: This message and any attachments are 
intended
only
for the use of the intended recipient(s), are confidential, and may 
be privileged. If you are not the intended recipient, you are hereby
notified
that any review, retransmission, conversion to hard copy, copying, 
circulation or other use of this message and any attachments is 
strictly prohibited. If you are not the intended recipient, please 
notify the
sender
immediately by return e-mail, and delete this message and any 
attachments from your system.



____________________________________________________________________
_____ This mailing list is neither sponsored nor endorsed by 
Schneider Electric (formerly The Foxboro Company).  Use the info you 
obtain here at your own risks.  See the disclaimer at
https://urldefense.com/v3/__http://www.thecassandraproject.org/disclai
mer.html__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS
3LWkIHvPQnkbHKC_dByzavXg$

foxboro mailing list:
https://urldefense.com/v3/__//www.freelists.org/list/foxboro__;!3
32wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbH
KC_cOZXSvNQ$
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx
?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx
?subject=leave




______________________________________________________________________
___ This mailing list is neither sponsored nor endorsed by Schneider 
Electric (formerly The Foxboro Company).  Use the info you obtain here 
at your own risks.  See the disclaimer at 
https://urldefense.com/v3/__http://www.thecassandraproject.org/disclai
mer.html__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS
3LWkIHvPQnkbHKC_dByzavXg$

foxboro mailing list:               
https://urldefense.com/v3/__//www.freelists.org/list/foxboro__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_cOZXSvNQ$
 
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave




--
Confidentiality Warning: This message and any attachments are intended only for 
the use of the intended recipient(s), are confidential, and may be privileged. 
If you are not the intended recipient, you are hereby notified that any review, 
retransmission, conversion to hard copy, copying, circulation or other use of 
this message and any attachments is strictly prohibited. If you are not the 
intended recipient, please notify the sender immediately by return e-mail, and 
delete this message and any attachments from your system.

 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric 
(formerly The Foxboro Company).  Use the info you obtain here at your own 
risks.  See the disclaimer at 
https://urldefense.com/v3/__http://www.thecassandraproject.org/disclaimer.html__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_dByzavXg$
 
 
foxboro mailing list:               
https://urldefense.com/v3/__//www.freelists.org/list/foxboro__;!332wCyZQUuk!eVj4Wg-vLp-YnC_7SFUzUZKA7eFcKDKLWcdMI1ltLPqgJS3LWkIHvPQnkbHKC_cOZXSvNQ$
 
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: