Chad,
I think you are right that you are overlapping addresses. That is
probably why you got the Duplicate Channel error on the Foxboro side prior to
MODBUS+DUPS modification in ECB201. The PAKIN/PAKOUT blocks read/write 32 bits
by default so if you were reading packed Boolean values with a PAKIN from
MODBUS input register 30001 it would really be reading 16 bits from 30001 and
16 bits from 30002. Likewise, if using a PAKOUT to write holding register
40001 you would be writing 40001 and 40002 by default. For a PAKIN reading
contact input 10001 you would really be reading 10001-10032. To complicate
issues some MODBUS implementations from different vendors require Word/Byte
swaps and some interpret individual bits within the bytes in reverse order.
There are a host of options within the Foxboro MODBUS interface configuration
to reverse engineer all of the crazy things vendors do with MODBUS. If you see
a MODBUS Address Point ID in a Foxboro interface such as 40001:F4:W3 you will
know that the 3rd party vendor has done something funky to bastardize MODBUS
for their advantage.
Although it involves creating more blocks I prefer to use individual
BIN or BOUT blocks instead of PAKIN/PAKOUT blocks when unique discrete values
such as motor run status, valve limit switches, discrete alarm statuses are
being passed to/from 3rd party interfaces. The BIN's and BOUT's read/write
individual bits rather than groups of bits. It is much easier for anyone to
understand exactly which bit is being accessed/written. Beware of the default
feature of the BIN block however. There is a parameter named .SELOPT whose
default value is set to 1. SELOPT = 1 means that the block will always
initialize with a FALSE/ZERO value regardless of what the actual MODBUS
register value currently holds. This means that if the BIN block alarm state
is set to alarm on a FALSE/ZERO input it will alarm anytime the block is
downloaded even if the actual MODBUS value is TRUE/1. It also means that any
downstream logic/shutdown block that uses the BIN's .CIN parameter could get
toggled when modifying/downloading the BIN block. To make the BIN block react
like any other Foxboro block that hold the last value during initialization,
ALWAYS be sure to set .SELOPT = 0. Would really like to locate the programmer
responsible for the default SELOPT=1 setting so I could smack him up side his
boney head;<) Thanks again to Anthony Stankiewicz for tipping me off about
.SELOPT. It is easy to miss when reading the BIN block documentation.

Cheers,
Tom VandeWater
Control Conversions, Inc.

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Chad Ziesemer
Sent: Wednesday, November 18, 2015 1:02 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Anyone using Cutler Hammer SVX drives with Foxboro?

Thanks for the tip Tom, I tried it and DUPS resolves the duplicate address
Foxboro error too. One other thing I'm noticing is if I have the PAKOUT set-up
without the *:C16 or *:C8 addresses (matching the table length provided in the
manual) and I toggle higher numbered bits on the packout, the drive itself
faults on a comms error. I have to have the DUPS parameter in to make this
work or the DCI blocks will show the "duplicate address" error, so I'm assuming
I'm overlapping addresses accidently. I never quite figured out exactly what
addresses on the drive I was toggling, but it was none too happy.


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Vandewater, Tom (HI Contractor)
Sent: Wednesday, November 18, 2015 3:42 PM
To: 'foxboro@xxxxxxxxxxxxx'
Subject: Re: [foxboro] Anyone using Cutler Hammer SVX drives with Foxboro?

Chad,
Great write-up. I have sent similar stuff to the list to document what
I did for future reference for me, (and anyone else it might benefit). I have
even had new work referrals as a result of these postings, (a side benefit of
taking the time to document;<)

One thing you mentioned jumped out at me because it created some problems for
me in the past. You said:
" I ran into a lot of "duplicate address" errors when I put in multiple DCI
blocks."

The child ECB 201 only allows one DCI block reference to a MODBUS contact
input/output or register within its interface. By changing the ECB201 DVOPTS
parameter as shown below you can have duplicate references.

from
DVOPTS: MODBUS
to
DVOPTS: MODBUS+DUPS

Regards,
Tom VandeWater
Control Conversions, Inc.

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Chad Ziesemer
Sent: Wednesday, November 18, 2015 11:27 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Anyone using Cutler Hammer SVX drives with Foxboro?

I wanted to follow-up to stuff the archive for anyone searching in the future,
including myself when I forget how to do this again in 2 weeks. We
successfully have a trial Cutler Hammer drive communicating well with an FBM
232. So far we are able to control anything that can be done with hard I/O and
get any information available from the keypad.
Here's the set-up that worked:
Drive: Cutler Hammer SVX 9000 series
Drive option card: Modbus / TCP IP OPTCI-V, installs in expander slot D
Alternative: Eaton DG-1 series is supposed work exactly the same way but has
the Modbus comms card integrated as standard
Configuration: In the keypad change remote control option to "fieldbus" and
remote reference to "fieldbus".

FBM 232 connected to the comms card through a generic unmanaged Ethernet swtich
(was a Netgear JGS524, will be a phoenix contact) Also connected with a
crossover cable while troubleshooting and that worked as well, the manual says
explicitly it wouldn't work, not sure why.

ECB 200:
DEV_ID: GNBA08
HWTYPE: 232
SWTYPE: 232
PORTEX: 1
FILEID: GNAA08.XML
FSENAB: 0 (default)
FSDLAY: 1000 (default)
WDTMR: 10 (default)
SFILEID: MODBUS.ZIPH
SYSCFG: 1000 (default)
SYSOPT: 0 (default)


ECB 201:
NAME: VFD100
HWTYPE: 232
SWTYPE: 232
PARENT: GNBA08
DVNAME: 192.168.100.100
DVOPTS: MODBUS
PORTNO: 1
ERROPT : 0xFFFE (default)
All other options blank (default)

GNAA08.XML:
IP address: 192.168.100.99
Subnet mask: 255.255.255.0
Default Gateway: 192.168.100.99 (I have no idea what to put here or if it even
matters but it's working)

DCI block for controlling drive:
This is where I had the most troubles, I'm just barely understanding Modbus
life after all of this but it seems to be working well, so take all this with a
grain of salt. I ran into a lot of "duplicate address" errors when I put in
multiple DCI blocks. I learned that I need to add the :C16, :C8, etc in the
PKCOGP (where 16 represents the length of bits? in the address space).
According to the drive comms manual at address 00001 there are 16 consecutive
bits. When I left it without the :C16 it defaults to 32 bits and it didn't
communicate.

Name: CONTROL
Type: PAKOUT
IOM_ID: VFD100
PKCOGP: 00001:C16
PKCOPT: 1
All other values default

Now toggling the following bits does the following (full memory map in the
cutler hamer manual)
IN_1 starts/stops
IN_2 fwd/rev
IN_3 fault reset
IN_4-IN_16 FBDIN1-10, I don't' use these or know what they do yet

Name: FEEDBACK
Type: PAKIN
IOM_ID: VFD100
PKINGP: 10001:C8
PKIOPT: 1
PAKCIN: 0
UPDPER: 10000
SIMOPT: 0

1 is ready confirm
2 is run confirm, 3-8 are other nice things to see

Then I added IIN blocks for any other value we want to see. One example is
torque feedback:
TYPE: IIN
IOM_ID: VFD100
PNT_NO: 410301
All other parameters default

All the other nice to know things are in addresses 410301 - 410325, so I'm
thinking I have to set up an IIN block for each one I care to watch.

Hopefully someday this helps someone else out there!

Chad Ziesemer
Control Systems Engineer
Cell: 920.427.9147
Desk: 920.886.2376

Galloway Company
601 South Commercial Street
PO Box 609, Neenah, WI 54957-0609




From: Chad Ziesemer
Sent: Thursday, November 05, 2015 5:20 PM
To: 'foxboro@xxxxxxxxxxxxx'
Subject: Anyone using Cutler Hammer SVX drives with Foxboro?

Is anyone else out there using Cutler Hammer (Eaton) SVX series drives at their
facility with Foxboro? I'm setting up a trial to communicate all of the drive
info into and out of Foxboro via an FBM 232. I'd love to hear in general what
your control set-up looks like and what your experience was: smooth sailing or
rough sledding.

Also I'll take this opportunity to see, is there anyone else on this list using
Foxboro reasonably close to Neenah, Wisconsin? We've got a small group of
engineers here that would love to network with someone local and see what we
can learn from each other.

Chad Ziesemer
Control Systems Engineer
Cell: 920.427.9147
Desk: 920.886.2376

Galloway Company
601 South Commercial Street
PO Box 609, Neenah, WI 54957-0609




_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company). Use the info you obtain here at your own
risks. See the disclaimer at www.thecassandraproject.org/disclaimer.html

foxboro mailing list: //www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


----------- Please note that my email address has changed. Please update my
contact information to reflect my address as forwarding for the old address
will end on January 1st 2016. The only change is modifying the domain name of
the email address from @ppetrol.com to @parpacific.com.


_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company). Use the info you obtain here at your own
risks. See the disclaimer at www.thecassandraproject.org/disclaimer.html

foxboro mailing list: //www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


Other related posts: