Re: [foxboro] Alarm Management

  • From: Terry Doucet <doucet427@xxxxxxxxxxx>
  • To: <foxboro@xxxxxxxxxxxxx>
  • Date: Wed, 14 Apr 2010 10:56:45 -0400

Billy,

INHOPT is non-connectable and non-settable so only a configuator or config tool 
can modify this parameter.

INHIB is connectable and settable

INHALM is connectable and settable

You can see a detail display (Foxboro standard display) for the AIN block - 
Alarms where you can see the difference between the INHIB and the INHALM 
parameters but basically INHIB suppresses all alarm message while INHALM is a 
packed boolean where you specify a pattern that can selectively supppress the 
messages from some or all of the various alarms in the block. Only one 
parameter needs to be TRUE to inhibit messages but both must be FALSE to get an 
alarm message.

I believe that there are Invensys and third party applications that will 
suppress alarm messages based on specific input conditions. So if a pump is to 
be taken out of service and you can expect 20 alarms while that pump is gone, 
you can set up the program to suppress these 20 messages perhaps based on 
Operator (Maintenance) input or zero flow switch (for example). The logic 
itself will take a large amount of work to determine and usually must pass 
through a Management of Change committee so that the process safety can be 
assurred. 
Programms that I worked on write (hex) to the INHALM parameter. Maintenance 
staff who had access to the Foxboro detail display used the INHIB parameter 
whenever they needed to suppress alarms while they worked on transmitters, etc. 
Run some internet searchs on Alarm Management to see options.

Terry

 

> Hi List: I'm wondering if there is a tool or script that can be used to
> modify the INHOPT parameter (to 2, Disable Alarm message plus Auto
> acknowledgement ) and the INHIB parameter (to 1) on a given block.
> Thanks!
> Billy
                                          
_________________________________________________________________
Hotmail & Messenger are available on your phone. Try now.
http://go.microsoft.com/?linkid?24461
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: