To all members, I have just read the email from William and as someone who is independant and has nothing to gain from criticising sprinkler or water mist systems I would comment as follows: Firstly we need to establish the difference between a 'life safety sprinkler system' and a 'life safety' sprinkler system. BS5306 has a clear set of guidelines as to what needs to be carried out to ensure that a sprinkler system complies with 'life safetey'. If the system is fed from the towns main then the system should be fed from superior mains with two separate connections to seperate mains. If the system is fed from pumps and tanks then the tank needs to be split into two seperate sections with seperate ball valves and suction lines. The main valve set needs to have a bypass fitted. All floors need to be split into zones and no zone shall have more than 200 sprinkler heads fed from it. All valves need to be monitored and the signals should go to a panel which gives clear indication of the valve status. All sprinkler heads should be quick response. If two ecectric pumps are installed (one duty & one standby) then there should be an auto changeover panel installed so that should mains electricity fail then the pumps will run off stanby generaor. Mains electricity needs to be brought in from an uninterupted supply. All of these reccomendations are there with the intention of reducing risk. It would be wrong to confuse 'life safety' and these sort of precautions when talking about domestic or residential systems as if the above actions were implemented when protecting someones home then they would almost certainly push the cost of the system way beyond the budget of the house holder, builder, local authority etc. With regard to the other questions I would comment as follows: 1) Pressure ratings of systems are normally linked with the nozzle design. As William will no doubt be aware different nozzles work with different pressures. A long throw sidewall head will need a different pressure to a ESFR head. Asking for the pressure requirement is a neither here nor there question, what will be deduced from this? 2) Why ask if pipework complies with DD252 or UL listings? Why do you leave out FM, CEN, BS, NFPA? If pipework delivers water to a fire then is it not doing what its meant to be doing? What if you fitted 65mm fire hoses throughout the premises, these are used by fire fighters every day and are strung across roads, pulled up the sides of buildings, dragged through builders yards to get to skip fires but still deliver water to a fire. Are these not acceptable? What exactly is your point? 3) Apparently there are no residential sprinkler or water mist heads listed in Barbados! What happens if someone wants to protect themselves against fire in the home there? Come on, technology needs to move on, if systems can be installed that reduce fatalities and reduce fire damage then we should all be embracing them. 4) What blockages would you invisage in a water mist system that are different to a sprinkler system. Sprinkler systems are fantastic but I have come across sprinkler systems with lumps of wood holding the clack open, birds nests in alarm gongs, metal discs from mechanical tee installs left in the pipework, I could go on but what is your thinking behind asking this question? 5) Why do you think that leaking through diaphram seals in the states is due to maintenance issues? I can only think that by diaphram seals you mean the seals on the nozzles themselves. How many sprinkler systems have the heads removed on every service visit and the seal inspected? If the heads were removed then they would in accordance with BS5306 need to be replaced with new heads. Are you suggesting that every sprinkler and water mist nozzle in the world should be replaced every service visit? Or do you think they may need replacing more frequently due to this 'diaphram seal' problem? I would welcome your advice on this. 6)Sprinkler systems do not have a blanket 'approval' complying with water authority regulations, the design has to take in to account these regulations. Systems cannot be boosted directly from the town main, a double check valve needs to be installed and if a tank is used on the system then it should have a type 'A' air gap. These water authority regulations can be designed into a sprinkler or water mist system quite easily. What are your reccomendations on this subject? 7) If the water authority regulations mentioned above are complied with then there should not be a problem as these are written up specifically to prevent cross contamination. The same obviously goes for sprinkler and water mist systems. I do know that US, fire departments have been using these type of wetting agents for a number of years with amazing results. Do some research and check it out. 8) With regard to full capacity operating for ten minutes then this would need to be answered by a water mist company. A thought however: Should the water board shut the main for repairs then could a sprinkler system operate for the full time? Fire needs to be dealt with as quickly as possible as the longer it burns the quicker it will spread. The first few seconds/minutes of the fire are the most critical, controlling it at this stage are paramount. I could not make sense of the paragraph about retro-fit systems. To finish I would say to you all sprinkler systems have a huge role to play in this world, so do water mist systems. Do not be inclined to fight each other because you think that one system is a threat to the other in terms of market share. There is plenty of work out there, lets all pull together and make this a safer place. PS: Who is Simon Quillish? Best regards Billy B. >From: "William" <william@xxxxxxxxxxxxxxxxxxx> >Reply-To: dd251@xxxxxxxxxxxxx >To: <dd251@xxxxxxxxxxxxx> >Subject: [dd251] Water Mist Systems >Date: Tue, 21 Jan 2003 17:36:57 -0000 > >To all members > >I have read the recent e-mail on water mist sytems and have a few questions >that many people have asked.I am also astounded that the word guarantee for >any sprinkler system is used. The principals of a life safety system is >based on risk as there will never be a guarantee of electric or water. > >QUESTIONS > >1) What pressure rating does the system work at > >2) Does all the pipework comply with DD252 or UL listing and also comply >with the manufactures requirements. > >3) Are mist sprinkler heads listed for residential use any where in the >world. > >4) Are there blockages within the system over a period of time /or is it >dry > >5) Systems like these used in the states have failed through leakage of >diaphram seals this is probably because of maintenance issues > >6) Cross contamination with water ( has the system got the relevant >approvals from the relevant authorites) This is a legal requirement > >7) Are the fire retardent agents used within the system ok for the water >authorites and manufacturers of products used > >8) Can the system operate at full capacity for 10 minutes as in the NFPA >13D or DD251 standard. > >To my knowledge water mist systems are currently being fitted to domestic >properties where a standard is not applicable (retro-fit) as these are >deemed to be above and beyond whats required for regulations? > >In my opinion no system not stated or complying with the relevant standards >can be considered for any form of relaxations either building or fire. > >I trust I will receive comments back on this issue > >William Butler > >===================================================================== >Residential Sprinkler Forum >Archives: //www.freelists.org/archives/dd251 >WebSite: www.dd251.org.uk >To unsubscribe from the list, send an email to >dd251-request@xxxxxxxxxxxx with ?unsubscribe? in the Subject line or >unsubscribe from the website www.dd251.org.uk > _________________________________________________________________ Use MSN Messenger to send music and pics to your friends http://messenger.msn.co.uk ===================================================================== Residential Sprinkler Forum Archives: //www.freelists.org/archives/dd251 WebSite: www.dd251.org.uk To unsubscribe from the list, send an email to dd251-request@xxxxxxxxxxxx with ?unsubscribe? in the Subject line or unsubscribe from the website www.dd251.org.uk