Joel, a driver pumping into an infinitely long, or ideally terminated 
transmission line never sees a far end because no energy ever reflects 
back.  A PDN that is arranged to look like an ideal infinite 
transmission structure, similarly reflects nothing back to the load.  
All the load sees is the characteristic resistive Z of the transmission 
structure it is attached to.

Best Regards,


Steve.
Joel Brown wrote:
> I hate to prolong this but...
> When I think about a transmission line in the normal sense (signal
> propagation), A driver switches at one end but initially all it sees is Zo
> which looks like a resistor maybe 50 ohms and it does not even see the load
> until wave propagates the length of the line. So there is a time delay. Now
> think of the driver being the power pin of the IC and the load being the
> bypass cap on the corner of the board or visa versa and I see a propagation
> delay, so what am I missing?
>
> Joel
>  
>
> -----Original Message-----
> From: SILR [mailto:silr@xxxxxxxxxxxx] 
> Sent: Thursday, March 13, 2008 6:27 PM
> To: 'steve weir'; 'Joel Brown'
> Cc: 'Istvan Novak'; si-list@xxxxxxxxxxxxx
> Subject: RE: [SI-LIST] Re: Antwort: Re: Questions about interplane
> capacitance
>
> Joel asked:
> <<< ...why is charge propagation velocity not a factor when the PDN is
> purely resistive? >>>
>
>
> Well, here's a crazy way to think about this (which I'm sure not everyone
> will agree)... I guess this would be like how Eric B. might put it... "Be
> the Signal"
>
>
> I'm the charge on some corner of a board...there's an IC in the middle of
> the board...
>
> I have to get to that IC using this transmission line called the PDN.   If
> this Transmission Line had the classical Ls and Cs (and Rs) to describe its
> characteristics, then that means I have to deal with changing EM fields to
> get to that IC...  but these time varying EM fields always cause some delay
> in my charge getting to that IC in a timely manner...   
>
> BUT!!! ...if this Transmission Line had nothing but Rs (no Ls and Cs) to
> describe its characteristics then that means I don't have to deal with time
> varying EM fields any longer...   I just have to deal with resistive losses
> only but this only equates to a drop in Static Voltage Potential and nothing
> more... (so keep the Z low!!!)  And I can get there (to the IC) in no time
> and the IC gets the charges that it needs and it wouldn't even know anything
> is different...
>
> Again, this is a crazy way to look at this... but it works for me, for
> now... until I get grilled by the senior members...   :-)
>
> Silvester
>
> -----Original Message-----
> From: si-list-bounce@xxxxxxxxxxxxx [mailto:si-list-bounce@xxxxxxxxxxxxx] On
> Behalf Of steve weir
> Sent: Thursday, March 13, 2008 5:57 PM
> To: Joel Brown
> Cc: 'Istvan Novak'; si-list@xxxxxxxxxxxxx
> Subject: [SI-LIST] Re: Antwort: Re: Questions about interplane capacitance
>
> Joel,  it is transmission line theory.  Think about an infinitely long
> signal transmission line for a moment.  At any instant a driver sees a
> constant impedance across frequency.  The voltage to current relation is
> independent of prior history.  What Istvan describes is a very low impedance
> transmission structure for power.
>
> Sadly, a lot of IC vendors are still playing catch-up in terms of  power
> delivery.  If they had their game together, they would be telling you:  
> The actual voltage tolerances at the die, the current spectrum at the die,
> and the parasitics of the die and package.  From that you could engineer
> your PDN.  Instead often what we see are partial recipes like you describe.
> On a good day the recipes cost extra money.  On a bad day, they result in
> failures.
>
> One can build a resistive networks several ways.  One is to add discrete
> resistance by any number of methods, another is to use the FDTIM method that
> Larry Smith has long championed.  And even though resistive networks have
> attractive qualities, reactive networks may still be cheaper and equally
> effective.  It all depends on the circumstances.  It is somewhat akin to
> surface finishes:  there is no ideal one.  But there are several that when
> used properly work very well.  One just needs to respect the limitations of
> each method.
>
> Part of the problem figuring this stuff out is having sufficient experience
> to judge trade-offs early in the design process.  That's just something that
> has to be learned.  As more training materials come out on power delivery,
> it will probably get easier.  In the shameless plug department, we (
> Teraspeed ) do very nice jobs optimizing power delivery systems for
> customers.  If you've got a design you want advice on we can get you
> squared-up pretty quickly.
>
> Best Regards,
>
>
> Steve.
> Joel Brown wrote:
>   
>> Steve,
>>
>> So even though each cap has a relatively high ESR (1.6 Ohms) the PDN 
>> as a whole has a relatively low impedance which will result in low 
>> noise on the PDN. This goes against intuition and previous thinking 
>> that an IC needs a local bypass with low ESR and ESL to supply the 
>> needed charge during switching transients. I am starting to see that 
>> mathematically a resistive PDN lowers noise compared to one that is 
>> the inductive (you did a good job explaining that). The thing that I 
>> am having trouble grasping or
>>     
> visualizing
>   
>> is that why is charge propagation velocity not a factor when the PDN 
>> is purely resistive? Is the PDN model simply a resistor in series with 
>> the
>>     
> load
>   
>> and distance has no effect? Perhaps there is an analogy that would 
>> make
>>     
> this
>   
>> concept easier to understand? Also, when I see app notes from IC 
>> vendors that recommend using a 0.1uF and 1000pF cap on each supply pin 
>> and then instead I use distributed high ESR capacitors I feel like I 
>> am doing something quite different and contrary from the recommended 
>> and when I
>>     
> query
>   
>> the vendors on how they arrived at recommendations in the app note the 
>> answer I get is "we recommend that you do it exactly as shown in the 
>> app note, we know it works that way and if you don't follow it it may 
>> not
>>     
> work".
>   
>> Also I am wondering how all this relates to X2Y caps, I suppose they 
>> could be used with series resistors but that would somewhat defeat the 
>> purpose
>>     
> by
>   
>> adding inductance. Its not clear to me what approaches I should 
>> attempt on future designs.
>>
>> Joel
>>   
>>
>> -----Original Message-----
>> From: si-list-bounce@xxxxxxxxxxxxx 
>> [mailto:si-list-bounce@xxxxxxxxxxxxx]
>>     
> On
>   
>> Behalf Of steve weir
>> Sent: Wednesday, March 12, 2008 11:26 PM
>> To: Doug Brooks
>> Cc: Istvan Novak; si-list@xxxxxxxxxxxxx
>> Subject: [SI-LIST] Re: Antwort: Re: Questions about interplane 
>> capacitance
>>
>> Doug, Istvan's representations are analytically exact.  When the 
>> characteristic impedance of the transmission structure is high, and/or 
>> the rise times are slow then capacitors can be placed in close enough
>>     
> proximity
>   
>> that they load the transmission structure so as to make it appear a 
>> lower impedance with some little bumps.  For example if one had a 10" 
>> x 10" 4
>>     
> mil
>   
>> er4.0 board = 22.5nF and loaded it with bypass every square inch of 
>> 150pH, then for slow enough signals, the distributed impedance would 
>> look like 80mOhms.  If the network were constructed from 200 
>> capacitors, an ESR
>>     
> value
>   
>> of 1.6Ohms / cap would make that impedance uniform down to the RC knee 
>> of the parts.  Assume that were matched by an AVP regulator of 80mOhms 
>> and
>>     
> the
>   
>> entire thing looks like 80mOhms from DC to over 1GHz.  80mOhms would
>>     
> support
>   
>> a 32 bit transition w/ about 5% droop.  The impedance scales with
>>     
> dielectric
>   
>> height and the inverse square root of eR.  Scale the dielectric down 
>> to 0.1mils and now 320 lines can switch simultaneously in one 
>> direction with
>>     
> 5%
>   
>> droop, and at arbitrary edge rates. 
>>
>> Istvan has shown using analysis with the reverse pulse technique an 
>> inductive PDN shunt impedance acts like a noise high pass filter  ( 
>> See DC papers from at least as far back as DC East 2005 ).  Put in a 
>> square wave noise pulse ( load current ) and the leading edge changes 
>> by Vdelta = -L*di/dt below the baseline.  Allow the pulse to persist 
>> long enough and
>>     
> the
>   
>> system recovers back to the baseline which would be -I*Rpdn.  
>> Return the load current to zero, and now the energy stored in the
>>     
> inductance
>   
>> kicks back -L*di/dt.  The p-p noise is then 2*Ldi/dt - (Imax-Imin)*Rpdn.
>>     
> If
>   
>> Rpdn is very small then it approximates 2*Ldi/dt.  
>> This behavior is apparent in the transient response plots of virtually 
>> any non-AVP VRM.
>>
>> Now, suppose that the VRM and PDN can be made to appear resistive 
>> right through Fknee.  Then the response to a current pulse of I is 
>> simply Vdelta
>>     
> =
>   
>> -I*Rpdn.  There is no component of di/dt, and so the total p-p noise 
>> is
>>     
> just
>   
>> (Imax - Imin)*Rpdn.  AVP schemes position the DC operating point 
>> intentionally high so that at Imin they are at their margined high 
>> limits and at Imax they are at their low limits.  This allows 
>> increasing Rpdn
>>     
> while
>   
>> still meeting the same current and voltage specifications.
>>
>> Best Regards,
>>
>>
>> Steve.
>>
>>
>> Doug Brooks wrote:
>>   
>>     
>>> Istvan,
>>>
>>> With all due respect, I would modify your argument a little bit. In 
>>> very simplistic terms, suppose we need x amount of charge to 
>>> transition from a zero to a one in one ns. That amount of charge (I
>>> suggest) must be within
>>> 6 inches of the need (what I think we are referring to as the service 
>>> radius). If not, it takes a little longer to reach the logical one state.
>>> I look at it, not from the standpoint of a dip in the rail, as much 
>>> as the ability to satisfy the rise time requirement (unless you are 
>>> referring to a dip in the rail that occurs during the rise time
>>> itself.) In the slightly longer term, the charge will replenish 
>>> fairly quickly, but not, perhaps fast enough to meet the rise time
>>>       
> requirement.
>   
>>> Doug Brooks
>>>
>>>
>>>
>>>   
>>>     
>>>       
>>>> Andreas,
>>>>
>>>> Yes and no.  It is true that charge moves with finite speed, so for 
>>>> any given time duration the charge has to come from locations closer 
>>>> than the ratio of distance over speed.  BUT the whole notion of 
>>>> service radius is based on the assumption that as you deplete the 
>>>> charge available in the immediate vicinity of the active device, you 
>>>> have to wait for replenishment, otherwise you get a big dip on the 
>>>> supply rail.
>>>>
>>>> Having a matched
>>>> transmission medium to deliver power to the active device, the 
>>>> charge moves without interruption, and as you deplete the planes 
>>>> close to the device, it gets replenished on the fly from areas 
>>>> further away, so the service area concept is pretty much meaningless 
>>>> in this scenario.  Current flows without interruption.
>>>> The bucket brigade of infinitesimally small inductive and capacitive 
>>>> elements of the transmission line transmits the power continuously.
>>>> If the load current changes, for any I(t) time function of load 
>>>> current, the transient noise at the load point will be I(t)*Zo, 
>>>> where we assume that Zo is the resistive and frequency independent 
>>>> characteristic impedance of the transmission medium.  This is a very 
>>>> simplistic one-dimensional model, but it gives a good insight of why 
>>>> the service radius matters only on PDNs where the network is not 
>>>> matched.
>>>>
>>>> Regards,
>>>>
>>>> Istvan Novak
>>>> SUN Microsystems
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> Andreas.Lenkisch@xxxxxxxxxx wrote:
>>>>     
>>>>       
>>>>         
>>>>> Istvan,
>>>>> I'm wodering a little about your comments to the service radius.
>>>>> Independant if the impedance is resistive, we have still a 
>>>>> propagation time which would limit the service radius from my
>>>>>         
>>>>>           
>> understanding.
>>   
>>     
>>>>> Do I'm wrong?
>>>>>
>>>>> regards
>>>>> Andreas
>>>>>
>>>>>
>>>>>
>>>>> Istvan Novak <istvan.novak@xxxxxxxxxxx> Gesendet von: 
>>>>> si-list-bounce@xxxxxxxxxxxxx
>>>>> 11.03.2008 13:14
>>>>>
>>>>> An
>>>>> Joel Brown <joel@xxxxxxxxxx>
>>>>> Kopie
>>>>> si-list@xxxxxxxxxxxxx
>>>>> Thema
>>>>> [SI-LIST] Re: Questions about interplane capacitance
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> Joel,
>>>>>
>>>>> Just one quick comments to the good summary from Steve:
>>>>>
>>>>> While considering planes and bypass capacitors in terms of 
>>>>> effective capacitances and inductances is a valid approach, we need 
>>>>> to keep in mind that focusing on the capacitive or inductive nature 
>>>>> of parts without looking at the wider picture misses a very 
>>>>> important and useful class of solutions, namely that of matched 
>>>>> transmission lines.  As it was pointed out earlier several times on 
>>>>> the SI list, the best
>>>>> (self) impedance for a power distribution network is a resistive 
>>>>> one, neither capacitive, nor inductive.
>>>>> We can get resistive impedance from a matched transmission line, 
>>>>> regardless of its capacitance and inductance, and in such cases the 
>>>>> notion of 'service area' of parts become meaningless: you can put 
>>>>> bypass components further away from the active devices without 
>>>>> sacrificing performance.
>>>>>
>>>>> Regards,
>>>>>
>>>>> Istvan Novak
>>>>> SUN Microsystems
>>>>>
>>>>> Joel Brown wrote:
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> Interplane capacitance is frequently cited as the only effective 
>>>>>> bypass capacitance on a PCB at frequencies above 200 MHz.
>>>>>> I am currently working on a design which brings up some questions
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> regarding
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> interplane capacitance.
>>>>>>
>>>>>> 1. Power planes normally carry "standard" voltage rails that are 
>>>>>> used throughout a board such as +5V and +3.3V.
>>>>>> High speed ICs usually have core voltages that are local to the IC 
>>>>>> and
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> are
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> provided by a local regulator which converts the standard rail to 
>>>>>> the
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> core
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> voltage (example 3.3 to 1.8V).
>>>>>> The local core voltage is distributed on a plane area that is 
>>>>>> local to
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> the
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> IC and therefore is small in area (0.25 sq in or less) which 
>>>>>> results in
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> a
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> very small amount of interplane capacitance.
>>>>>> Is this very small amount of capicitance effective for bypassing 
>>>>>> the IC?
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> I
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> am sure it depends somewhat on the current waveform being drawn by 
>>>>>> the
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> IC
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> but this can only be estimated because semiconductor manufacturers 
>>>>>> do
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> not
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> provide current consumption profile as a function of frequency. To 
>>>>>> make matters worse, some ICs have several different VCC pins which 
>>>>>> the manufacturer recommends connecting to separate networks of 
>>>>>> bypass caps
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> and
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> ferrite beads. This cuts the power distributuion up even more 
>>>>>> resulting
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> in
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> less (practically zero) interplane capacitance. It is somewhat 
>>>>>> ironic
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> that
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> the the voltages such as +5V and +3.3V which are required at 
>>>>>> points
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> across
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> the whole board and therefore have the most interplane capacitance 
>>>>>> are
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> also
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> the voltages which have least requirement for interplane 
>>>>>> capacitance
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> because
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> they do not directly supply high speed rails.
>>>>>>
>>>>>> 2. There has been a lot of emphasis on reducing the mounted 
>>>>>> inductance
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> of
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> bypass capacitors. Even with this reduced inductance they are 
>>>>>> still only effective up to several hundereds of MHz at which point 
>>>>>> the interplane capacitance becomes the only bypass capacitance 
>>>>>> mechanism. However there
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> is
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> inductance between the connection of the IC to the planes. This
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> inductance
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> consists of vias and package inductance. I did look for some 
>>>>>> numbers for package inductance and did not find much, it seems to 
>>>>>> be a closely held secret. Also it is unknown how much bypass 
>>>>>> capacitnace is internal to
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> the IC
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> package. Just for example if we assume 250pH for the vias and 500 
>>>>>> pH for
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> the
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> package, then the impedance at 500 MHz would be 2.36 Ohms. This 
>>>>>> seems
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> rather
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> high for the interplane capacitance to be of much benefit.
>>>>>>
>>>>>> In summary how much interplane capacitance is needed to be 
>>>>>> beneficial,
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>>> and
>>>>>
>>>>>       
>>>>>         
>>>>>           
>>>>>> why is it beneficial given the inductance in the vias and package?
>>>>>>
>>>>>> Thanks - Joel
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>         
>>>>>>           
>>>>>>             
>>>> ------------------------------------------------------------------
>>>> To unsubscribe from si-list:
>>>> si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject 
>>>> field
>>>>
>>>> or to administer your membership from a web page, go to:
>>>> //www.freelists.org/webpage/si-list
>>>>
>>>> For help:
>>>> si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
>>>>
>>>>
>>>> List technical documents are available at:
>>>>                 http://www.si-list.net
>>>>
>>>> List archives are viewable at:
>>>>            //www.freelists.org/archives/si-list
>>>> or at our remote archives:
>>>>            http://groups.yahoo.com/group/si-list/messages
>>>> Old (prior to June 6, 2001) list archives are viewable at:
>>>>            http://www.qsl.net/wb6tpu
>>>>
>>>>
>>>>
>>>>     
>>>>       
>>>>         
>>> ------------------------------------------------------------------
>>> To unsubscribe from si-list:
>>> si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
>>>
>>> or to administer your membership from a web page, go to:
>>> //www.freelists.org/webpage/si-list
>>>
>>> For help:
>>> si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
>>>
>>>
>>> List technical documents are available at:
>>>                 http://www.si-list.net
>>>
>>> List archives are viewable at:     
>>>             //www.freelists.org/archives/si-list
>>> or at our remote archives:
>>>             http://groups.yahoo.com/group/si-list/messages
>>> Old (prior to June 6, 2001) list archives are viewable at:
>>>             http://www.qsl.net/wb6tpu
>>>   
>>>
>>>
>>>   
>>>     
>>>       
>> --
>> Steve Weir
>> Teraspeed Consulting Group LLC
>> 121 North River Drive
>> Narragansett, RI 02882
>>
>> California office
>> (408) 884-3985 Business
>> (707) 780-1951 Fax
>>
>> Main office
>> (401) 284-1827 Business
>> (401) 284-1840 Fax
>>
>> Oregon office
>> (503) 430-1065 Business
>> (503) 430-1285 Fax
>>
>> http://www.teraspeed.com
>> This e-mail contains proprietary and confidential intellectual 
>> property of Teraspeed Consulting Group LLC
>>
>>     
> ----------------------------------------------------------------------------
>   
>> --------------------------
>> Teraspeed(R) is the registered service mark of Teraspeed Consulting 
>> Group LLC
>>
>> ------------------------------------------------------------------
>> To unsubscribe from si-list:
>> si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
>>
>> or to administer your membership from a web page, go to:
>> //www.freelists.org/webpage/si-list
>>
>> For help:
>> si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
>>
>>
>> List technical documents are available at:
>>                 http://www.si-list.net
>>
>> List archives are viewable at:     
>>              //www.freelists.org/archives/si-list
>> or at our remote archives:
>>              http://groups.yahoo.com/group/si-list/messages
>> Old (prior to June 6, 2001) list archives are viewable at:
>>              http://www.qsl.net/wb6tpu
>>   
>>
>>
>>
>>
>>   
>>     
>
>
> --
> Steve Weir
> Teraspeed Consulting Group LLC
> 121 North River Drive
> Narragansett, RI 02882 
>
> California office
> (408) 884-3985 Business
> (707) 780-1951 Fax
>
> Main office
> (401) 284-1827 Business
> (401) 284-1840 Fax 
>
> Oregon office
> (503) 430-1065 Business
> (503) 430-1285 Fax
>
> http://www.teraspeed.com
> This e-mail contains proprietary and confidential intellectual property of
> Teraspeed Consulting Group LLC
> ----------------------------------------------------------------------------
> --------------------------
> Teraspeed(R) is the registered service mark of Teraspeed Consulting Group
> LLC
>
> ------------------------------------------------------------------
> To unsubscribe from si-list:
> si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
>
> or to administer your membership from a web page, go to:
> //www.freelists.org/webpage/si-list
>
> For help:
> si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
>
>
> List technical documents are available at:
>                 http://www.si-list.net
>
> List archives are viewable at:     
>               //www.freelists.org/archives/si-list
> or at our remote archives:
>               http://groups.yahoo.com/group/si-list/messages
> Old (prior to June 6, 2001) list archives are viewable at:
>               http://www.qsl.net/wb6tpu
>   
>
>
>
>
>   


-- 
Steve Weir
Teraspeed Consulting Group LLC 
121 North River Drive 
Narragansett, RI 02882 

California office
(408) 884-3985 Business
(707) 780-1951 Fax

Main office
(401) 284-1827 Business 
(401) 284-1840 Fax 

Oregon office
(503) 430-1065 Business
(503) 430-1285 Fax

http://www.teraspeed.com
This e-mail contains proprietary and confidential intellectual property of 
Teraspeed Consulting Group LLC
------------------------------------------------------------------------------------------------------
Teraspeed(R) is the registered service mark of Teraspeed Consulting Group LLC

------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List technical documents are available at:
                http://www.si-list.net

List archives are viewable at:     
                //www.freelists.org/archives/si-list
or at our remote archives:
                http://groups.yahoo.com/group/si-list/messages
Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu
  

Other related posts: