[lit-ideas] Re: The Compressor Shorted To Ground

  • From: Jlsperanza@xxxxxxx
  • To: lit-ideas@xxxxxxxxxxxxx
  • Date: Tue, 20 Nov 2007 22:18:58 EST

GEARY'S COLUMN
 
Q: Why does a compressor short to ground?
G: Because you _let_ it short to ground, that's because.
 
 
          "The compressor  shorted to ground -- and I know why"
               J. M. Geary 
 
 
_Subject: 50 HP Copeland Discus died - experiences?_ 
(http://www.elitesoft.com/sci.hvac/itmotfal.html)      Be sure to check the 
wiring between the  
contactors to the compressor for a short to ground -  don't laugh, I found one 
like 
this after "professionals"  ...
www.elitesoft.com/sci.hvac/itmotfal.html  

_Property Management Software for apartment managers, owners, and  ..._ 
(http://www.softwareforlandlords.com/hvac6.php)       
When a compressor fails short, what  happens is that insulation on the wires 
... resulting in insulation  damage that shorts the rotor either to ground or 
to  ...
_www.softwareforlandlords.com/hvac6.php_ 
(http://www.softwareforlandlords.com/hvac6.php)   

-----

 
"I lost a compressor last week :~(" 

"It was a  pump-down unit."

"The other compressor works fine, BTW. Unit ohms and  megs good. No history ( 
7 year old unit ) of failure. Oil good, freon  good."

"Clean. All the way. Pulled off everything that pulls - 4 heads,  end bell, 
oil pump (and took pump apart)".
 
"You didn't say. Does the compressor attempt to spin? My only thought is  
that you have a winding short."
 
"Are any of the windings discolored?"

"No -- why?"

"Well, you have to check the wiring between the contactors to the  compressor 
for a short to ground - don't laugh, I found one like this after  
"professionals" condemned a 2 thousand dollar semi-hermetic compressor (which  
had not 
one ____ thing wrong with it)"

"You don't say!"
 
"Yep. Usually a short like this makes itself fairly obvious (smoke and so  
forth), but if the lead(s) is(are) able to weld themselves and create a  
connection that will trip the breaker every time with no further deterioriation 
 of 
the leads, you will be hard pressed to see it."
 
"It's no laughing matter. I did check the wiring, to the extent of  stripping 
off the BX to examine every inch of every wire. I've seen the wrong  
diagnoses things you speak of. I was called on one unit to second-guess a  
contractor 
who wanted to change a chattering contactor. The owner didn't want to  pay for 
a new 100 amp contactor. Turns out it was a 240V coil, in series with a  
safety in the compressor. When I popped the compressor open ( 15 HP Carlyle ),  
it 
was major toast city - I couldn't have made it any blacker in there with  
spray paint ! One side of the contactor control circuit was grounded inside the 
 
compressor, the other side was hot w/ 120V, thus the chatter. I got to tell 
the  owner 'good news, bad news'... contactor's OK, compressor's gone !  :~):

"Sometimes they can wear such that they touch and ground out, then  the force 
of that spark pushes them away such that they ohm good, then the  vibration 
of start-up and running eventually brings the bare spot back into  ground 
contact ( another trip ), etc."
 
"I also ran across one case where a contactor was shorted to the backplate  
of the relay panel it was installed on - the short was in the back bakelite of  
the contactor (to the backplate) and was absolutely impossible to see."
 
"But you _did_ see"
 
"Well, yes. BTW, I caught both these problems with a Simpson 260 (no megger  
required) and have learned to make sure that wiring downstream of the 
contactor  and upstream of the compressor is not shorted phase to phase or 
phase to 
ground.  Hope this helps you."
 
"Sure. The new compressor is in now and spins like a top."
 
"Yes. I'm glad you learned. Once you know the why, there shouldn't be a  
because! The symptoms would first indicate bearing failure, but you looked at  
that and found nothing, right?
 
"Right"
 
"So, the only other thing it could be is a shorted stator winding. Not a  
short to ground, which is easy to detect, but just a few shorted turns."
 
"Exactly -- but how would my _wife_ know?"
 
"Well, explain to her. The compressor, if shorted, will not absorb  enough 
energy from the stator flux, and act as a heavy drag on the motor,  causing 
increased current draw". 
 
"Right, and the winding resistance may not be altered enough to read the  
difference. The failed turns are nearly always at the inside of the winding, so 
 
the burned insulation is rarely visible. This is because the innermost layer 
of  turns in a winding are farthest from the cooling effect (in this case of  
refrigerant) of the motor's coolant, and also have been bent to the sharpest  
radius, and also are subjected to the most intense alternating magnetic fields  
(from all the windings above it), and so have the most eddy current heating. 
The  innermost windings often run 10-30 C hotter than the outermost. The heat 
leads  to insulation breakdown earlier in the innermost winding."

"Well, that would explain the price". 

"Right. An inductance bridge will show the problem, but you probably  don't 
have one of those. The inductance of the bad winding won't differ much  either, 
but the shorted turns will cause the 'Q' (quality factor) of the bad  winding 
be approximately ZERO! That will be the indication of shorted turns. An  
impedance bridge is similar to a wheatstone bridge, however it is used at AC  
instead of DC, to measure the complex impedance of capacitors and inductors. 
Not  
only does it measure capacitance or inductance, but it measures the quality of 
 the component, as well. A stator winding (either in or out of the motor) 
will  show small resistance and large inductance. It should have high 'Q' when 
out of  the motor."

"Now, when you say, 'absorb energy from stator flux'?--  Is this something 
like creating an opposing field?"
 
"Well, no. Exactly the opposite."
 
"How come?"

"Well, the iron in the stator (and the magnetic field in the rotor once it  
is spinning) oppose the field of the stator, thereby preventing it from drawing 
 current from the line. The shorted turns remove the magnetic field, thereby  
causing the rest of the winding to draw MORE current from the line."
 
"Very interesting! Are internal sensors usually placed there?"

"Yes,  when the compressor is tested for insulation class, a thermocouple is  
placed near the innermost turns of the winding, or some other location that 
the  motor designer determines will be the hottest winding location in the 
entire  motor. The temperature rise is then determined at full load. This 
procedure is  described in some detail in some versions of the NFPA's National 
Electrical Code  book."
 
"Will do".

"What is 'quality factor' ? It's a new term to  me."

"Well, Quality Factor, or Q, is an electrical engineering term  relating to 
the loss in an inductor. Higher Q means less loss."
 
"How much then?"
 
"How much did I say?"

"Before you go, is there a way to use a  capacitance meter to gain 
information ? Or to home=brew an inductance bridge (  assuming one owns a good 
digital 
multi-meter with capacitance function ( Fluke  12 )?" 

"Well, not really. The problem with the rotor inside the stator is that the  
copper conductors in the rotor are SUPPOSED to be shorted. And, the stator  
windings definitely see the short. The stator draws large current from the 
line, 
 transfers large flux across the gap between stator and rotor, and causes 
current  to flow in the rotor winding, causing opposing magnetic flux. This is 
what  starts the motor spinning. But with the stator not conducting current, 
and 
the  rotor not spinning, it looks like a short, and will make it much harder 
to see  the difference between a good and bad stator. It doesn't matter 
whether the  stator is in or out of the motor housing, but it will matter 
whether 
the rotor  is inside the stator."

"Thanks again, for more really great information! It's really appreciated.  I 
always like to know the whys of things."
 
 
 --------------------
 
SUMMARY

"Air conditioner compressors usually fail due to one of two conditions:  time 
and hours of operation (wearout), or abuse. There are some failures that  can 
occur elsewhere in the system that will cause a compressor failure, but  
these are less common unless the system has been substantially abused."
 
"Usually abuse is a result of extended running with improper freon charge, or 
 as a consequence of improper service along the way. This improper service 
can  include overcharging, undercharging, installing the wrong starter 
capacitor 
as a  replacement, removing (rather than repairing/replacing) the thermal 
limiter,  insufficient oil, mixing incompatible oil types, or wrong oil, 
installing the  compressor on a system that had a major burnout without taking 
proper 
steps to  remove the acid from the system, installing the wrong compressor 
(too small) for  the system, or installing a new compressor on a system that 
had 
some other  failure that was never diagnosed." 
"The compressor can fail in only a handful of different ways. It can fail  
open, fail shorted, experience a bearing failure, or a piston failure (throw a  
rod), or experience a valve failure. That is pretty much the entire list." 
"When a compressor fails open, a wire inside the compressor breaks. This is  
unserviceable and the symptom is that the compressor does not run, though it 
may  hum. If the compressor fails open, and following the steps here does not 
fix it,  then the system may be a good candidate for a new compressor. This 
failure  causes no further failures and won't damage the rest of the system; if 
the rest  of the system is not decrepit then it would be cost effective to just 
put a new  compressor in." 
"Testing for a failed open compressor is easy. Pop the electrical cover for  
the compressor off, and remove the wires and the thermal limiter. Using an  
ohmmeter, measure the impedance from one terminal to another across all three  
terminals of the compressor. Also measure the impedance to the case of the  
compressor for all three terminals." 
"You should read low impedance values for all terminal to terminal  
connections (a few hundred ohms or less) and you should have a high impedance  
(several 
kiloohms or greater) for all terminals to the case (which is ground).  If any 
of the terminal to terminal connections is a very high impedance, you  have a 
failed open compressor. In very rare cases, a failed open compressor may  
show a low impedance to ground from one terminal (which will be one of the  
terminals associated with the failed open). In this case, the broken wire has  
moved and is contacting the case. This condition - which is quite rare but not  
impossible - could cause a breaker to trip and could result in a misdiagnosis 
of 
 failed short. Be careful here; do an acid test of the contents of the lines  
before deciding how to proceed with repair." 
"When a compressor fails short, what happens is that insulation on the wires  
has worn off or burned off or broken inside the compressor. This allows a 
wire  on a motor winding to touch something it shouldn't touch - most commonly 
itself  a turn or two further along on the motor winding. This results in a 
"shorted  winding" which will stop the compressor immediately and cause it to 
heat 
up and  burn internally." 
"Bad bearings can cause a failed short. Either the rotor wobbles enough to  
contact the stator, resulting in insulation damage that shorts the rotor either 
 to ground or to the stator, or end bearing wear can allow the stator to 
shift  down over time until it begins to rub against the stator ends or the  
housing." 
"Usually when one of these shorts occur, it isn't immediately a hard short -  
meaning that initially the contact is intermittent and comes and goes. Every  
time the short occurs, the compressor torque drops sharply, the compressor 
may  shudder a bit visibly as a result, and this shudder shakes the winding 
enough to  separate the short. While the short is in place, the current through 
the shorted  winding shoots up and a lot of heat is produced. Also, usually the 
short will  blow some sparks - which produces acid inside the air conditioner 
system by  decomposing the freon into a mixture of hydrochloric and 
hydrofluoric acid." 
"Over time (possibly a couple of weeks, usually less) the shuddering and the  
sparking and the heat and the acid cause insulation to fail rapidly on the  
winding. Ultimately, the winding loses enough insulation that the inside of the 
 compressor is literally burning. This will only go on for a few minutes but 
in  that time the compressor destroys itself and fills the system with acid. 
Then  the compressor stops. It may at that time melt a wire loose and short to 
the  housing (which can trip your house main breaker) or it may not. If the 
initial  cause of the failure was bad bearings causing the rotor to rub, then 
usually  when the thing finally dies it will be shorted to the housing." 
"If it shorts to the housing, it'll blow fuses and/or breakers and your  
ohmmeter will show a very low impedance from one or more windings to ground. If 
 
it doesn't short to the housing, then it will just stop. You still establish 
the  type of failure using an ohmmeter." 
"You cannot directly diagnose a failed short with an ohmmeter unless it  
shorts to the housing - a shorted winding won't show up with an ohmmeter though 
 
it would with an inductance meter (but who has one of those?) Instead, you have 
 to infer the failed short. You do this by establishing the the ohmmeter 
gives  normal readings, the starter capacitor is good, power is arriving at the 
 
compressor, AND an acid test of the freon shows acid present." 
"With a failed short, just give up. Change everything, including the lines if 
 possible. It is not worth fixing; it is full of acid and therefore is all 
junk.  Further, a failed short could have been initially induced by some other 
failure  in the system that caused a compressor overload; by replacing the 
whole system  you also will get rid of that potential other problem." 
"Less commonly, a compressor will have a bearing failure, piston failure or a 
 valve failure. These mechanical failures usually just signal wearout but 
could  signal abuse (low lubricant levels, thermal limiter removed so 
compressor  
overheats, chronic low freon condition due to unrepaired leaks). More rarely, 
 they can signal another failure in the system such as a reversing valve 
problem  or an expansion valve problem that winds up letting liquid freon get 
into 
the  suction side of the compressor." 
"If a bearing fails, usually you'll know because the compressor will sound  
like a motor with a bad bearing, or it will lock up and refuse to run. In the  
worst case, the rotor will wobble, the windings will rub on the stator, and  
you'll wind up with a failed short." 
"If the compressor locks up mechanically and fails to run, you'll know  
because it'll buzz very loudly for a few seconds and may shudder (just like any 
 
stalled motor) until the thermal limiter cuts it off. When you do your  
electrical checks, you will find no evidence of failed open or failed short. 
The  acid 
test will show no acid. In this case, you might try a hard-start kit but if  
the compressor has failed mechanically the hard-start kit won't get the  
compressor to start. In this case, replacing the compressor is a good plan so  
long 
as the rest of the system is not decrepit. After replacing the compressor,  
you must carefully analyze the performance of the entire system to determine  
whether the compressor problem was induced by something else." 
"Rarely, the compressor will experience a valve failure. In this case, it  
will either sit there and appear to run happily but will pump no fluid (valve  
won't close), or it will lock up due to an inability to move the fluid out of  
the compression chamber (valve won't open). If it is running happily, then 
once  you have established that there is indeed plenty of freon in the system, 
but  nothing is moving, then you have no choice but to change the compressor. 
Again,  a system with a compressor that has had a valve failure is a good 
candidate for  a new compressor." 
"Now, if the compressor is mechanically locked up it could be because of a  
couple of things. If the compressor is on a heat pump, make sure the reversing  
valve isn't stuck half way. Also make sure the expansion valve is working; if 
it  is blocked it can lock the compressor. Also make sure the filter isn't 
clogged.  I once saw a system that had a locked compressor due to liquid lock. 
Some idiot  had "serviced" the system by adding freon, and adding freon, and 
adding freon  until the thing was completely full of liquid. Trust me; that 
doesn't work." 
"Should diagnosis show a clogged filter, then this should be taken as  
positive evidence of some failure in the system OTHER than a compressor 
failure.  
Typically, it will be metal fragments out of the compressor that clogs the  
filter. This can only happen if something is causing the compressor to wear 
very  
rapidly, particularly in the pistons, the rings, the bores, and the bearings.  
Either the compressor has vastly insufficient lubrication OR (and more 
commonly)  liquid freon is getting into the compressor on the suction line. 
This 
behavior  must be stopped. Look at the expansion valve and at the reversing 
valve 
(for a  heat pump)." 
"Often an old system experiences enough mechanical wear internally that it is 
 "worn in" and needs more torque to start against the system load than can be 
 delivered. This system will sound just like one with a locked bearing; the  
compressor will buzz loudly for a few seconds then the thermal limiter will 
kill  it. Occasionally, this system will start right up if you whack the 
compressor  with a rubber mallet while it is buzzing. Such a system is a good 
candidate for  a hard-start kit. This kit stores energy and, when the 
compressor is 
told to  start, dumps extra current into the compressor for a second or so. 
This  overloads the compressor, but gives some extra torque for a short time 
and 
is  often enough to make that compressor run again. I have had hard-start kits 
give  me an extra 8 or 9 years in some old units that otherwise I would have 
been  replacing. Conversely, I have had them give only a few months. It is 
your call,  but considering how cheap a hard-start kit is, it is worth trying 
when the  symptoms are as described." 
"And this, in a nutshell, is what can happen to an air conditioner compressor 
 when it shorts to ground, and what you can do about  it."