I agree with the concept that the UPS time is really based on holding the 
control system alive until the generators kick in at the correct voltage. 
Whether the kick in is automatic or manual, there will always be some zero 
voltage time that you need the UPS to keep power for the computers. The most 
damaging thing that UPS can prevent is the ON,  OFF,  ON,  OFF. etc that could 
happen during a utility brown out of capacitor switching times.  Such voltage 
losses and re-connections can kill a hard drive pretty fast.
 
If you have no generators, then the UPS has to hold long enough for an orderly 
shutdown of the IA.
 
Testing of the UPS should be scheduled whenever there is a plant shutdown or 
scheduled maintenance. We tested this once by pulling the main panel connection 
from the Utility at a site where I was asked to help.  The IA kept running OK 
as the UPS worked as expected but there were a few surprises in other areas.  
We scheduled the power fail days in advance and informed all departments.  A 
coulple minutes after we pulled the power, the IT guys came running over to say 
we had killed their servers!  They fouund out that their UPS was defective!
 
Terry
-- No attachments (even text) are allowed --
-- Type: application/ms-tnef
-- File: winmail.dat


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: