Rakesh, Floating point is supported. First of all, if you haven't done it, remove the Backup FBM from the base-plate to test the configuration with a single operating Modbus Master. Makes life much easier for troubleshooting.... Did you add the +H to the XML configuration if the Slave supports function code 8 (diagnostics)? If this option is enabled and there is no FDSI block configured, it will only send out heartbeats. If the device stays healthy in SMDH it proves that the wiring & termination is correct because the heartbeat is replied. If you add the +H and the device fails it is not in your FDSI block configuration. Then you might have to swap the "+" and "-" on the RS-485 wiring, or enable termination, or check the SG & Sh, or check the dipswitches on the TA. Even if you do not use RS-232, the dipswitches do have influence on the RS-485 communication so they must all be switched to OPEN. If you have the FDSI driver 1.1QF2 or later AND you are using a TA (Terminal Assembly board) rev E, you may have to toggle only C5 and C6 to CLOSED (noise immunity enhancement). BTW: Are you sure it is address 430001 (6 digits) and not 43001 (5 digits). It's not quite common for Slaves to support the 6 digit numbering (especially older Slaves do not support this). PS: When you checked the configuration with ModScan, did you use the RS-485 communication (including the converters if you are using converters in the field) or did you use RS-232? FoxDoc B0700BG explains the Modbus FDSI Protocol Handler. FoxDoc B0700AH explains quite in detail how to wire, ground and terminate the wiring between the TA and devices. Good luck, Gerrit van Doorn -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of RAKESH DASH Sent: zaterdag 30 juni 2012 19:53 To: foxboro@xxxxxxxxxxxxx Subject: [foxboro] FBM231 RS485 COMMUNICATION Hi there, I am trying to interface FBM231 with an external device over RS485. The modbus data is Holding Register Floating Point (4 bytes) I checked the communication and data using modscan in a laptop and all is good. The configuration in FDSI baud rate etc. is also fine FBM231 is showing healthy on communication. But As soon as I define even one signal in the RIN block in the compound for receiving the data & download, the FBM231 goes out of order and shows me as device failed. I have configured the point address PNT_NO as 430001:F4. I there any known issue of such kind ? Does the FBM231 support floating point signals ? I am stuck with this and I have to wind this up by Tuesday. Any help on the subject is appreciated. Thanks !! Regards, - Rakesh _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave *** Confidentiality Notice: This e-mail, including any associated or attached files, is intended solely for the individual or entity to which it is addressed. This e-mail is confidential and may well also be legally privileged. If you have received it in error, you are on notice of its status. Please notify the sender immediately by reply e-mail and then delete this message from your system. Please do not copy it or use it for any purposes, or disclose its contents to any other person. This email comes from a division of the Invensys Group, owned by Invensys plc, which is a company registered in England and Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 7AW (Registered number 166023). For a list of European legal entities within the Invensys Group, please go to http://www.invensys.com/en/legal/default.aspx. You may contact Invensys plc on +44 (0)20 3155 1200 or e-mail reception@xxxxxxxxxxxxx This e-mail and any attachments thereto may be subject to the terms of any agreements between Invensys (and/or its subsidiaries and affiliates) and the recipient (and/or its subsidiaries and affiliates). _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave