[foxboro] CP60 Failure Error
- From: kabir ahmed <worldofkabir@xxxxxxxxx>
- To: foxboro@xxxxxxxxxxxxx
- Date: Thu, 16 Jul 2009 21:41:43 -0700 (PDT)
Dear Experts,
We've experienced a strange CP60 Failure and the details of the system is as
follow:
CP60 Redundant on I/A system 6.5
with AW51E as Engineernig Station
two WP51D as Operator stations
One of the CP60s got the red indication and system Alarm observed that became
Blinking Green after few seconds but the CP60 remained red indicated.
the line printer showed the following messages in sequence
15-07-09 16:49:51 0 SYSMON = SYSMN2 03CP02 Process = PMAINT03CP02
PIOMAI 000002 hardware Fault 251550(Valve) FAILSAFE TIMOUT
15-07-09 17:52:25 0 SYSMON = SYSMN2 03CP02 Process = PMAINT03CP02
PIOMAI 000002 hardware Fault 251550(Valve) FAILSAFE TIMOUT
15-07-09 18:01:00 0 SYSMON = SYSMN2 03CP02 Fault Tolerant Exec
SM_MSG -00047 Fault Tolerant Prim Module Now single. ROM Addr 00006C170EB0
15-07-09 18:01:02 0 SYSMON = SYSMN2 03CP02 Error Protocol
FTXSS 000081 Error Escalation Threshold has been exceeded 00006C173E08
15-07-09 18:01:02 0 SYSMON = SYSMN2 03CP02 Error Protocol
FTXSS 000081 Error Escalation Threshold has been exceeded 00006C173E08
Kindly Suggest possibile causes for such failure and How could we configure our
CP in FAILSAFE mode so that it retain the last good value in case pf any such
failure.
thanks
Kabir Ahmed
G.E.P I&C
Pakistan Refinery Ltd.
K A B I R AHMED
________________________________
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts:
- » [foxboro] CP60 Failure Error - kabir ahmed