Dear Kabir,
When you say, "One of the CP60s got the red indication" you mean the LEDs on
the modules or the indication in SMDH? If red in SMDH, what did the detail
display show?
It appears from your messages below you lost communication briefly with a field
device and shortly thereafter had a fault tolerant CP go single. Because these
happened relatively close together I'd certainly look at your fieldbus and
cellbus installation, power and grounding. There are fairly extensive
recommendations for CP60 fieldbus installation and isolation - have these been
followed?
What is 251550? Is this an FBM43 with intelligent positioner? How is the
fieldbus installed on this CP60 - all copper, copper/fiber? What I/O modules -
100 series or 200 series? What fieldbus interface modules, and how many FBMs
total and per interface?
Failsafe engineering is critical and needs more attention than a brief email,
however the documentation does cover how to set failsafe actions when desired
for FBMs and intelligent field devices. You want your CP to maintain last good
value of inputs? Or your final control elements to maintain last good value on
loss of comms with the CP? Last good value is the default behavior but
specific failsafe actions can be configured on a channel by channel basis as
appropriate. If failsafe actions are configured on some of your outputs, be
very sure of the consequences before you change those back to use last good
value.
Regards,
Kevin FitzGerrell
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of kabir ahmed
Sent: Friday, July 17, 2009 1:42 PM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] CP60 Failure Error
Dear Experts,
We've experienced a strange CP60 Failure and the details of the system is as
follow:
CP60 Redundant on I/A system 6.5
with AW51E as Engineernig Station
two WP51D as Operator stations
One of the CP60s got the red indication and system Alarm observed that became
Blinking Green after few seconds but the CP60 remained red indicated.
the line printer showed the following messages in sequence
15-07-09 16:49:51 0 SYSMON = SYSMN2 03CP02 Process = PMAINT03CP02
PIOMAI 000002 hardware Fault 251550(Valve) FAILSAFE TIMOUT
15-07-09 17:52:25 0 SYSMON = SYSMN2 03CP02 Process = PMAINT03CP02
PIOMAI 000002 hardware Fault 251550(Valve) FAILSAFE TIMOUT
15-07-09 18:01:00 0 SYSMON = SYSMN2 03CP02 Fault Tolerant Exec
SM_MSG -00047 Fault Tolerant Prim Module Now single. ROM Addr 00006C170EB0
15-07-09 18:01:02 0 SYSMON = SYSMN2 03CP02 Error Protocol
FTXSS 000081 Error Escalation Threshold has been exceeded 00006C173E08
15-07-09 18:01:02 0 SYSMON = SYSMN2 03CP02 Error Protocol
FTXSS 000081 Error Escalation Threshold has been exceeded 00006C173E08
Kindly Suggest possibile causes for such failure and How could we configure our
CP in FAILSAFE mode so that it retain the last good value in case pf any such
failure.
thanks
Kabir Ahmed
G.E.P I&C
Pakistan Refinery Ltd.
K A B I R AHMED
________________________________
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: