[SI-LIST] Re: Trace width and current capacity

  • From: Jim Roberts <jgroberts@xxxxxxxxxx>
  • To: jrbarnes@xxxxxxxxx
  • Date: Fri, 21 Mar 2003 17:17:22 +0100

Hi John,
        Have you only considered solid wires. What about braided and 
multicore?

        Another point is that with over-etching traces have "sharp" 
edges at high frequencies
skin effect forces the current to flow in the corners.
        With high power high frequency it is interesting to see how 
quickly the traces burn.
Fortunately for the majority of applications we are talking about low 
levels of high frequency power so the only problem  is the  increased 
signal loss.

Thanks,
Jim

John Barnes wrote:

>Harry,
>A related subject to the ampacity (safe current-carrying capacity) of
>printed circuit board traces is the ampacity of wires.  I've been
>studying both topics seriously since June 1999.  I will be including the
>results of these studies in the book I am writing for Kluwer (Robust
>Electronic Design Reference, to be published late this year) in:
>*  Appendix F: Important Properties of Wires and Cables.
>*  Appendix G: Important Properties of PCB Traces, Flat Cables, and 
>   Busbars.
>
>I've come up with a simple way to estimate the ampacity of wires with
>about +/-34% accuracy (+/-2 standard deviations, should cover 95% of
>real data).  I would like some SI-LIST'ers and EMC-PSTC'ers to try my
>method, see how it compares to data they have seen/gathered/used, and
>give me feedback.  From various sources I found over 1300 datapoints of
>wire ampacity versus:
>*  Type of conductor (Kcond, from Table F-6).
>*  Environment (Kenv, from Table F-7).
>*  Number of wires in bundle/cable (N).
>*  Wire cross-sectional area (CSA, in mm^2 = 10^-6 m^2).
>*  Wire temperature (Twire, in degrees C).
>      AND
>*  Ambient temperature (Tamb, in degrees C) (or temperature rise, in 
>   degrees C).
> 
>For American Wire Gage (AWG),
>   solid wire diameter = 0.0082515 * 0.89053^AWG meters
>   CSA = (pi/4) * diameter^2
>
>I had to use two equations, because plotting and regression analyses of
>the data showed a sharp bend at about 0.5-0.7 mm^2 CSA.  For large wires
>changing the CSA has a strong effect on the wire resistance, and thus
>the heat produced in the wire by current (P = I^2 * R), but a relatively
>small effect on the surface area of the wire.  For small wires changing
>the CSA seems to have a much greater relative effect on surface area,
>and thus the wire's ability to conduct/convect/radiate heat away.  I
>decided to make the break-point between the equations at 0.5 mm^2,
>because this is the smallest size wire permitted for linecords.  So the
>first equation covers linecords and other power wiring, while the second
>equation basically covers signal wiring.
>
>Here is my proposed method for estimating the ampacity of wires.  
>For CSA >= 0.5 mm^2 (20AWG and larger)
>    I = Kcond * Kenv * N^-0.2 * CSA^0.642 * sqrt(Twire - Tamb) amperes
>For CSA <= 0.5 mm^2 (21 AWG and smaller)
>    I = Kcond * Kenv * N^-0.2 * 1.122 * CSA^0.808 * sqrt(Twire - Tamb)
>        amperes 
>
>Table F-6: Ampacity Factor for Base Conductor Material
>*  Copper has   Kcond = 1.00.
>*  Aluminum has Kcond = 0.80.
>*  Nickel has   Kcond = 0.56.   
>
>Table F-7: Ampacity Factor for Environment
>*  Free air has        Kenv = 2.60.
>*  Cables have         Kenv = 2.24.
>*  Equipment has       Kenv = 2.06.
>*  Wire in conduit has Kenv = 1.77.
>
>Many standards specify the wire size to be used for a given current in a
>specified environment.  So Appendix F also (already) includes 23 tables
>summarizing these requirements from:
>*  IEC 950.
>*  SAE AS50881.
>*  MIL-W-5088.
>*  HS-1738.
>*  NFPA 79.
>*  UL 486.
>*  UL 817.
>*  CAN/CSA C22.2 No.21-95.
>*  IEC 60799.
>*  National Electrical Code (NFPA 70).
>*  Canadian Electrical Code.
>
>My list of references for Appendix F is 5 pages long, so I won't include
>it with this post.  But I can post it later if there is interest.
>
>So, if you are working on something that requires you to choose a wire
>size/temperature rating based on the current through the wire, how about
>giving my proposed method a try?  Please see how it compares to your
>present method(s), and let me know the results.
> 
>I would like to specifically acknowledge Doug Brooks' article
>"Temperature Rise in PCB Traces" (   http://www.ultracad.com/pcbtemp.pdf
>) as the inspiration for the method I used to come up with these
>equations.
>
>Thanks!
>               John Barnes KS4GL, PE, NCE, ESDC Eng., SM IEEE
>               dBi Corporation
>               http://www.dbicorporation.com/
>               (859)253-1178  phone
>               (859)252-6128  fax
>               jrbarnes@xxxxxxxxx
>------------------------------------------------------------------
>To unsubscribe from si-list:
>si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field
>
>or to administer your membership from a web page, go to:
>//www.freelists.org/webpage/si-list
>
>For help:
>si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field
>
>List archives are viewable at:     
>               //www.freelists.org/archives/si-list
>or at our remote archives:
>               http://groups.yahoo.com/group/si-list/messages 
>Old (prior to June 6, 2001) list archives are viewable at:
>               http://www.qsl.net/wb6tpu
>  
>
>  
>



------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field

List archives are viewable at:     
                //www.freelists.org/archives/si-list
or at our remote archives:
                http://groups.yahoo.com/group/si-list/messages 
Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu
  