Re: [foxboro] Windows-NT AW70s viewing sequence block code via FoxSelect

  • From: <Martin.Theobald@xxxxxxxxxxxxxx>
  • To: <foxboro@xxxxxxxxxxxxx>
  • Date: Thu, 30 Oct 2014 13:10:05 +0000

Joe,

The newer detail displays for the sequence blocks also have a button for 
displaying the Source code so you may want to copy the <.s> files around as 
well.

Need less to say, if plants are using SFC then there another extensions to be 
copied as well, as well as having to have 'dummy' checkpoint files to the 
non-host boxes to allow the SFC client to work.


Regards,

Martin Theobald

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of Joseph M. Riccardi
Sent: 27 October 2014 23:52
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows-NT AW70s viewing sequence block code via 
FoxSelect

Tom,

Thanks for the confirmation.  You actually reminded me that I only need to copy 
the *.r files...


Joseph M. Riccardi
386-441-0250 Office
386-451-7607 Cell

Joe@xxxxxxxxxxxxx

"To give real service you must add something that cannot be bought or measured 
with money; and that is sincerity and integrity." - Donald A. Adams

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of Badura, Tom
Sent: Monday, October 27, 2014 4:44 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Windows-NT AW70s viewing sequence block code via 
FoxSelect

Joe,
We do this annually from our AW91 host to our WP92 workstations so the sequence 
and PLB detail displays are at least close to accurate.  I think the 
directories listed below are still valid.

Tom Badura
Plastics Engineering Company
tbadura@xxxxxxxxxx

* Update Sequence and PLB Files on Workstations
PLB Files:  usr\plcfv\CMP_NAME\PLB_NAME\*.fdf
Sequence Files:  opt/fox/ciocfg/CMP_NAME/*.r


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of Joseph M. Riccardi
Sent: Monday, October 27, 2014 6:18 PM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Windows-NT AW70s viewing sequence block code via FoxSelect

Folks,
On Windows-NT AW70s, do I have to copy the HLBL files to the non-host AWs to 
view the sequence block code via FoxSelect?  I vaguely remember this was an 
issue in the beginning with UNIX AWs but eventually resolved.  If so, I am 
guessing it was not an easy fix due to the Windows limitations.

Also, the HLBL files are not in the default location.  If the only solution is 
to manually copy the files, where would I copy them to; the default location or 
the host AWs custom location?

Thanks again for all of the help.


Joseph M. Riccardi
386-441-0250 Office
386-451-7607 Cell

Joe@xxxxxxxxxxxxx <mailto:Joe@xxxxxxxxxxxxx>

"To give real service you must add something that cannot be bought or measured 
with money; and that is sincerity and integrity." - Donald A. Adams



_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process Systems 
(formerly The Foxboro Company). Use the info you obtain here at your own risks. 
Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave





_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process Systems 
(formerly The Foxboro Company). Use the info you obtain here at your own risks. 
Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave

***************************************************************************** 
This e-mail and any files attached are strictly confidential, may be legally 
privileged and are intended solely for the addressee. If you are not the 
intended recipient please notify the sender immediately by return email and 
then delete the e-mail and any attachments immediately. The views and or 
opinions expressed in this e-mail are not necessarily the views of De La Rue 
plc or any of its subsidiaries and the De La Rue Group of companies, their 
directors, officers and employees make no representation about and accept no 
liability for its accuracy or completeness. You should ensure that you have 
adequate virus protection as the De La Rue Group of companies do not accept 
liability for any viruses. De La Rue plc Registered No.3834125, De La Rue 
Holdings plc Registered No 58025 and De La Rue International Limited Registered 
No 720284 are all registered in England with their registered office at: De La 
Rue House, Jays Close, Viables, Basingstoke, Hampshire RG22 4BS 
*****************************************************************************
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: