Christian,

Thanks for the reply. I checked "show spantree adminedge" and found Edge-Port 
turned ON for all fe.x.x device ports, and Non-Edge-Port turned ON for all 
ge.x.x uplink ports. Each switch was configured with SCAS 3.4.1.

"show rmon stats" revealed mostly no CRC errors or fragments on most all of the 
ports experiencing the "hot re-marry". ATS connected ports show a number of CRC 
errors and fragments, but these do not experience the issue. The switches have 
been running for 131 days and have experienced no additional respans since 
startup.

I have opened a case with TAC and will pass along this additional information 
when contacted. Thank you for giving me further food for thought.

Regards,
Dave


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of Horn, Christian
Sent: Tuesday, January 31, 2012 4:00 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Switch Port Failure and Recovery on ZCPs/FCPs

Dave

The 7 days is the time between the CP's force diagnostic "Hot Re-marry" (803.3 
mac reset), this is normal behaviour and happens on all CPs.

However the errors and messages you are getting suggest your switch ports are 
incorrectly configured, in brief, all "uplink" ports should be set up with 
adminedge = false and all device ports i.e CPs AWs should have adminedge = 
true. Were the switches configured using the Invensys Switch Configurator? 
Also you check for bad fibre connections on each switch within the switch 
console with 'show rmon stats' command, look for CRC errors, fragments etc.


Regards,
Christian Horn

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of dave.caldwell@xxxxxxxxxxxxxx
Sent: 16 January 2012 19:21
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Switch Port Failure and Recovery on ZCPs/FCPs

All knowing list,

I am running ZCP/FCP image 860050, I/A version 8.6, and N series switch 
firmware 06.12.03.003.

I consistently see the same behavior for every ZCP/FCP on my system:
- Every 7 days to the minute both the control and IO ports of the ZCP and the 
control ports of the FCP record a "link down" error in the syslog for the 
switch, followed by a "link up"
- WireShark shows a drop out of the Primary Port Test and Alternate Port Test 
for control ports of about 1.5 seconds
- the link light on the switch for the ZCP/FCP ports goes out for 1.5 seconds
- both the A switch and B switch are affected simultaneously
- on the ZCP/FCP the green light goes out and red light comes on, then returns 
normal
- not sure what the TX/RX lights on ZCP/FCP did, but suspect they too went out
- appears an 802.3 MAC Reset is incremented in SMDH (I'll verify tomorrow when 
it happens next)
- Occasionally, these will also record as port failures and recoveries in SMDH 
and system monitor log
- Occasionally, these will also record as FCM failures and recoveries in SMDH 
and system monitor log
- this started in September after we upgraded all ZCPs/FCPs to 8.6 and our 
CBLAN to MESH with ATSs and new switches
- no such errors occur on any other type of ports such as ATSs or AWs

The times are different for each ZCP/FCP but all have the same period (7 days 
to the minute) and do not line up easily with anything we might be scheduling 
weekly on the system.

Thankfully, the error appears fairly harmless. I'm thinking ZCP/FCP firmware 
bug, but is it possible that it's something else? I could find nothing on a 
search of the support sight. I have not contacted TAC, but plan on doing so 
soon. 

Before proceeding, has anyone else seen this issue?

Thanks,
Dave

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 


*** Confidentiality Notice: This e-mail, including any associated or attached 
files, is intended solely for the individual or entity to which it is 
addressed. This e-mail is confidential and may well also be legally privileged. 
If you have received it in error, you are on notice of its status. Please 
notify the sender immediately by reply e-mail and then delete this message from 
your system. Please do not copy it or use it for any purposes, or disclose its 
contents to any other person. This email comes from a division of the Invensys 
Group, owned by Invensys plc, which is a company registered in England and 
Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 
7AW (Registered number 166023). For a list of European legal entities within 
the Invensys Group, please go to http://www.invensys.com/en/legal/default.aspx.

You may contact Invensys plc on +44 (0)20 3155 1200 or e-mail 
reception@xxxxxxxxxxxxx This e-mail and any attachments thereto may be subject 
to the terms of any agreements between Invensys (and/or its subsidiaries and 
affiliates) and the recipient (and/or its subsidiaries and affiliates).


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: