Hi Matt,
Thank you for this. The code obviously looks better than what I have 
implemented; This was done on a fast track mode, I tested to work at the time; 
I wanted to visit this but dragged till I saw this email chain.

I process little better with IF cycle on a panic mode; So, introduced 2sec (LC 
scan was 2s) wait between two IFs to make sure that the level really drops to 
avoid spurious trip was the aim of that 2sec delay; I should have avoided the 
2sec WAIT for alarm FLAG, moving one line upwards when HOLIM is set to true as 
you have done below

I will test this to be sure (due to my deficiency) as I see it works and modify 
the existing code, this year. Thank you

Regards,
Srini

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On ;
Behalf Of Gunter, Matt
Sent: Wednesday, February 06, 2019 8:46 AM
To: foxboro@xxxxxxxxxxxxx
Subject: [EXT] Re: [foxboro] Rate of drop Alarm with respect to time

WARNING: This email originated from outside of the organization. Exercise 
caution when viewing attachments, clicking links, or responding to requests.


Srini,
I offer this up without any testing or guarantees...  The usual disclaimers 
regarding the use of anything below could result in the end of life as we know 
it all apply!

In a real text editor, everything lines up with slight indentation for 
readability.

I don't care for the use of labels because it lends itself to spaghetti code.  
I don't know the purpose of all of the 2s delays so there is only one in the 
code below, but I think it would accomplish what you are after.

VARIABLES
NOW    :R;
DELTA  :R;
PREV   :R;
FLAG   :B;
SET    :B;

USER_LABELS
{INPUT}
LC30   : RI0001;        {LC30.MEAS}

{OUTPUT}
FLAG   : BO0001;        {Status of Logic for Alarms}
HOLIM  : RO0001;        {HOLIM connect to LC30_HOLIM}
OUT1   : RO0002;

STATEMENTS

PREV   := LC30;
HOLIM  := 100;

WHILE
  NOW   := LC30;
  DELTA := PREV - NOW;
  OUT1  := DELTA;
  IF ((DELTA >= 5) AND SET) THEN
    HOLIM := 0;
    FLAG  := TRUE;
  ELSEIF (DELTA >= 5) THEN
    SET   := TRUE;
  ELSE
    SET   := FALSE;
  ENDIF;
  WAIT  2;
  HOLIM := 100;
  FLAG  := FALSE;
  PREV  := NOW;
ENDWHILE;

ENDSEQUENCE





------------------------------------------------------------------------------

Notice: This e-mail is intended solely for use of the individual or entity to 
which it is addressed and may contain information that is proprietary, 
privileged and/or exempt from disclosure under applicable law. If the reader is 
not the intended recipient or agent responsible for delivering the message to 
the intended recipient, you are hereby notified that any dissemination, 
distribution or copying of this communication is strictly prohibited. This 
communication may also contain data subject to U.S. export laws. If so, data 
subject to the International Traffic in Arms Regulation cannot be disseminated, 
distributed, transferred, or copied, whether incorporated or in its original 
form, to foreign nationals residing in the U.S. or abroad, absent the express 
prior approval of the U.S. Department of State. Data subject to the Export 
Administration Act may not be disseminated, distributed, transferred or copied 
contrary to U. S. Department of Commerce regulations. If you have received thi  
s communication in error, please notify the sender by reply e-mail and destroy 
the e-mail message and any physical copies made of the communication.
 Thank you.
*********************


_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric 
(formerly The Foxboro Company).  Use the info you obtain here at your own 
risks.  See the disclaimer at 
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.thecassandraproject.org_disclaimer.html&d=DwIDaQ&c=zgHsTqBQkGAdNuoPRxUzSQ&r=k7AF9dsAUnHrqp5ddRhLBXpnci0j0uVlauIdM6flLFM&m=D0YUae1oiU_E6Q8tC5eV8HzyPocJIxYg4SdIWUJP8GQ&s=TlBj_EwE7G4oVpWCM7qhwWaXM5Q92Y_K_X242quGwZM&e=

foxboro mailing list:               
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.freelists.org_list_foxboro&d=DwIDaQ&c=zgHsTqBQkGAdNuoPRxUzSQ&r=k7AF9dsAUnHrqp5ddRhLBXpnci0j0uVlauIdM6flLFM&m=D0YUae1oiU_E6Q8tC5eV8HzyPocJIxYg4SdIWUJP8GQ&s=2WywDf9LH-mcBfTmedKrhEiIhJ-bNp988Q-deLZsBPc&e=
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


For more information on Nutrien's email policy or to unsubscribe, click here: 
https://www.nutrien.com/important-notice
Pour plus de renseignements sur la politique de courrier électronique de 
Nutrien ou pour vous désabonner, cliquez ici: 
https://www.nutrien.com/avis-important
 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: