Re: [foxboro] OPC Server Tag Quality "bad non-specific" for some Point

  • From: Vitor Vale <vitorvale@xxxxxxxxx>
  • To: "Lars K. Bekker" <lkb@xxxxxxxxxx>, foxboro@xxxxxxxxxxxxx
  • Date: Thu, 14 Mar 2019 13:08:24 -0300

Thanks Lars for return.
But unfortunately I cant do deploy frequently on control strategy, because
(if I understood correctly your answer) when I change execution order, for
example, a have to deploy all bocks on control strategy and thus could
disturb process variable due block reinitialization.

Best Regards

Em qui, 14 de mar de 2019 Ã s 09:22, Lars K. Bekker <lkb@xxxxxxxxxx>
escreveu:

Hello Vitor,


We are having exactly the same issues, and we have found some temporary
fixes.

- If we change the execution order for  E.G two temperature transmitters
and then download.

- Restart the machine with hosting the OPC server.

Our system is quite fragile and not maintained at all and are going to be
out -phased within short time, so our client is not interested in investing
any resources(time and money) in it.
So we only have the temporarily fixes, and it happens frequently 5 days to
3rd week.

Have you found any permanent solution?


Med vennlig hilsen / Best regards

Lars K. Bekker
Automation engineer



-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> On
Behalf Of Vitor Vale
Sent: Tuesday, March 12, 2019 19:30
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] OPC Server Tag Quality "bad non-specific" for some Point

Hi All,
We have a problem with our OPC server (DA) related some tags. When we
check the point through Matrikon OPC Explorer(Client) some points for
different
controllers(FCP27)) are OK (good non-specific) but others from another
controllers ara bad non-specific. We already check all services and they
are running as well.

That situation occurs only on 1 of our 8 servers.

Server: HP Z400  Windows 7 professional
IA ver. 8.8
AIM API ver 5.5.0

I hope that you can help us.

Thanks

Vitor Nascimento
PETROBRAS




_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html

foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave




 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: