Jason,The Foxboro  thermocouple 8 input card has channel 9 reading a RTD on the 
termination assembly. You can read that value without having to install a 
thermocouple unless you need to read the "roof" temperature in a cabinet. 
Remember that a TC gives temperature difference so might not give the best 
reading if it is in the same location as the termination assembly. You  might 
need to use RTD.Each particular item in the heat sensitive area can be checked 
in the specification sheets (PSS for Foxboro) to find the maximum operating 
temperature.The P92 PSS 21H-4D13 B4 gives max operating temperature 35 C and 20 
-80 % RH. There is no indication of what can fail if you run at or above 35 
C.If the air conditioning fails, most installations where I have been will open 
the DELL processor cabinet doors when the room temperature reaches 28 -29 C. I 
have never seen a control room or a rack room go over 30 degrees C and suspect 
that Operators might want to shutdown the plant, if this happened. But maybe 
this is a biased (Canadian) perspective on temperatures.
Terry

> To: foxboro@xxxxxxxxxxxxx
> Subject: [foxboro] FCP270 System Temperature Limits
> From: jaedwards@xxxxxxx
> Date: Tue, 22 Jun 2010 14:07:55 -0500
> 
> I looking for reasonable temperature limits for a system built with FCP270 
> processors, P90 and P92 work stations.  This is to help when the air 
> handling system fails.
> Most of our system is in one room.  The 270 processors and most of the I/O 
> are there.  The Servers for the Data Collectors, Historian, Galaxy and 
> Engineering Workstation are there also.  I put a thermocouple in the 
> Server cabinet that contains all of our computer servers and made one for 
> the general room temperature.   
> 
> So here are the questions. 
> 
> At what temperature do we start a level 3?  Operators take notice and you 
> have approximately 10 hours to fix it by opening doors, putting fans in 
> front of the cabinets, etc. 
> At what temperature do we start a level 2?  Operators consider what to do 
> if failures begin. 
> At what temperature do we start a level 1?  Failure eminent. 
> 
> The Dell servers seem a bit more fragile than the I/A hardware.  But I 
> would like to hear what others are doing.
> So what would fail first?
> 
> CP
> I/O Cards
> Communication cards
> P90
> P91 
> 
> 
> Jason
> 
>  
>  
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>  
> foxboro mailing list:             //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>  
                                          
_________________________________________________________________
Turn down-time into play-time with Messenger games
http://go.microsoft.com/?linkid?34385
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: