Re: [foxboro] FBM207B contact sense

  • From: "Brown, Stanley" <stan.brown@xxxxxxxxxxxxxxxxx>
  • To: "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>
  • Date: Wed, 2 Feb 2011 13:59:15 -0500

Hay if you have one of these $xoensive Foxboro support contract, the 
incremental cost should be $0 :-)


> -----Original Message-----
> From: Stan Brown [mailto:stanb@xxxxxxxxx] On Behalf Of Terry Doucet
> Sent: Wednesday, February 02, 2011 12:04 PM
> To: foxboro@xxxxxxxxxxxxx
> Subject: Re: [foxboro] FBM207B contact sense
>
> Most of my relay work was intended to separate the (expensive) FBM's
> from other electrical products so that an electrician working on a
> (usually 120V ) device who makes a mistake, does not put 120 V anywhere
> near the FBM's.  So relays were located in close proximity to the
> FBM's.  The rack rooms were air conditioned and filtered so that there
> was no corrosion. Corrosion monitoring was part of their maintenance.
> Often, my relay was driving a starter coil or isolating a motor status
> contact from the motor control center. But even if I had a field
> contact (tank level switch) I would bring the contact to a relay and
> then that relay would go to the FBM.  These relays were about $50 each
> so much cheaper than a blown FBM.
> Terry
>
> > To: foxboro@xxxxxxxxxxxxx
> > Subject: Re: [foxboro] FBM207B contact sense
> > From: corey.clingo@xxxxxxxx
> > Date: Wed, 2 Feb 2011 10:38:41 -0600
> >
> > If I had to guess, this relay is not sealed, or gold-plated, and it's
> a
> > CYA for them to account for any surface corrosion that may wind up on
> the
> > contacts and increase the resistance.
> >
> > Like I said, we have not had problems when the relays are mounted in
> a
> > relatively climate-controlled environment, but if you want to be
> sure, for
> > some years down the road, you'll have to explore other options.
> >
> >
> > Corey
> >
> >
> >
> >
> >
> > From:
> > "Joseph M. Riccardi" <Joe@xxxxxxxxxxxxx>
> > To:
> > <foxboro@xxxxxxxxxxxxx>
> > Date:
> > 02/02/2011 09:23 AM
> > Subject:
> > Re: [foxboro] FBM207B contact sense
> > Sent by:
> > foxboro-bounce@xxxxxxxxxxxxx
> >
> >
> >
> > Terry,
> >
> > The 72 mW rating is in the published spec for the A-B relay.  I am
> > guessing
> > that all contact closures are not equal, some have a higher
> resistance
> > than
> > others (i.e., silver-plated vs. gold-plated).  With lower power
> sources
> > like
> > the FBM207B, this voltage drop across the contact becomes more
> > significant.
> > I just never realized how significant until matching the FBM207B
> power
> > output spec published to the published A-B relay minimum power
> > requirements
> > across the contact.  The output of the FBM207B is current limited to
> 2.5
> > maDC because it supplies the 24 vDC source.
> >
> > I thought the same way you do until someone started reading the
> specs.
> >
> > Joseph M. Riccardi
> >
> > Senior I&C Engineer
> >
> > Bechtel Parsons Blue Grass Team
> >
> >
> >
> >
> >
> >
> >
> >
> _______________________________________________________________________
> > This mailing list is neither sponsored nor endorsed by Invensys
> Process
> > Systems (formerly The Foxboro Company). Use the info you obtain here
> at
> > your own risks. Read
> http://www.thecassandraproject.org/disclaimer.html
> >
> > foxboro mailing list:
> //www.freelists.org/list/foxboro
> > to subscribe:         mailto:foxboro-
> request@xxxxxxxxxxxxx?subject=join
> > to unsubscribe:      mailto:foxboro-
> request@xxxxxxxxxxxxx?subject=leave
> >
>
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list:             //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>


The information contained in this message and any attached files may be 
privileged and/or confidential and protected from disclosure. If you are not 
the intended recipient, any disclosure, copying, distribution or use of any of 
the information contained in or attached to this transmission is strictly 
prohibited. If you have received this transmission in error, please so notify 
the sender immediately without reading it. Also, please promptly destroy the 
original transmission and its attachments. Any views or opinions presented in 
this message or attachments are those of the author and do not necessarily 
represent those of KapStone Paper and Packaging Corporation or its subsidiaries.
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at