Joe, Below caption was taken from the B0400FA Din Rail User Guide...hope it helps... Fail-Safe Functionality FBM actions that occur during various failed conditions are dependent upon two things: the configuration of the FBM fail-safe parameters and the type of FBM failure. Two basic types of FBM failures can occur: Type 1 failures, such as FBM OFF-LINE, FBM DOWNLOAD, or FBM EEPROM UPDATE, involve an actual FBM failure. Type 2 failures (COMM FAIL), involve a loss of communications. Fail-Safe for Type 1 Failures - FBM FAIL Two variables (parameters), fail-safe mask (FSMM1) and fail-safe data (FSD0n), determine the action that the FBM takes when a Type 1 failure occurs. FSMM1, configured for a particular output, determines the state that is asserted at the output: Fallback Value, or Hold Current Value. The default setting of the fail-safe mask parameter is zero, to assert the Fallback Values. The mask can be set so that some outputs hold while others fall back. FSD0n, also configured for a particular output, determines the fallback value. The default value for analog outputs is zero, and the default value for digital values is false. Fail-Safe for Type 2 Failures - COMM FAIL In addition to the fail-safe mask and fail-safe data parameters, there are two other parameters, FSENAB and FSDLAY, that affect the FBM’s response to communications failures. FSENAB determines whether the output simply holds (FSENAB = 0) its output value during the communications failure until the communications failure ceases, or if it delays fail-safe action (FSENAB = 1) for the time specified by FSDLAY and then responds in the same way as Type 1 failures. Fail-Safe -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Riccardi, Joseph Sent: Tuesday, December 13, 2011 3:18 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FBM off-line Terry, I read the exact same quote you referenced and came to the same conclusion but was hoping to verify it with this inquiry to the List. I'll wait until tomorrow and if nothing else pops up I'll run with our conclusion until I can also test it. Thanks. Joseph M. Riccardi Senior I&C Engineer Bechtel Parsons Blue Grass Team Richmond, KY 859-626-4368 Office 386-451-7607 Personal Cell -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Terry Doucet Sent: Tuesday, December 13, 2011 5:53 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FBM off-line Joseph, I always loved the small note in EDOC below the description of the ECB's FSENAB parameter. "FSENAB does not affect Failsafe configuration. Setting FSENAB false does prevent the FBM from going to the Failsafe state because of CP-to-FBM communications failure, but it cannot prevent the FBM from going to Failsafe for any other reason." I'm pretty sure that the action that you describe (taking FBM off line in System Manager) is one of those "other reason"(s). So if you have selected and configured values for your outputs in the ECB, then taking the FBM off line will force the values at the outputs regardless of your configuration of the FSENAB parameter. But I have not tested it recently. Terry > Subject: [foxboro] FBM off-line > Date: Tue, 13 Dec 2011 15:43:08 -0600 > From: Joseph.Riccardi@xxxxxxxxxxx > To: foxboro@xxxxxxxxxxxxx > > Folks, > What state do the outputs go to when the FBM is manually taken off-line > (i.e., digital outputs, etc.)? Failsafe settings, just like lost > communications to the CP? Or something else? > > Joseph M. Riccardi > Senior I&C Engineer > Bechtel Parsons Blue Grass Team > Richmond, KY > 859-626-4368 Office > 386-451-7607 Personal Cell > > > > > > _______________________________________________________________________ > This mailing list is neither sponsored nor endorsed by Invensys Process > Systems (formerly The Foxboro Company). Use the info you obtain here at > your own risks. Read http://www.thecassandraproject.org/disclaimer.html > > foxboro mailing list: //www.freelists.org/list/foxboro > to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join > to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave > _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave *** Confidentiality Notice: This e-mail, including any associated or attached files, is intended solely for the individual or entity to which it is addressed. This e-mail is confidential and may well also be legally privileged. If you have received it in error, you are on notice of its status. Please notify the sender immediately by reply e-mail and then delete this message from your system. Please do not copy it or use it for any purposes, or disclose its contents to any other person. This email comes from a division of the Invensys Group, owned by Invensys plc, which is a company registered in England and Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 7AW (Registered number 166023). For a list of European legal entities within the Invensys Group, please go to http://www.invensys.com/en/legal/default.aspx. You may contact Invensys plc on +44 (0)20 3155 1200 or e-mail reception@xxxxxxxxxxxxx This e-mail and any attachments thereto may be subject to the terms of any agreements between Invensys (and/or its subsidiaries and affiliates) and the recipient (and/or its subsidiaries and affiliates). _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave