Hi Joe,
It depends on the type of your Siemens CPU (ex: SIMATIC S7-400: CPU 412-1 / 
412-2, 412-2 PN, 414-2 / 414-3, 414-3 PN/DP, 416-2 / 416-3, 416-3 PN/DP, 417-4).
Example: CPU 416-2 Central processing unit with: work memory 2.8 MB, (1.4 MB 
code, 1.4 MB data), 1st interface MPI/DP 12 Mbit/s, 2nd interface PROFIBUS DP.

Then you must choose the type of the Interface that you want to use, ex. 
Interface type: RS485, then you must define the Protocols you want to use, ex. 
PROFIBUS DP master, PROFIBUS DP slave.

The Siemens PLC interface configuration depends mostly on the CPU you have in 
the system. The system integration will have to be tested as much as possible 
on an off-line system.
It will require a good understanding of the hardware you already have in the 
system and the composition of the messages sent across the bus. (Are you using 
Matrikon OPC Server?). Also, Foxboro may impose some delays that has to be 
considered when the control interface is implemented with FBM222/223.

If you have more info to share on this site, then we will help with this 
integration.

Ion.

Ion Schiopu, MEE, P. Eng. - Electrical Engineer
Phone: 1 (403) 241 7752

________________________________
From: foxboro-bounce@xxxxxxxxxxxxx <foxboro-bounce@xxxxxxxxxxxxx> on behalf of 
Currano, Joe <Joseph.Currano@xxxxxxxxx>
Sent: Friday, May 28, 2021 2:27 PM
To: foxboro@xxxxxxxxxxxxx <foxboro@xxxxxxxxxxxxx>
Subject: [foxboro] DCS link to Siemens Simatic S7-400 with Profibus DP

We are trying to establish a link between our Foxboro DCS and a Siemens Simatic 
S7-400 PLC system. For most of our PLCs, we use FBM230/232/233 to read data via 
Modbus. However, this Siemens PLC already has an Anybus Profibus 
Master-Profibus Slave device set up on it which was used for remote monitoring 
by a vendor when they were running the Siemens system for us. Now our own 
operators are running the system, and we would like to be able to monitor 
(and/or control) it from the DCS.
I just found out the FBM222 and FBM223 are made for Profibus, and I'm thinking 
since the Profibus stuff is all there it should take less configuration on the 
Siemens side compared to setting up a brand new Modbus connection - is that 
right? Can someone give me some direction on how to accomplish this? How do you 
connect the hardware? Would the Anybus device still need to be there, or does 
the FBM take its place? I'm pretty new to the Siemens S7 system and Profibus.
I also need to decide whether to get a system integrator to help or try to do 
this all in-house, so trying to determine how complex this will be.


_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at 
https://na01.safelinks.protection.outlook.com/?urlÿtp%3A%2F%2Fwww.thecassandraproject.org%2Fdisclaimer.html&amp;data%7C01%7C%7C476efd9ce2a841ed005308d9221f7162%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637578340752549716%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdataÿfZKaRwF4UC1s%2B9fsmaGp1I0GNkgnCnL17MxtqjnrI%3D&amp;reservedÿ
foxboro mailing list:               
https://na01.safelinks.protection.outlook.com/?urlÿtp%3A%2F%2Fwww.freelists.org%2Flist%2Ffoxboro&amp;data%7C01%7C%7C476efd9ce2a841ed005308d9221f7162%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637578340752549716%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdataÿda705x8iTTJGmAZFJI3Miy%2BHaMiIvJayGFY0H5Hbg%3D&amp;reservedÿto
 subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subjectÿin
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subjectþave



 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts:

  • » Re: [foxboro] DCS link to Siemens Simatic S7-400 with Profibus DP - ION SCHIOPU