Foxboro recommends no more than one block per CP. Although this can get a 
little pricey, it keeps the "D" in DCS.


No really, I think there are some CP sizing spreadsheets on the customer 
support web site.

It's easy enough to look at the "LTRBUG"_STA:STATION information either 
with select or using omget to periodically grab a snapshot. Some of the key 
indicators are

"LTRBUG"_STA:STATION.IOLOAD     % of time scanning the physical I/O subsystem
"LTRBUG"_STA:STATION.BPLOAD     % of time processing blocks
"LTRBUG"_STA:STATION.SQLOAD     % of time processing sequence code
"LTRBUG"_STA:STATION.CPLOAD     Total of above

You probably want to keep the CPLOAD < 80% although anything < 90 seems to 
work pretty well on CP40s and CP60s, YMMV.

The object manager also places a load on the CP
"LTRBUG"_STA:STATION.OML_DAV    obeject manager load


"LTRBUG"_STA:STATION.IDLE_TM    % of time doing nothing (kind of)

Make sure that there aren't too many overruns.
"LTRBUG"_STA:STATION.CUMOVR     Total of number of CP overruns since last reset


Look to make sure that everything is phased well and you don't have periods 
and phases that fall together occasionally making for a big spike in CP 
activity.

I think that would do it.

Regards,
David






"The only reason for time, is so that everything doesn't happen at once." 
Buckaroo Banzai 

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: