Re: you can use the new NASTDB and NASOPT parameter (time related parameters to 
avoid chattering), but I am  almost sure that PID\PIDA\etc... do not support 
that yet

These parameters and others were added in V8.4. This is taken from B0700RT - 
Table D-3 Process Alarm Enhancements Summary:

The following Block Types
   PID, PIDA, PIDE,PIDX, PIDXE, DPIDA

Added support for:
   * Alarm Reprioritizaiton (PRTYPE) on these alarms: HHA/LLA, HA/LA, HDA/LDA, 
HOA/LOA
   * Alarm Message Regeneration (AMRTIN) on these alarms: HHA/LLA, HA/LA, 
HDA/LDA, HOA/LOA
   * Nuisance Alarm Suppression (NASOPT, NASTDB) on these alarms: HHA/LLA, 
HA/LA, HDA/LDA, HOA/LOA


Regards,
 
Alex Johnson
Invensys Operations Management
10900 Equity Drive
Houston, TX 77041
+1 713 329 8472 (desk)
+1 713 329 1600 (operator)
+1 713 329 1944 (SSC Fax)
+1 713 329 1700 (Central Fax)
alex.johnson@xxxxxxxxxxxx


-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On 
Behalf Of Corey R Clingo
Sent: Friday, May 06, 2011 10:58 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Alarm timer supression on PIDA block

"This can be a good Improvement for the I/A actually."

+1.  We try to attach alarms to the "primary operator interface" blocks, 
and if a controller exists, the PID(A) is almost always that block.
 

Corey



From:
Ricardo Abech <abech@xxxxxxxxxxxx>
To:
foxboro@xxxxxxxxxxxxx
Date:
05/06/2011 07:48 AM
Subject:
Re: [foxboro] Alarm timer supression on PIDA block
Sent by:
foxboro-bounce@xxxxxxxxxxxxx



Hi Luciano,

For most block types (AIN, CIN, etc?) you can use the new NASTDB and 
NASOPT parameter (time related parameters to avoid chattering), but I am 
almost sure that PID\PIDA\etc... do not support that yet, so you have to 
stick with the deadband (MEASDB), not very reliable to avoid chattering if 
the noise or variance is high. Unless you can use the AIN instead of the 
PID to alarm (not a good idea most of the time, since the PID is normally 
the block you use in the display).

This can be a good Improvement for the I/A actually. Maybe there is 
something already, but I am not aware of it.

Ricardo



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 


*** Confidentiality Notice: This e-mail, including any associated or attached 
files, is intended solely for the individual or entity to which it is 
addressed. This e-mail is confidential and may well also be legally privileged. 
If you have received it in error, you are on notice of its status. Please 
notify the sender immediately by reply e-mail and then delete this message from 
your system. Please do not copy it or use it for any purposes, or disclose its 
contents to any other person. This email comes from a division of the Invensys 
Group, owned by Invensys plc, which is a company registered in England and 
Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 
7AW (Registered number 166023). For a list of European legal entities within 
the Invensys Group, please go to 
http://www.invensys.com/legal/default.asp?top_nav_id=77&nav_id=80&prev_id=77.

You may contact Invensys plc on +44 (0)20 3155 1200 or e-mail 
reception@xxxxxxxxxxxxx This e-mail and any attachments thereto may be subject 
to the terms of any agreements between Invensys (and/or its subsidiaries and 
affiliates) and the recipient (and/or its subsidiaries and affiliates).


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: