We have a perplexing problem. One 4-20 mA input on a FBM04 is reading consistently lower in the AIN block than at the transmitter. The AIN is set for SCI=3 (4-20 mA) with KSCALE=1 and BSCALE=0. We've bench-tested the transmitter (Rosemount 3051) and it is right on the money, both with the HART and independently measuring the current output. What I see in the AIN is that both the RAW counts and the MEAS values are showing 0.8 psi lower than the transmitter (this is about 2% of scale). The odd thing is that this is across the range, so it looks like a bias. We've replaced the FBM and the problem is still there. We're going after the nosecone next. Could there be a drain in the wiring, like a poor termination, that would show a constant reduction in current? Anybody seen anything like this before? Brad Wilson Process Control Engineer ExxonMobil Chemical Co Edison Synthetics Plant 732-321-6115 732-321-6177 fax Brad.S.Wilson@xxxxxxxxxxxxxx _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave